EPA 608 HVAC Certification Exam
Recovery & Recycling Practice Questions
35 practice questions with detailed explanations — aligned to the EPA 608 HVAC Certification Exam.
Q1.What is the primary reason for recovering refrigerant?
A.To save moneyB.To prevent venting of ozone-depleting and global warming substances into the atmosphereC.To clean the systemD.To measure the chargeB. To prevent venting of ozone-depleting and global warming substances into the atmosphereExplanation: The core mandate of Section 608 is environmental protection: preventing the release of harmful ODS (CFCs/HCFCs) and HFCs.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q2.Recovery equipment used for the service or repair of small appliances must be certified by an EPA-approved laboratory if manufactured after:
A.July 1, 1992B.November 15, 1993C.January 1, 1995D.January 1, 2018B. November 15, 1993Explanation: November 15, 1993 is the cutoff date. Equipment made after this date must be third-party certified.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q3.During refrigerant recovery, which state of refrigerant is removed first to minimize time?
A.VaporB.LiquidC.SolidD.Superheated gasB. LiquidExplanation: Liquid recovery is much faster than vapor recovery because liquid has a higher density. Removing liquid first bulk-transfers the mass.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q4.A 'Self-Contained' recovery device:
A.Relies on the appliance compressorB.Has its own compressor to pump refrigerant out of the applianceC.Captures only vaporD.Is a plastic bagB. Has its own compressor to pump refrigerant out of the applianceExplanation: Self-contained (active) equipment has its own means (compressor/pump) to draw refrigerant out, independent of the appliance's operation.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q5.When recovering refrigerant into a non-pressurized container from a refrigerator with an inoperative compressor:
A.It is necessary to heat the compressor and strike it with a rubber malletB.It is necessary to use a vacuum pumpC.It is illegalD.You only need to access the low sideA. It is necessary to heat the compressor and strike it with a rubber malletExplanation: Heating and tapping the compressor helps release refrigerant trapped in the oil, which is critical when the compressor cannot run to circulate it.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q6.Which factor can affect the speed and efficiency of refrigerant recovery?
A.The length of the hosesB.The diameter of the hosesC.The ambient temperatureD.All of the aboveD. All of the aboveExplanation: Long/narrow hoses increase friction (pressure drop). High ambient temps raise tank pressure (bad) but help boil system refrigerant (good). All play a role.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q7.If a system contains 100 lbs of R-500, what is the required evacuation level before opening the system?
A.0 inches HgB.4 inches HgC.10 inches HgD.15 inches HgA. 0 inches HgExplanation: R-500 is a high-pressure refrigerant. <200 lbs requires 0 inches Hg vacuum.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q8.The push-pull method of recovery is used:
A.For recovering vapor onlyB.When the system contains less than 5 lbsC.For bulk liquid recovery from large systemsD.When the compressor is burned outC. For bulk liquid recovery from large systemsExplanation: Push-pull uses vapor from the recovery cylinder to push liquid out of the system, speeding up bulk transfer in large systems (>10 lbs).
Join 1,000+ users passing the EPA 608 HVAC Certification
Q9.Why is it important to monitor the weight of the recovery cylinder?
A.To calculate the billB.To prevent overfilling (hydrostatic pressure explosion)C.To verify the refrigerant typeD.To check for leaksB. To prevent overfilling (hydrostatic pressure explosion)Explanation: Safety is the primary reason. Overfilling (>80%) leaves no room for expansion, creating an explosion hazard.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q10.Mixing different refrigerants in a recovery tank will:
A.Create a more efficient blendB.Make the mixture impossible to reclaim and likely result in disposal feesC.Have no effectD.Lower the pressureB. Make the mixture impossible to reclaim and likely result in disposal feesExplanation: Mixed refrigerants cannot be separated easily. Reclaimers will destroy the mix and charge high fees.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q11.If a reclamation facility determines that the refrigerant sent to them is too contaminated to be reclaimed, they will:
A.Destroy itB.Return it to the technicianC.Sell it as-isD.Use it for fuelA. Destroy itExplanation: Heavily contaminated or mixed refrigerant that cannot be purified is incinerated (destroyed) in accordance with EPA rules.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q12.When recovering from a system with a burnout, what additional step is recommended?
