Type III (Low-Pressure) Practice Questions

45 practice questions with detailed explanations — aligned to the EPA 608 HVAC Certification Exam.

  1. Q1.What type of appliances are covered by Type III certification?

    A.High-pressure appliances
    B.Low-pressure appliances
    C.Small appliances
    D.Motor vehicle air conditioners
    BLow-pressure appliances

    Explanation: Type III certification covers the maintenance, service, repair, and disposal of low-pressure appliances, such as centrifugal chillers.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  2. Q2.Which refrigerant is typically used in low-pressure chillers?

    A.R-22
    B.R-410A
    C.R-123
    D.R-134a
    CR-123

    Explanation: R-123 is a common HCFC refrigerant used in low-pressure centrifugal chillers. (Older units used R-11).

    Join 1,000+ users passing the EPA 608 HVAC Certification

  3. Q3.What is the primary purpose of a purge unit on a low-pressure chiller?

    A.To remove moisture and non-condensables (air) from the system
    B.To add refrigerant to the system
    C.To circulate oil
    D.To cool the compressor
    ATo remove moisture and non-condensables (air) from the system

    Explanation: Since low-pressure systems operate in a vacuum, air and moisture can leak IN. The purge unit runs to separate and remove these non-condensables from the refrigerant.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  4. Q4.At what pressure does the rupture disc on a low-pressure centrifugal chiller typically burst?

    A.5 psig
    B.10 psig
    C.15 psig
    D.150 psig
    C15 psig

    Explanation: The rupture disc is a safety relief device set to burst at 15 psig to prevent over-pressurization of the low-pressure vessel.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  5. Q5.Where does air and moisture usually enter a low-pressure system?

    A.Through the condenser
    B.Through the purge unit vent
    C.Through leaks in gaskets or fittings when the system is operating
    D.It doesn't enter; refrigerant leaks out
    CThrough leaks in gaskets or fittings when the system is operating

    Explanation: Because low-pressure systems operate below atmospheric pressure (in a vacuum), leaks pull air and moisture INTO the system rather than pushing refrigerant out.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  6. Q6.When leak testing a low-pressure centrifugal with nitrogen, what is the maximum test pressure?

    A.5 psig
    B.10 psig
    C.15 psig
    D.25 psig
    B10 psig

    Explanation: You must not exceed 10 psig when pressurizing a low-pressure system, as the rupture disc will burst at 15 psig.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  7. Q7.What is the required recovery vacuum level for a Type III appliance using recovery equipment manufactured after Nov 15, 1993?

    A.0 inches Hg
    B.10 inches Hg
    C.25 inches Hg vacuum
    D.25 mm Hg absolute
    D25 mm Hg absolute

    Explanation: For Type III appliances, the required recovery level is 25 mm Hg absolute pressure (which is a deeper vacuum than 25 inches Hg).

    Join 1,000+ users passing the EPA 608 HVAC Certification

  8. Q8.When recovering liquid refrigerant from a chiller, you should remove liquid from the:

    A.Lowest point in the system
    B.Highest point in the system
    C.Compressor discharge
    D.Purge unit
    ALowest point in the system

    Explanation: Liquid settles at the bottom. Recovering from the lowest access point (often the evaporator or condenser drain) ensures you get the liquid first.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  9. Q9.After removing the liquid refrigerant, what must be done next?

    A.Fill with nitrogen
    B.Remove the remaining vapor refrigerant
    C.Change the oil
    D.Open the system
    BRemove the remaining vapor refrigerant

    Explanation: After liquid recovery, significant vapor remains. You must recover the vapor to the required vacuum level (25 mm Hg absolute) before opening the system.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  10. Q10.Why should you circulate water through the chiller bundles during refrigerant recovery?

