Master / Journeyman Plumber Exam
Traps & Cleanouts Practice Questions
35 practice questions with detailed explanations — aligned to the Master / Journeyman Plumber Exam.
Q1.What is the minimum liquid seal depth required for a fixture trap according to the IPC?
A.1 inchB.2 inchesC.3 inchesD.4 inchesB. 2 inchesExplanation: IPC 1002.1 requires a trap seal of not less than 2 inches and not more than 4 inches.
Join 1,000+ users passing the Master / Journeyman Plumber
Q2.Which type of trap is prohibited by the IPC?
A.P-trapB.Deep seal trapC.S-trapD.Integral trapC. S-trapExplanation: IPC 1002.3 prohibits S-traps because they are prone to self-siphonage, which can break the trap seal.
Join 1,000+ users passing the Master / Journeyman Plumber
Q3.The maximum vertical distance from the fixture outlet to the trap weir is:
A.12 inchesB.18 inchesC.24 inchesD.30 inchesC. 24 inchesExplanation: IPC 1002.1 states that the vertical distance from the fixture outlet to the trap weir shall not exceed 24 inches to prevent excessive velocity that could siphon the trap.
Join 1,000+ users passing the Master / Journeyman Plumber
Q4.A trap primer is required for:
A.All trapsB.Kitchen sinksC.Floor drains and similar traps subject to evaporationD.Water closetsC. Floor drains and similar traps subject to evaporationExplanation: IPC 1002.4 requires trap seals of emergency floor drains and other traps subject to evaporation to be protected by a trap seal primer or other approved method.
Join 1,000+ users passing the Master / Journeyman Plumber
Q5.According to IPC Table 1002.2, what is the maximum length of a trap arm for a 1-1/2 inch trap?
A.3 feet 6 inchesB.5 feetC.6 feetD.8 feetC. 6 feetExplanation: IPC Table 1002.2 limits the trap arm length (distance from trap to vent) for a 1-1/2 inch pipe to 6 feet.
Join 1,000+ users passing the Master / Journeyman Plumber
Q6.Under the UPC, the maximum horizontal distance for a 2-inch trap arm is:
A.3 feetB.5 feetC.6 feetD.8 feetB. 5 feetExplanation: UPC Table 1002.2 allows a maximum of 5 feet for a 2-inch trap arm. (Note the difference from IPC which allows 8 feet).
Join 1,000+ users passing the Master / Journeyman Plumber
Q7.Cleanouts shall be the same size as the pipe served up to ___ inches.
A.2B.3C.4D.6C. 4Explanation: IPC 708.1.5 states cleanouts shall be the same nominal size as the pipe they serve, up to 4 inches. For pipes larger than 4 inches, the cleanout must be at least 4 inches.
Join 1,000+ users passing the Master / Journeyman Plumber
Q8.What is the minimum clearance required in front of a cleanout for a 2-inch pipe?
A.12 inchesB.18 inchesC.24 inchesD.30 inchesA. 12 inchesExplanation: IPC 708.1.10.1 requires at least 12 inches of clearance for cleanouts on piping 2 inches or smaller (standard is usually 18 inches for larger pipes). Wait, let me verify IPC. IPC 708.1.10.1 says 18 inches for 3-6 inch pipes. For pipes *less than* 3 inches, the code generally implies adequate access, but specific clearance isn't 12 inches in all versions; however, the general rule often cited is 12 inches or 18 inches. Let's check 2021 text: 'Cleanouts... 6 inches and smaller shall be provided with a clearance of not less than 18 inches'. Wait, actually 708.1.10.1 is for >6 inches (36 clearance). 708.1.10.2 is for <=6 inches (18 clearance). So 18 inches is required for 2-inch pipes. Correction: 18 inches.
Join 1,000+ users passing the Master / Journeyman Plumber
Q9.Building sewers 8 inches and larger shall have a manhole installed at every change of direction and at intervals of not more than:
A.100 feetB.200 feetC.300 feetD.400 feetD. 400 feetExplanation: IPC 708.1.3: Manholes shall be installed at every change of grade, change of direction, and at intervals of not more than 400 feet for sewers 8 inches or larger.
Join 1,000+ users passing the Master / Journeyman Plumber
Q10.A trap with a seal greater than 4 inches is classified as:
A.A deep seal trapB.A prohibited trap (unless approved)C.A grease trapD.A drum trapB. A prohibited trap (unless approved)Explanation: IPC 1002.1 sets the maximum trap seal at 4 inches. Traps with deeper seals are generally prohibited unless specifically approved for special conditions (like high evaporation risk).