A.Install a suction line filter drier before the recovery machineB.Vent the gasC.Heat the oilD.Use a smaller hoseA. Install a suction line filter drier before the recovery machineExplanation: Burnouts create acid and sludge. A filter drier protects the recovery machine from these contaminants.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q13.Recycling refrigerant involves:
A.Sending it to a factoryB.Running it through oil separators and filter-driersC.Chemical analysisD.DistillationB. Running it through oil separators and filter-driersExplanation: Recycling is the onsite cleaning of refrigerant to remove oil and moisture using filters, allowing reuse in the same owner's equipment.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q14.When switching a recovery unit from R-22 to R-410A, you must:
A.Change the oil and filter, and evacuate the machineB.Just switch the hosesC.Wash it with waterD.Do nothingA. Change the oil and filter, and evacuate the machineExplanation: To prevent cross-contamination (mixing oils and refrigerants), the machine must be purged/evacuated and filters changed.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q15.For small appliances, how much refrigerant must be recovered if the compressor is operative?
A.80%B.90%C.100%D.4 inches Hg vacuumB. 90%Explanation: With a working compressor, the standard is 90% of the charge.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q16.What feature of a recovery machine helps prevent the tank from overfilling?
A.Low pressure switchB.High pressure cutoutC.Tank liquid level float switchD.Oil separatorC. Tank liquid level float switchExplanation: A float switch connects to the recovery machine and shuts it off when the tank reaches 80% capacity.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q17.Passive recovery is fastest when:
A.The system is coldB.The system is warm and the recovery tank is coldC.Both are warmD.The tank is higher than the systemB. The system is warm and the recovery tank is coldExplanation: Heat increases system pressure (pushing refrigerant out), and cold lowers tank pressure (pulling refrigerant in). This differential drives passive recovery.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q18.To remove ice from a sight glass or viewing port, use:
A.An open flameB.A screwdriverC.Alcohol sprayD.Hot waterC. Alcohol sprayExplanation: Alcohol spray melts ice without damaging the glass or creating a fire hazard (unlike a torch).
Join 1,000+ users passing the EPA 608 HVAC Certification
Q19.The required recovery level for a very high-pressure appliance (like R-503) is:
A.0 inches HgB.10 inches HgC.20 inches HgD.0 psigA. 0 inches HgExplanation: Very high-pressure appliances require recovery to 0 inches Hg vacuum.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q20.Which of the following creates a 'High Pressure' condition that stops recovery?
A.The recovery tank valve is closedB.The recovery tank is emptyC.The system is emptyD.The ambient temp is lowA. The recovery tank valve is closedExplanation: If the tank valve is closed, the recovery machine pumps against a dead head, rapidly raising discharge pressure until the high-pressure switch trips.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q21.Why is it necessary to purge the gauge hoses before connecting to a system?
A.To check for leaksB.To remove non-condensables (air) from the hosesC.To cool the hosesD.To lubricate the sealsB. To remove non-condensables (air) from the hosesExplanation: Air trapped in hoses will be pushed into the system or recovery tank if not purged, contaminating the refrigerant.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q22.During vapor recovery, the compressor of the recovery machine might overheat if:
A.The suction pressure is too highB.The suction pressure is too low (restricted flow)C.The tank is coldD.The hoses are shortB. The suction pressure is too low (restricted flow)Explanation: Recovery compressors rely on the flow of refrigerant vapor for cooling. If flow is restricted (deep vacuum or blockage), it can overheat.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q23.Recovering refrigerant in the vapor phase reduces:
A.The chance of oil loss from the systemB.The recovery timeC.The tank pressureD.The efficiencyA. The chance of oil loss from the systemExplanation: Liquid recovery can sweep oil out of the system. Vapor recovery leaves the oil behind but is slower.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q24.What does 'Dehydration' mean in refrigeration?
A.Removing refrigerantB.Removing oilC.Removing moisture (water)D.Removing airC. Removing moisture (water)Explanation: Dehydration is the process of removing moisture from a system, typically via deep evacuation.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q25.Ideally, a system should be evacuated to:
A.0 psigB.25 inches HgC.500 micronsD.1000 micronsC. 500 micronsExplanation: 500 microns is the industry standard for a deep vacuum that ensures moisture removal.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q26.Recovery cylinders are designed to be refilled. Disposable cylinders are designed to be:
A.Refilled onceB.Discarded after one useC.Used for recoveryD.Returned to the manufacturerB. Discarded after one useExplanation: Disposable cylinders (DOT 39) have a check valve that prevents refilling. They must be used once and discarded.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q27.Before disposing of an appliance, you must:
A.Recover the refrigerant to the required levelB.Crush it immediatelyC.Bleed the chargeD.Remove the oil onlyA. Recover the refrigerant to the required levelExplanation: The key disposal requirement is recovering refrigerant to the EPA-mandated vacuum levels.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q28.Which condition allows for evacuating a system to 0 psig instead of a deep vacuum?
A.If the system is very oldB.If the system leaks enough that air enters when a vacuum is pulledC.If the technician is in a hurryD.If the ambient temperature is below 32°FB. If the system leaks enough that air enters when a vacuum is pulledExplanation: If leaks prevent holding a vacuum, pulling deep vacuum would just suck in air. The EPA allows stopping at 0 psig in this case.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q29.When using a gauge manifold, the 'Low Loss Fitting' refers to:
A.A fitting that restricts flowB.A fitting that closes automatically or manually to prevent venting when disconnecting hosesC.A leaky fittingD.A fitting for low pressure systemsB. A fitting that closes automatically or manually to prevent venting when disconnecting hosesExplanation: Low-loss fittings (required by EPA) seal the hose end to minimize refrigerant release during disconnection.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q30.What effect does low ambient temperature have on recovery?
A.It speeds it upB.It slows it downC.It has no effectD.It makes the tank pressure riseB. It slows it downExplanation: Cold temperatures lower the system pressure, reducing the pressure differential that pushes refrigerant into the recovery machine, slowing the process.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q31.Which recovery method is typically used on a system with a receiver?
A.Liquid recovery from the King ValveB.Vapor recovery from the suction lineC.System-dependent recoveryD.Gravity drainA. Liquid recovery from the King ValveExplanation: The King Valve (receiver outlet valve) provides direct access to liquid refrigerant, making it the ideal spot for bulk liquid recovery.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q32.The scale used to weigh a recovery tank must be:
A.Calibrated annuallyB.Able to shut off the machineC.AccurateD.DigitalC. AccurateExplanation: While shut-off features are great, the fundamental requirement is accuracy to prevent overfilling.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q33.When recovering R-11 or R-123 (Low Pressure), the recovery tank pressure will likely be:
A.Very high (200 psig)B.In a vacuumC.AtmosphericD.50 psigB. In a vacuumExplanation: Low-pressure refrigerants boil above room temperature (R-11 ~75°F, R-123 ~82°F). At normal room temp, they are liquids and often in a vacuum or very low pressure.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q34.Why is it important to remove the Schrader valve core before recovery on large systems?
A.To prevent it from freezingB.To increase flow rate and reduce recovery timeC.To check the oilD.To vent pressureB. To increase flow rate and reduce recovery timeExplanation: The valve core is a significant restriction. Removing it allows full-bore flow, drastically speeding up recovery.
Join 1,000+ users passing the EPA 608 HVAC Certification
Q35.Refrigerant leaving a recovery machine is typically:
A.LiquidB.VaporC.SolidD.OilA. LiquidExplanation: Recovery machines condense the vapor they pump so it enters the recovery cylinder as a liquid.