    A.To cool the recovery machine
    B.To prevent the water from freezing in the tubes
    C.To wash the tubes
    D.To increase the pressure
    BTo prevent the water from freezing in the tubes

    Explanation: As refrigerant boils off during recovery, it absorbs heat, potentially freezing the water in the heat exchanger tubes. Circulating water prevents this freezing.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  11. Q11.To raise the pressure of a low-pressure system for leak detection without using nitrogen, you can:

    A.Run the compressor
    B.Circulate hot water through the tubes or use heating blankets
    C.Use a torch
    D.Add air
    BCirculate hot water through the tubes or use heating blankets

    Explanation: Heating the refrigerant (using warm water or heating blankets) raises the system pressure naturally, allowing leaks to be found without introducing nitrogen.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  12. Q12.A hydrostatic tube test kit is used to:

    A.Check for leaks in the chiller tubes
    B.Measure the refrigerant level
    C.Test the oil acidity
    D.Measure the water flow
    ACheck for leaks in the chiller tubes

    Explanation: A hydrostatic tube test kit determines if a specific tube in the heat exchanger is leaking.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  13. Q13.What is the maximum leak rate allowed for 'Comfort Cooling' chillers containing 50 lbs or more of refrigerant?

    A.5%
    B.10%
    C.15%
    D.20%
    B10%

    Explanation: Comfort cooling appliances (like chillers for AC) have a 10% annual leak rate threshold.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  14. Q14.High-efficiency purge units are designed to:

    A.Discharge refrigerant to the atmosphere
    B.Return a higher percentage of refrigerant to the system while removing air
    C.Run continuously
    D.Compress the air
    BReturn a higher percentage of refrigerant to the system while removing air

    Explanation: Modern high-efficiency purge units separate air from refrigerant more effectively, minimizing the amount of refrigerant vented with the air.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  15. Q15.When recharging a low-pressure system, you should introduce vapor first until the pressure reaches 16.9 inches Hg vacuum (saturation temp of 32°F) to prevent:

    A.The rupture disc from bursting
    B.The water in the tubes from freezing
    C.The compressor from starting
    D.The oil from foaming
    BThe water in the tubes from freezing

    Explanation: If liquid refrigerant is added into a deep vacuum, it will boil instantly, dropping the temperature below 32°F and freezing the water in the tubes. Vapor is added first to raise the pressure/temperature above freezing.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  16. Q16.ASHRAE Standard 15 requires that a machine room with a chiller must have:

    A.A refrigerant monitor and mechanical ventilation
    B.Air conditioning
    C.Windows
    D.A phone line
    AA refrigerant monitor and mechanical ventilation

    Explanation: ASHRAE 15 mandates a refrigerant sensor that activates an alarm and ventilation system if a leak is detected.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  17. Q17.If you suspect a leak in the water box of a chiller, you should:

    A.Check for refrigerant in the water (using litmus paper or detector)
    B.Add dye to the water
    C.Increase the water pressure
    D.Taste the water
    ACheck for refrigerant in the water (using litmus paper or detector)

    Explanation: Place the leak detector probe in the drain valve opening or check the water for refrigerant presence.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  18. Q18.The rupture disc on a low-pressure chiller is connected to:

    A.The suction line
    B.The evaporator
    C.The condenser or evaporator (low side)
    D.The compressor discharge
    CThe condenser or evaporator (low side)

    Explanation: The rupture disc is typically mounted on the evaporator or condenser shell to relieve excess pressure.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  19. Q19.When recovering refrigerant from a system with a major leak, you are only required to evacuate to:

    A.0 psig (Atmospheric pressure)
    B.25 inches Hg vacuum
    C.10 inches Hg vacuum
    D.500 microns
    A0 psig (Atmospheric pressure)

    Explanation: If a leak makes it impossible to reach the deep vacuum levels, you evacuate to 0 psig to prevent pulling air into the recovery tank.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  20. Q20.Excessive running of the purge unit generally indicates:

    A.The system is overcharged
    B.The system is leaking (pulling in air)
    C.The oil is low
    D.The condenser is dirty
    BThe system is leaking (pulling in air)

    Explanation: The purge unit's job is to remove air. If it runs frequently, it means air is constantly entering the system through a leak.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  21. Q21.Before disposing of a low-pressure appliance, the refrigerant must be recovered to:

    A.0 psig
    B.25 mm Hg absolute
    C.25 inches Hg vacuum
    D.10 psig
    B25 mm Hg absolute

    Explanation: Disposal requires the same evacuation level as repair: 25 mm Hg absolute.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  22. Q22.Type III appliances typically use which type of compressor?

