Q1.The 'Building Sewer' typically starts at a point ___ outside the building wall.
A.12 inchesB.30 inches (2.5 feet)C.5 feetD.10 feetB. 30 inches (2.5 feet)Explanation: IPC Definitions state the Building Drain extends to 30 inches exterior of the building wall. Beyond that point, it becomes the Building Sewer.
Join 1,000+ users passing the Master / Journeyman Plumber
Q2.What is the minimum size of a building sewer?
A.3 inchesB.4 inchesC.6 inchesD.Based on the building drain size, but not less than 4 inchesD. Based on the building drain size, but not less than 4 inchesExplanation: IPC 710.1 requires the building sewer to be at least the size of the building drain. While 3 inch is theoretically possible by hydraulic calculation, practically and historically most codes mandate a 4-inch minimum for the main sewer lateral.
Join 1,000+ users passing the Master / Journeyman Plumber
Q3.A cleanout is required on the building sewer at the junction with the building drain and at intervals not exceeding ___ feet.
A.50B.75C.100D.150C. 100Explanation: IPC 708.1.2 requires cleanouts every 100 feet in horizontal drainage lines, including the sewer.
Join 1,000+ users passing the Master / Journeyman Plumber
Q4.Building sewers 8 inches and larger require:
A.Manholes at every change of directionB.Copper pipingC.Double check valvesD.No cleanoutsA. Manholes at every change of directionExplanation: IPC 708.1.3 mandates manholes for larger sewers (8 inch+) at changes of direction or grade.
Join 1,000+ users passing the Master / Journeyman Plumber
Q5.The minimum slope for a 4-inch building sewer is:
A.1/16 inch per footB.1/8 inch per footC.1/4 inch per footD.1/2 inch per footB. 1/8 inch per footExplanation: IPC 704.1 allows 1/8 inch per foot for pipes 3 inches (where approved) or 4 inches and larger. Standard practice often targets 1/4 inch, but 1/8 inch is the code minimum for 4 inch.
Join 1,000+ users passing the Master / Journeyman Plumber
Q6.No building sewer shall be installed in the same trench as water service piping unless:
A.They are the same materialB.The water pipe is at least 12 inches above the top of the sewer and placed on a solid shelfC.They are painted blue and greenD.The trench is 6 feet deepB. The water pipe is at least 12 inches above the top of the sewer and placed on a solid shelfExplanation: IPC 603.2 allows common trenching only if this separation and shelf requirement is met to protect the water supply from sewage leaks.
Join 1,000+ users passing the Master / Journeyman Plumber
Q7.When a building sewer is installed in filled or unstable ground, it shall be made of:
A.PVCB.Cast IronC.ConcreteD.Any approved material, but laid on a concrete pad or pilesD. Any approved material, but laid on a concrete pad or pilesExplanation: IPC 306.2 requires piping in unstable ground to be supported on a concrete pad, piles, or other approved methods to prevent settling and breakage.
Join 1,000+ users passing the Master / Journeyman Plumber
Q8.Under UPC, the building sewer must have a cleanout located within ___ feet of the property line.
A.2B.5C.10D.It is not requiredA. 2Explanation: UPC 719.1 requires a cleanout within 2 feet of the property line (often called a property line cleanout or test tee).
Join 1,000+ users passing the Master / Journeyman Plumber
Q9.Existing building sewers may be used for new building plumbing ONLY if:
A.They are cast ironB.They are inspected and tested to show they are in good condition and adequate sizeC.The owner requests itD.They are less than 10 years oldB. They are inspected and tested to show they are in good condition and adequate sizeExplanation: IPC 701.2 allows reuse of existing sewers only after examination and testing confirm they comply with code requirements.
Join 1,000+ users passing the Master / Journeyman Plumber
Q10.Backwater valves used in a building sewer must be:
A.AccessibleB.Buried permanentlyC.Made of leadD.Normally closedA. AccessibleExplanation: IPC 715.5 requires backwater valves to be accessible for inspection and maintenance (cleaning).
Join 1,000+ users passing the Master / Journeyman Plumber
Q11.The connection of the building sewer to the public sewer must be made:
A.At a 90-degree angleB.At the manhole onlyC.Using a wye or other approved fitting to direct flowD.By drilling a hole and gluingC. Using a wye or other approved fitting to direct flowExplanation: Connections must use fittings that direct flow (wyes/saddles) and must be gas-tight and watertight.
Join 1,000+ users passing the Master / Journeyman Plumber
Q12.For testing a building sewer with water, the static water head must be at least:
A.5 feetB.10 feetC.15 feetD.20 feetB. 10 feetExplanation: IPC 312.6 requires a 10-foot head of water for testing gravity sewer piping.
Join 1,000+ users passing the Master / Journeyman Plumber
Q13.Forced main sewers (pumped sewage) piping shall be:
A.Larger than gravity sewersB.Pressure rated pipe (e.g., PVC SDR 21 or 26)C.Standard DWV Schedule 40D.Copper onlyB. Pressure rated pipe (e.g., PVC SDR 21 or 26)Explanation: Pump discharge piping must be pressure rated to handle the pump head pressure; standard foam-core DWV is generally not acceptable for pressure.
