Journeyman Electrician Exam
Grounding & Bonding Essentials (Article 250) Practice Questions
10 practice questions with detailed explanations — aligned to the Journeyman Electrician Exam.
Master Grounding & Bonding Essentials (Article 250) to boost your score on the Journeyman Electrician Exam. Each question below mirrors the style and difficulty of real exam questions, complete with detailed explanations so you understand the why behind every answer. Work through all 10 questions, review any that trip you up, and use the related topics below to round out your preparation.
Q1.On the electrician exam, what is the key difference between grounding and bonding?
A.They are two words for the same connectionB.Grounding connects a system or equipment to earth; bonding connects metal parts together to form an effective ground-fault current pathC.Bonding connects to earth; grounding ties enclosures togetherD.Grounding applies only to DC systems✓B. Grounding connects a system or equipment to earth; bonding connects metal parts together to form an effective ground-fault current pathExplanation: Per NEC Article 100, grounding is the connection to earth (or to a conductive body serving in place of earth), while bonding is the connection of metallic parts to establish electrical continuity and an effective ground-fault current path (250.4(A)(3)). The exam frequently tests this distinction: earth itself is NOT an effective fault-clearing path.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q2.What is the minimum size copper grounding electrode conductor for a service with 3/0 AWG copper service-entrance conductors?
A.8 AWGB.6 AWGC.4 AWGD.2 AWG✓C. 4 AWGExplanation: Per NEC Table 250.66, service-entrance conductors of 3/0 AWG copper (or 250 kcmil aluminum) require a minimum 4 AWG copper grounding electrode conductor. Memorize Table 250.66 ranges for the journeyman exam.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q3.A grounding electrode conductor connecting to a concrete-encased electrode (Ufer) is never required to be larger than:
A.6 AWG copperB.4 AWG copperC.2 AWG copperD.1/0 AWG copper✓A. 6 AWG copperExplanation: Per NEC 250.66(B), where the GEC connects to a concrete-encased electrode, that portion is not required to be larger than 4 AWG copper. For a connection to a ground rod (250.66(A)) the limit is 6 AWG copper. Know each exception separately.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q4.The portion of the grounding electrode conductor that is the sole connection to a single ground rod is never required to be larger than:
A.8 AWG copperB.6 AWG copperC.4 AWG copperD.2 AWG copper✓B. 6 AWG copperExplanation: Per NEC 250.66(A), the GEC to a single rod, pipe, or plate electrode need not be larger than 6 AWG copper (or 4 AWG aluminum). This is a very commonly tested figure.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q5.Where a single ground rod does not achieve 25 ohms or less to earth, the NEC requires:
A.Nothing further; 25 ohms is only a recommendationB.Augmenting with one additional electrodeC.Replacing the serviceD.Three additional rods✓B. Augmenting with one additional electrodeExplanation: Per NEC 250.53(A)(2) Exception, a single rod with a resistance of 25 ohms or less may stand alone; otherwise it must be augmented by one additional electrode. Installing two rods spaced at least 6 ft apart is the common way to satisfy this without measuring resistance.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q6.What is the minimum required separation between two driven ground rods used together?
A.3 feetB.5 feetC.6 feetD.10 feet✓C. 6 feetExplanation: Per NEC 250.53(A)(3), rods, pipes, and plate electrodes must be spaced at least 6 ft (1.8 m) apart. Spacing them closer reduces the benefit of the second rod because their effective resistance areas overlap.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q7.The minimum size of a copper equipment grounding conductor for a circuit protected by a 60-ampere overcurrent device is:
A.12 AWGB.10 AWGC.8 AWGD.6 AWG✓B. 10 AWGExplanation: Per NEC Table 250.122, a 60-ampere overcurrent device requires a minimum 10 AWG copper equipment grounding conductor. Note 250.122 sizes the EGC by the rating of the overcurrent device, not the load.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q8.At a service, the connection between the grounded (neutral) conductor and the equipment grounding system is made by the:
A.Grounding electrode conductorB.Main bonding jumperC.Equipment grounding conductorD.Supply-side bonding jumper✓B. Main bonding jumperExplanation: Per NEC 250.24(B) and 250.28, the main bonding jumper connects the grounded (neutral) conductor to the equipment grounding terminal/enclosure at the service. Downstream of the service, neutrals and grounds must be kept separate (250.142).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q9.In a separately derived system, the connection between the derived neutral and the equipment grounding conductor is the:
A.Main bonding jumperB.System bonding jumperC.Grounding electrode conductorD.Bonding bushing✓B. System bonding jumperExplanation: Per NEC 250.30(A)(1), a separately derived system (e.g., a transformer secondary) uses a system bonding jumper to connect the derived grounded conductor to the equipment grounding conductor at a single point. The term differs from the service main bonding jumper.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q10.Metal water piping in a building must be bonded, and where used as a grounding electrode it is required to be supplemented because:
A.Copper pipe corrodes too quicklyB.Plastic repair sections can interrupt the electrode path, so it cannot be the sole electrodeC.Water pipe is never permitted as an electrodeD.It exceeds 25 ohms by definition✓B. Plastic repair sections can interrupt the electrode path, so it cannot be the sole electrodeExplanation: Per NEC 250.53(D)(2), a metal underground water pipe electrode must be supplemented by an additional electrode because future plastic repairs or meter replacements can break electrical continuity. The interior metal water piping must also be bonded per 250.104(A).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime