Master / Journeyman Plumber Exam

Backflow Prevention Practice Questions

30 practice questions with detailed explanations — aligned to the Master / Journeyman Plumber Exam.

  1. Q1.What is the minimum air gap required between the supply outlet and the flood level rim of a fixture?

    A.1 inch
    B.Twice the diameter of the supply pipe
    C.Three times the diameter of the supply pipe
    D.6 inches
    BTwice the diameter of the supply pipe

    Explanation: IPC 608.15.1 requires the air gap to be at least twice the diameter of the effective opening of the supply pipe, but never less than 1 inch.

    Join 1,000+ users passing the Master / Journeyman Plumber

  2. Q2.Which backflow preventer provides the highest level of protection against high-hazard contamination?

    A.Double Check Valve Assembly (DCVA)
    B.Pressure Vacuum Breaker (PVB)
    C.Reduced Pressure Zone Assembly (RPZ)
    D.Atmospheric Vacuum Breaker (AVB)
    CReduced Pressure Zone Assembly (RPZ)

    Explanation: The RPZ (Reduced Pressure Principle Backflow Preventer) protects against both backpressure and backsiphonage for high-hazard (health hazard) applications.

    Join 1,000+ users passing the Master / Journeyman Plumber

  3. Q3.An Atmospheric Vacuum Breaker (AVB) shall NOT be installed where:

    A.It is subject to continuous pressure for more than 12 hours
    B.It is installed 6 inches above the flood rim
    C.It protects a hose bibb
    D.It is used for a sink sprayer
    AIt is subject to continuous pressure for more than 12 hours

    Explanation: AVBs are not designed for continuous pressure (pressure applied for more than 12 hours in a 24-hour period) because the air inlet valve may stick closed.

    Join 1,000+ users passing the Master / Journeyman Plumber

  4. Q4.A Pressure Vacuum Breaker (PVB) must be installed at least ___ inches above the highest downstream piping or outlet.

    A.6
    B.12
    C.18
    D.24
    B12

    Explanation: IPC 608.13.5 requires PVBs to be installed a minimum of 12 inches above the highest downstream usage to function correctly.

    Join 1,000+ users passing the Master / Journeyman Plumber

  5. Q5.Which device is approved for protecting against backpressure?

    A.Atmospheric Vacuum Breaker
    B.Pressure Vacuum Breaker
    C.Double Check Valve Assembly
    D.Hose connection vacuum breaker
    CDouble Check Valve Assembly

    Explanation: Vacuum breakers (AVB, PVB) only protect against backsiphonage. Double checks (DCVA) and RPZs protect against backpressure and backsiphonage.

    Join 1,000+ users passing the Master / Journeyman Plumber

  6. Q6.Testable backflow prevention assemblies must be tested:

    A.Every 6 months
    B.Annually
    C.Every 3 years
    D.Only upon installation
    BAnnually

    Explanation: IPC 312.10 requires annual testing and inspection of backflow prevention assemblies to ensure they are working properly.

    Join 1,000+ users passing the Master / Journeyman Plumber

  7. Q7.A hose bibb vacuum breaker (ASSE 1011) is required on:

    A.Water heater drains
    B.Sill cocks and hose bibbs where a hose can be attached
    C.Shower arms
    D.Lavatory faucets
    BSill cocks and hose bibbs where a hose can be attached

    Explanation: IPC 608.13.6 (and 608.15.4.2) requires vacuum breakers on hose connections to prevent backsiphonage from hoses left in puddles or chemical buckets.

    Join 1,000+ users passing the Master / Journeyman Plumber

  8. Q8.The Double Check Valve Assembly (DCVA) is typically suitable for:

    A.High hazard applications
    B.Low hazard (non-health hazard) applications
    C.Chemical injection systems
    D.Any application
    BLow hazard (non-health hazard) applications

    Explanation: DCVAs are approved only for low-hazard applications (pollutants, not contaminants) because they do not have a relief valve to dump water if both checks fail.

    Join 1,000+ users passing the Master / Journeyman Plumber

  9. Q9.Backsiphonage is caused by:

    A.Pressure in the downstream piping exceeding the supply pressure
    B.Negative or reduced pressure in the supply piping
    C.A pump downstream
    D.Heating the water
    BNegative or reduced pressure in the supply piping

    Explanation: Backsiphonage occurs when a vacuum (negative pressure) in the supply line sucks contaminated water back into the potable system (e.g., water main break).