Join 1,000+ users passing the Master / Journeyman Plumber
Q14.If the public sewer is not available, the building sewer shall connect to:
A.A storm drainB.A drywellC.A private sewage disposal system (septic system)D.A holding tankC. A private sewage disposal system (septic system)Explanation: IPC 701.2 requires connection to an approved private sewage disposal system (septic) if public sewer is unavailable.
Join 1,000+ users passing the Master / Journeyman Plumber
Q15.Can a building sewer run under another building?
A.Yes, alwaysB.No, building sewers cannot pass under or through another building unless they serve that buildingC.Only if encased in concreteD.Only if it is cast ironB. No, building sewers cannot pass under or through another building unless they serve that buildingExplanation: Typically, codes prohibit running one building's sewer under another building due to maintenance and easement issues.
Join 1,000+ users passing the Master / Journeyman Plumber
Q16.Tracer wire is required for:
A.Cast iron sewersB.Non-metallic (plastic) underground sanitary sewersC.Copper water linesD.Vent stacksB. Non-metallic (plastic) underground sanitary sewersExplanation: While mandated heavily for gas, many local amendments and good practice (often referenced in IPC 306) require tracer wire for plastic sewers to allow locating them later.
Join 1,000+ users passing the Master / Journeyman Plumber
Q17.The minimum cover (burial depth) for a building sewer is:
A.6 inchesB.12 inchesC.Determined by the local code official (frost depth protection)D.36 inchesC. Determined by the local code official (frost depth protection)Explanation: IPC 305.4.1 leaves the specific depth to the local jurisdiction (to be inserted in the code text) based on local frost lines.
Join 1,000+ users passing the Master / Journeyman Plumber
Q18.Mechanical joints in underground sewer piping (e.g., ferncos with shear rings) must be:
A.Supported properly to prevent shearB.Left looseC.GluedD.Wrapped in tapeA. Supported properly to prevent shearExplanation: Underground couplings, especially shielded ones, need proper bedding and support to prevent the weight of the earth from shearing the pipe connection.
Join 1,000+ users passing the Master / Journeyman Plumber
Q19.Sewer lines must be laid on:
A.RocksB.A firm bed of approved granular materialC.Wood blocksD.Frozen groundB. A firm bed of approved granular materialExplanation: IPC 306.2.3 requires proper bedding (sand, gravel) to support the pipe along its entire length.
Join 1,000+ users passing the Master / Journeyman Plumber
Q20.In the IPC, a building sewer cleanout is required for changes of direction greater than:
A.22.5 degreesB.45 degreesC.60 degreesD.90 degreesB. 45 degreesExplanation: IPC 708.1.4 requires cleanouts at changes of direction greater than 45 degrees.
Join 1,000+ users passing the Master / Journeyman Plumber
Q21.Relining existing sewers (CIPP) requires:
A.Approval by the code officialB.Removing the old pipeC.A structural engineerD.Nothing, it's unregulatedA. Approval by the code officialExplanation: Rehabilitation of piping systems (relining) is permitted but subject to approval (IPC 716) to ensure the reduced diameter still meets flow requirements.
Join 1,000+ users passing the Master / Journeyman Plumber
Q22.Septic tanks must be sized based on:
A.The lot sizeB.The number of bedrooms and soil percolation rateC.The number of bathrooms onlyD.The water pressureB. The number of bedrooms and soil percolation rateExplanation: Private sewage disposal sizing (IPC Chapter 13 or local health code) is typically based on the potential occupant load (bedrooms) and the soil's ability to absorb effluent.
Join 1,000+ users passing the Master / Journeyman Plumber
Q23.When transitioning from Building Drain to Building Sewer, the fitting used is typically a:
A.Sanitary TeeB.Cleanout Tee or WyeC.ReducerD.Check ValveB. Cleanout Tee or WyeExplanation: A cleanout is required at the junction (IPC 708.1.1), so a cleanout fitting is installed.
Join 1,000+ users passing the Master / Journeyman Plumber
Q24.Using IPC Table 710.1(1), what is the DFU capacity of a 6-inch building sewer sloped at 1/4 inch per foot?
A.500 DFUB.620 DFUC.840 DFUD.No limitC. 840 DFUExplanation: This specific value may vary by exact table edition, but typically a 6-inch sewer at 1/4 inch slope carries approx 840 DFU.
Join 1,000+ users passing the Master / Journeyman Plumber
Q25.Leak testing of a building sewer with air requires a pressure of:
A.5 psiB.10 psiC.50 psiD.Air testing plastic piping is prohibited in some jurisdictions, but generally 5 psi for 15 minutes if allowedA. 5 psiExplanation: IPC 312.3 allows air tests at 5 psi for 15 minutes (though many manufacturers prohibit air testing PVC due to shrapnel risk).