    A.Reciprocating
    B.Scroll
    C.Rotary
    D.Centrifugal
    DCentrifugal

    Explanation: Low-pressure systems are almost exclusively large centrifugal chillers.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  23. Q23.When charging liquid refrigerant into a low-pressure system, the system pressure should be at least:

    A.16.9 inches Hg vacuum
    B.0 psig
    C.5 psig
    D.29 inches Hg vacuum
    A16.9 inches Hg vacuum

    Explanation: This corresponds to a saturation temperature of 36°F for R-123 (or 32°F generally), ensuring water won't freeze when liquid hits the tubes.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  24. Q24.If you are using a water-cooled recovery unit, you must:

    A.Connect it to the chiller water loop
    B.Use local municipal water
    C.Ensure the water pump is on
    D.Drain the water from the unit after use if there is a risk of freezing
    DDrain the water from the unit after use if there is a risk of freezing

    Explanation: Water left in the recovery unit condenser can freeze and burst the tubes if the unit is stored in a cold area or if recovery lowers the temperature significantly.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  25. Q25.What is the boiling point of R-11 at atmospheric pressure?

    A.74.9°F
    B.-21.6°F
    C.-41°F
    D.32°F
    A74.9°F

    Explanation: R-11 boils at approx 75°F. This is why it stays liquid at room temperature in an open container (though it evaporates).

    Join 1,000+ users passing the EPA 608 HVAC Certification

  26. Q26.A chiller's rupture disc vents the refrigerant to:

    A.The machine room
    B.The outdoors via a vent line
    C.A recovery tank
    D.The sewer
    BThe outdoors via a vent line

    Explanation: The discharge from a rupture disc must be piped outdoors to prevent filling the machine room with toxic/asphyxiating gas.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  27. Q27.During evacuation of a system with large amounts of water, it may be necessary to:

    A.Increase the pressure with nitrogen to prevent freezing
    B.Heat the system with heat lamps or blankets
    C.Use a smaller vacuum pump
    D.Stop the pump periodically
    BHeat the system with heat lamps or blankets

    Explanation: Heating the system helps boil off the water and prevents it from freezing into ice, which would stop the dehydration process.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  28. Q28.Which test is used to determine if a tube is leaking?

    A.Hydrostatic test
    B.Eddy current test
    C.Litmus paper test
    D.Soap bubble test
    AHydrostatic test

    Explanation: While eddy current tests check wall thickness, a hydrostatic test (pressurizing the tube) confirms if it leaks.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  29. Q29.For a low-pressure system, the high-pressure cut-out control is typically set to:

    A.10 psig
    B.15 psig
    C.25 psig
    D.100 psig
    A10 psig

    Explanation: The cut-out is set to 10 psig to shut down the compressor before the rupture disc blows at 15 psig.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  30. Q30.If you are repairing a leak in a chiller and you add 100 lbs of refrigerant, you must:

    A.Report it to the EPA immediately
    B.Calculate the leak rate to see if it exceeds the threshold
    C.Replace the entire charge
    D.Do nothing
    BCalculate the leak rate to see if it exceeds the threshold

    Explanation: Any time refrigerant is added to a regulated appliance (≥50 lbs), the leak rate must be calculated to determine compliance with leak repair regulations.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  31. Q31.What is the definition of a 'Refrigerant Monitor'?

    A.A device that measures system pressure
    B.A device that detects refrigerant concentrations in the air
    C.A device that tracks refrigerant inventory
    D.A person who watches the system
    BA device that detects refrigerant concentrations in the air

    Explanation: A refrigerant monitor senses refrigerant vapor in the machinery room air and triggers alarms/ventilation.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  32. Q32.When pressurizing a low-pressure system with nitrogen for a leak check, you should:

    A.Exceed 15 psig to find small leaks
    B.Never exceed 10 psig
    C.Use liquid nitrogen
    D.Disconnect the relief valve
    BNever exceed 10 psig

    Explanation: Exceeding 10 psig risks blowing the rupture disc (15 psig setting).

    Join 1,000+ users passing the EPA 608 HVAC Certification

  33. Q33.In a low-pressure chiller, the purge unit takes its suction from the:

    A.Top of the condenser
    B.Bottom of the condenser
    C.Evaporator
    D.Compressor discharge
    ATop of the condenser

    Explanation: Air and non-condensables collect at the top of the condenser (highest point, coolest gas), so the purge unit draws from there.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  34. Q34.Which of the following safety precautions should be followed for low-pressure systems?

    A.Wear gloves and safety goggles
    B.Avoid siphoning refrigerant by mouth
    C.Ensure proper ventilation
    D.All of the above
    DAll of the above

    Explanation: Standard safety protocols apply: PPE, ventilation, and safe handling.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  35. Q35.Under EPA regulations, an 'Initial Verification Test' is required:

    A.Before adding refrigerant
    B.After the repair is finished but before the system is recharged/repressurized
    C.After the system is running
    D.Only for industrial process refrigeration
    BAfter the repair is finished but before the system is recharged/repressurized

    Explanation: Wait, verification tests are done *after* repair. Initial: Before charging (vacuum/pressure test). Follow-up: After system is running. So 'After repair but before recharged' is the correct timing for Initial Verification.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  36. Q36.A typical advantage of low-pressure chillers is:

    A.They are small and portable
    B.They operate at very high efficiency
    C.They use R-410A
    D.They do not require water cooling
    BThey operate at very high efficiency

    Explanation: Centrifugal chillers (low pressure) are known for high efficiency in large cooling applications.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  37. Q37.When removing oil from a low-pressure system, the oil should be heated to:

    A.100°F
    B.130°F
    C.200°F
    D.It should not be heated
    B130°F

    Explanation: Heating oil to 130°F helps release dissolved refrigerant, reducing the amount of refrigerant disposed of with the oil.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  38. Q38.If a low-pressure appliance is converted to a high-pressure refrigerant, the rupture disc must be:

    A.Replaced with a higher pressure relief device
    B.Removed completely
    C.Adjusted
    D.Left alone
    AReplaced with a higher pressure relief device

    Explanation: High-pressure refrigerants operate well above 15 psig. The rupture disc must be replaced with a relief valve rated for the new design pressure.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  39. Q39.According to ASHRAE Standard 15, the use of a room sensor and alarm is required for:

    A.All refrigerants
    B.A1 refrigerants (like R-123)
    C.B1 refrigerants
    D.Any refrigerant safety group
    DAny refrigerant safety group

    Explanation: ASHRAE 15 requires sensors for all refrigerant safety groups (A1, B1, etc.) in machinery rooms.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  40. Q40.A 'Controlled Hot Water' method for pressurization uses:

    A.Boiling water
    B.Hot water regulated to not exceed the safety relief setting pressure
    C.Steam
    D.Tap water
    BHot water regulated to not exceed the safety relief setting pressure

    Explanation: Hot water is used to warm the refrigerant and raise pressure for leak checking, but it must be controlled so pressure doesn't pop the rupture disc.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  41. Q41.Identify the low-pressure refrigerant from the list below:

    A.R-22
    B.R-123
    C.R-134a
    D.R-407C
    BR-123

    Explanation: R-123 is the standard low-pressure replacement for R-11.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  42. Q42.The maximum test pressure for leak testing a low-pressure chiller with nitrogen is:

    A.5 psig
    B.10 psig
    C.20 psig
    D.30 psig
    B10 psig

    Explanation: 10 psig is the safe limit to avoid bursting the 15 psig rupture disc.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  43. Q43.After recovering the liquid, about how much refrigerant vapor remains in a 350-ton R-123 chiller?

    A.None
    B.10 lbs
    C.100 lbs
    D.500 lbs
    C100 lbs

    Explanation: A significant amount of refrigerant (approx 100 lbs in a large machine) remains as vapor after liquid recovery, which is why vapor recovery is mandatory.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  44. Q44.When should the water pumps be turned on during recovery?

    A.They should be off
    B.They should be on to circulate water and prevent freezing
    C.Only during vapor recovery
    D.Only during liquid recovery
    BThey should be on to circulate water and prevent freezing

    Explanation: Pumps should run to keep water moving through the tubes, preventing localized freezing as refrigerant boils off.

    Join 1,000+ users passing the EPA 608 HVAC Certification

  45. Q45.Recovery of refrigerant from a low-pressure appliance must start with:

    A.Vapor recovery
    B.Liquid recovery
    C.Oil recovery
    D.Nitrogen sweep
    BLiquid recovery

    Explanation: Always recover liquid first to reduce the volume quickly, then switch to vapor recovery.

    Join 1,000+ users passing the EPA 608 HVAC Certification