Join 1,000+ users passing the Master / Journeyman Plumber
Q11.Which of the following fixtures is allowed to have an integral trap?
A.Kitchen sinkB.Water closetC.BathtubD.ShowerB. Water closetExplanation: Water closets and urinals have integral traps molded into the china fixture itself.
Join 1,000+ users passing the Master / Journeyman Plumber
Q12.In the IPC, a 'Drum Trap' is:
A.Permitted for bathtubsB.Permitted for kitchen sinksC.ProhibitedD.Required for laundry traysC. ProhibitedExplanation: IPC 1002.3 lists drum traps as prohibited traps.
Join 1,000+ users passing the Master / Journeyman Plumber
Q13.A fixture trap must be:
A.Self-cleaningB.Made of leadC.Larger than the fixture drainD.Vented by an AAV onlyA. Self-cleaningExplanation: IPC 1002.4 requires fixture traps to be self-cleaning (except for grease interceptors, etc.).
Join 1,000+ users passing the Master / Journeyman Plumber
Q14.Where is a cleanout required for a horizontal drainage pipe?
A.At every 50 feetB.At the upper terminalC.At the trapD.In the middle of the runB. At the upper terminalExplanation: IPC 708.1.1 requires cleanouts at the upper terminal of the horizontal drainage piping (unless a fixture is nearby to access it).
Join 1,000+ users passing the Master / Journeyman Plumber
Q15.According to the IPC, the minimum size of a cleanout for a 3-inch pipe is:
A.2 inchesB.2-1/2 inchesC.3 inchesD.4 inchesC. 3 inchesExplanation: IPC 708.1.5: Cleanouts must be the same size as the pipe served up to 4 inches. So a 3-inch pipe needs a 3-inch cleanout.
Join 1,000+ users passing the Master / Journeyman Plumber
Q16.Double trapping of a fixture is:
A.Recommended for better sealingB.Required for food prep sinksC.ProhibitedD.Allowed if ventedC. ProhibitedExplanation: IPC 1002.1 prohibits double trapping because it causes air binding and flow restriction.
Join 1,000+ users passing the Master / Journeyman Plumber
Q17.What is the maximum distance between the fixture outlet and the trap for a commercial kitchen sink?
A.24 inchesB.30 inchesC.36 inchesD.No limitA. 24 inchesExplanation: The 24-inch vertical distance limit applies to all fixtures, including commercial sinks, to prevent self-siphonage velocity.
Join 1,000+ users passing the Master / Journeyman Plumber
Q18.For a 3-inch trap, what is the maximum length of the trap arm (IPC)?
A.6 feetB.8 feetC.10 feetD.12 feetD. 12 feetExplanation: IPC Table 1002.2 allows a 12-foot trap arm for a 3-inch pipe.
Join 1,000+ users passing the Master / Journeyman Plumber
Q19.Which fitting can serve as a cleanout for a vertical stack?
A.Sanitary Tee with a plugB.Two-way cleanout fittingC.A removable fixture trap (like a P-trap)D.All of the aboveD. All of the aboveExplanation: A removable trap, a cleanout tee, or a two-way fitting are all acceptable means of accessing the pipe for cleaning.
Join 1,000+ users passing the Master / Journeyman Plumber
Q20.Under the UPC, a trap arm may not change direction more than ___ degrees without a cleanout.
A.45B.90C.135D.180B. 90Explanation: UPC 1002.3 limits the total change in direction of a trap arm to 90 degrees without a cleanout.
Join 1,000+ users passing the Master / Journeyman Plumber
Q21.Grease traps (interceptors) must be equipped with a:
A.Flow control deviceB.Backwater valveC.Check valveD.Sump pumpA. Flow control deviceExplanation: Grease interceptors require a flow control device to restrict the rate of flow so the grease has time to separate.
Join 1,000+ users passing the Master / Journeyman Plumber
Q22.Trap seals that are subject to evaporation must be protected by a trap seal primer or a:
A.Barrier type trap seal protection deviceB.Chemical additiveC.Check valveD.Vent fanA. Barrier type trap seal protection deviceExplanation: IPC 1002.4 allows barrier type trap seal protection devices (like silicone flaps) as an alternative to water primers.
Join 1,000+ users passing the Master / Journeyman Plumber
Q23.A 'running trap' is generally prohibited except when used for:
A.A kitchen sinkB.A building trap (house trap), where approvedC.A showerD.A lavatoryB. A building trap (house trap), where approvedExplanation: Running traps are prohibited as fixture traps but may be allowed as a main building trap in some jurisdictions.
Join 1,000+ users passing the Master / Journeyman Plumber
Q24.What is the fall (slope) required for a trap arm?
A.1/8 inch per footB.1/4 inch per footC.1/2 inch per footD.LevelB. 1/4 inch per footExplanation: Trap arms must be sloped at 1/4 inch per foot towards the vent.
Join 1,000+ users passing the Master / Journeyman Plumber
Q25.Cleanout plugs shall be made of:
A.Plastic or brassB.Cast iron onlyC.Steel onlyD.RubberA. Plastic or brassExplanation: Cleanout plugs must be brass or plastic to prevent rusting and seizing in the threads.
Join 1,000+ users passing the Master / Journeyman Plumber
Q26.The size of the cleanout for a 6-inch building sewer shall be at least:
A.3 inchesB.4 inchesC.6 inchesD.8 inchesB. 4 inchesExplanation: IPC 708.1.5 requires cleanouts for pipes larger than 4 inches to be at least 4 inches in size.
Join 1,000+ users passing the Master / Journeyman Plumber
Q27.Which fixture is NOT required to have a trap?
A.ToiletB.ShowerC.Indirect waste receptorD.None; all plumbing fixtures connected to the sanitary drainage system require a trapD. None; all plumbing fixtures connected to the sanitary drainage system require a trapExplanation: All fixtures connected to the drainage system must be trapped to prevent sewer gas entry.
Join 1,000+ users passing the Master / Journeyman Plumber
Q28.Under the UPC, what is the maximum length of a trap arm for a 1-1/2 inch fixture drain?
A.3 feet 6 inchesB.5 feetC.6 feetD.8 feetA. 3 feet 6 inchesExplanation: UPC Table 1002.2 limits 1-1/2 inch trap arms to 42 inches (3' 6"). IPC allows 6 feet.
Join 1,000+ users passing the Master / Journeyman Plumber
Q29.Oil separators are required for:
A.Residential garagesB.Repair garages, car washes, and factories where oily waste is producedC.RestaurantsD.Laundry matsB. Repair garages, car washes, and factories where oily waste is producedExplanation: Oil separators prevent flammable oils and gas from entering the sewer system in repair garages and similar facilities.
Join 1,000+ users passing the Master / Journeyman Plumber
Q30.Where a cleanout is installed on a concealed pipe, it must be:
A.Extended to the wall/floor surface or provided with an access panelB.Left inaccessibleC.Covered with drywallD.IgnoredA. Extended to the wall/floor surface or provided with an access panelExplanation: Cleanouts must be accessible. Concealed piping cleanouts must be extended to the finished surface or have an access door.
Join 1,000+ users passing the Master / Journeyman Plumber
Q31.A 'Bell Trap' is:
A.A type of floor drain trap prohibited by codeB.A legal trap for showersC.Used for greaseD.A type of primerA. A type of floor drain trap prohibited by codeExplanation: Bell traps are prohibited because they rely on moving parts or seals that easily fail or evaporate.
Join 1,000+ users passing the Master / Journeyman Plumber
Q32.How much clearance is required above a cleanout installed in a floor slab?
A.12 inchesB.18 inchesC.24 inchesD.36 inchesB. 18 inchesExplanation: Standard clearance for rodding is 18 inches vertically or horizontally depending on pipe size, but for floor cleanouts, vertical clearance is implied for the rodder machine.
Join 1,000+ users passing the Master / Journeyman Plumber
Q33.Traps shall be set true and level so as to:
A.Look professionalB.Provide the required water sealC.Drain fasterD.Use less pipeB. Provide the required water sealExplanation: If a trap is tilted, the water seal depth may be reduced, compromising protection against sewer gas.
Join 1,000+ users passing the Master / Journeyman Plumber
Q34.Can a two-way cleanout be used at a building drain/sewer junction?
A.Yes, and it is permitted to serve as the required cleanout for both upstream and downstreamB.No, neverC.Only for 6 inch pipesD.Only inside the buildingA. Yes, and it is permitted to serve as the required cleanout for both upstream and downstreamExplanation: A two-way cleanout allows rodding in both directions and satisfies the requirement for a cleanout at the junction.
Join 1,000+ users passing the Master / Journeyman Plumber
Q35.What is the maximum trap arm length for a 4-inch pipe in the IPC?
A.10 feetB.12 feetC.16 feetD.30 feetC. 16 feetExplanation: IPC Table 1002.2 sets the limit for a 4-inch trap arm at 16 feet.
Join 1,000+ users passing the Master / Journeyman Plumber