    Join 1,000+ users passing the Master / Journeyman Plumber

  10. Q10.Carbonated beverage dispensers must be protected by:

    A.A vented dual check valve with an atmospheric vent
    B.A single check valve
    C.An air gap only
    D.A hose bibb vacuum breaker
    AA vented dual check valve with an atmospheric vent

    Explanation: IPC 608.16.1 requires a backflow preventer for carbonators (ASSE 1022 - vented dual check) to prevent CO2 gas from mixing with copper pipe, which creates toxic copper carbonate.

    Join 1,000+ users passing the Master / Journeyman Plumber

  11. Q11.An RPZ assembly shall NOT be installed:

    A.In a vertical position
    B.In a pit or vault where it could be submerged
    C.Indoors
    D.Above the floor
    BIn a pit or vault where it could be submerged

    Explanation: IPC 608.13.2 requires RPZs to be installed where the relief port cannot be submerged. Pits are prohibited because floodwater could enter the potable supply through the open relief port.

    Join 1,000+ users passing the Master / Journeyman Plumber

  12. Q12.A barometric loop must rise at least ___ feet above the highest fixture it supplies.

    A.10
    B.25
    C.35
    D.50
    C35

    Explanation: A barometric loop protects against backsiphonage by rising 35 feet, effectively exceeding the atmospheric lift capability of a vacuum.

    Join 1,000+ users passing the Master / Journeyman Plumber

  13. Q13.Lawn irrigation systems with chemical injection pumps are considered:

    A.Low hazard
    B.High hazard
    C.No hazard
    D.Aesthetic only
    BHigh hazard

    Explanation: Injecting fertilizers or pesticides makes the system High Hazard, requiring an RPZ or PVB (if no backpressure).

    Join 1,000+ users passing the Master / Journeyman Plumber

  14. Q14.Which marking on a vacuum breaker indicates the minimum installation height?

    A.UPC
    B.ASSE
    C.C-L or Critical Level
    D.Flow Arrow
    CC-L or Critical Level

    Explanation: The 'C-L' (Critical Level) mark must be at the required distance (6" or 12") above the flood level rim.

    Join 1,000+ users passing the Master / Journeyman Plumber

  15. Q15.A connection between a potable water supply and a non-potable source is defined as a:

    A.Cross-connection
    B.Bypass
    C.Manifold
    D.Fixture branch
    ACross-connection

    Explanation: A cross-connection is any physical link between the potable water system and any other substance or non-potable source.

    Join 1,000+ users passing the Master / Journeyman Plumber

  16. Q16.Stop-and-waste valves (valves with a drain opening) shall not be installed:

    A.Above ground
    B.Underground
    C.In hot water lines
    D.In basements
    BUnderground

    Explanation: IPC 608.8 prohibits stop-and-waste valves underground because contaminated groundwater can enter the potable system through the drain port when the pressure drops.

    Join 1,000+ users passing the Master / Journeyman Plumber

  17. Q17.An Atmospheric Vacuum Breaker (AVB) must be installed at least ___ inches above the flood level rim of the fixture.

    A.1
    B.6
    C.12
    D.18
    B6

    Explanation: IPC 608.13.6 requires AVBs to be at least 6 inches above the flood level rim.

    Join 1,000+ users passing the Master / Journeyman Plumber

  18. Q18.Backflow protection for a fire sprinkler system utilizing chemical additives (antifreeze) requires a:

    A.Double Check Valve
    B.Reduced Pressure Zone Assembly
    C.Single Check Valve
    D.Vacuum Breaker
    BReduced Pressure Zone Assembly

    Explanation: Chemical additives create a high hazard (toxic), mandating an RPZ. (Systems with water only can often use a DCVA).

    Join 1,000+ users passing the Master / Journeyman Plumber

  19. Q19.The relief port of an RPZ must discharge to:

    A.A sanitary sewer directly
    B.An indirect waste receptor via an air gap
    C.The floor without a drain
    D.A bucket
    BAn indirect waste receptor via an air gap

    Explanation: The discharge must be visible and connect indirectly (air gap) to the drainage system to prevent sewer backup into the device.

    Join 1,000+ users passing the Master / Journeyman Plumber

  20. Q20.Spill-resistant Vacuum Breakers (SVB) are designed for:

    A.High backpressure
    B.Continuous pressure applications where spillage is undesirable (indoor use)
    C.Underground use
    D.Toxic chemicals only
    BContinuous pressure applications where spillage is undesirable (indoor use)

    Explanation: SVBs (ASSE 1056) reduce water spillage upon startup and are rated for continuous pressure, unlike AVBs.

    Join 1,000+ users passing the Master / Journeyman Plumber

  21. Q21.Which of the following is considered a 'Low Hazard' (Pollution)?

    A.Sewage
    B.Food coloring or nontoxic dye
    C.Chemical fertilizer
    D.Radioactive material
    BFood coloring or nontoxic dye

    Explanation: Low hazard substances are objectionable but not dangerous to health (e.g., food products).

    Join 1,000+ users passing the Master / Journeyman Plumber

  22. Q22.A potable water connection to a residential boiler (without chemicals) is typically protected by a:

    A.Dual check valve with intermediate atmospheric vent (ASSE 1012)
    B.Single check valve
    C.Vacuum breaker
    D.Air gap
    ADual check valve with intermediate atmospheric vent (ASSE 1012)

    Explanation: ASSE 1012 devices are standard for residential boiler feed lines where no chemicals are used.

    Join 1,000+ users passing the Master / Journeyman Plumber

  23. Q23.Where non-potable water is used for flushing toilets (gray water), the piping must be:

    A.Copper
    B.Painted purple or marked 'Non-potable water'
    C.White PVC
    D.Galvanized
    BPainted purple or marked 'Non-potable water'

    Explanation: IPC 608.9 requires non-potable water systems to be identified by purple pipe or purple tags/tape to prevent cross-connection.

    Join 1,000+ users passing the Master / Journeyman Plumber

  24. Q24.Backpressure backflow can be caused by:

    A.A broken water main
    B.High water demand from fire fighting
    C.Boiler pressure exceeding supply pressure
    D.Draining the system
    CBoiler pressure exceeding supply pressure

    Explanation: Backpressure happens when the downstream pressure is higher than the supply pressure (e.g., pumps, boilers, elevation).

    Join 1,000+ users passing the Master / Journeyman Plumber

  25. Q25.Laboratory faucets with hose connections must be protected by:

    A.A standard check valve
    B.A vacuum breaker
    C.A trap primer
    D.An expansion tank
    BA vacuum breaker

    Explanation: Hose connections always present a backsiphonage risk and require vacuum breaker protection.

    Join 1,000+ users passing the Master / Journeyman Plumber

  26. Q26.Double Check Valve Assemblies (DCVA) consist of:

    A.Two independently acting check valves
    B.Two check valves and a relief port
    C.One check valve and one air inlet
    D.Two gate valves only
    ATwo independently acting check valves

    Explanation: DCVAs have two redundant check valves. Unlike RPZs, they do NOT have a relief zone that opens to atmosphere.

    Join 1,000+ users passing the Master / Journeyman Plumber

  27. Q27.Which backflow preventer must be removed or protected during freezing conditions if installed outdoors?

    A.PVB
    B.RPZ
    C.DCVA
    D.All of the above
    DAll of the above

    Explanation: All backflow devices holding water can freeze and crack. They must be protected (heated enclosure) or removed/drained.

    Join 1,000+ users passing the Master / Journeyman Plumber

  28. Q28.A 'Break Tank' is used to:

    A.Store hot water
    B.Create an air gap separation between the potable supply and a booster pump
    C.Catch leaks
    D.Break down sewage
    BCreate an air gap separation between the potable supply and a booster pump

    Explanation: A break tank is a non-pressurized tank with an air gap on the inlet, used to supply pumps without risking backflow to the mains.

    Join 1,000+ users passing the Master / Journeyman Plumber

  29. Q29.The critical level of a vacuum breaker on a urinal flushometer must be installed at least ___ inches above the spill line of the bowl.

    A.4
    B.6
    C.12
    D.18
    B6

    Explanation: IPC 608.13.6 requires a minimum of 6 inches for AVBs/vacuum breakers on flushometers.

    Join 1,000+ users passing the Master / Journeyman Plumber

  30. Q30.Deck-mounted bath/shower faucets with a hand-held spray must have:

    A.A check valve in the hose
    B.An integral vacuum breaker or ASSE 1014 protection
    C.No protection
    D.A filter
    BAn integral vacuum breaker or ASSE 1014 protection

    Explanation: Handheld sprays can fall into the tub water (submerged inlet), creating a backsiphonage hazard. They require vacuum breaker protection.