  1. Q1.The 'Building Sewer' typically starts at a point ___ outside the building wall.

    A.12 inches
    B.30 inches (2.5 feet)
    C.5 feet
    D.10 feet
    B30 inches (2.5 feet)

    Explanation: IPC Definitions state the Building Drain extends to 30 inches exterior of the building wall. Beyond that point, it becomes the Building Sewer.

    Join 1,000+ users passing the Master / Journeyman Plumber

  2. Q2.What is the minimum size of a building sewer?

    A.3 inches
    B.4 inches
    C.6 inches
    D.Based on the building drain size, but not less than 4 inches
    DBased on the building drain size, but not less than 4 inches

    Explanation: IPC 710.1 requires the building sewer to be at least the size of the building drain. While 3 inch is theoretically possible by hydraulic calculation, practically and historically most codes mandate a 4-inch minimum for the main sewer lateral.

    Join 1,000+ users passing the Master / Journeyman Plumber

  3. Q3.A cleanout is required on the building sewer at the junction with the building drain and at intervals not exceeding ___ feet.

    A.50
    B.75
    C.100
    D.150
    C100

    Explanation: IPC 708.1.2 requires cleanouts every 100 feet in horizontal drainage lines, including the sewer.

    Join 1,000+ users passing the Master / Journeyman Plumber

  4. Q4.Building sewers 8 inches and larger require:

    A.Manholes at every change of direction
    B.Copper piping
    C.Double check valves
    D.No cleanouts
    AManholes at every change of direction

    Explanation: IPC 708.1.3 mandates manholes for larger sewers (8 inch+) at changes of direction or grade.

    Join 1,000+ users passing the Master / Journeyman Plumber

  5. Q5.The minimum slope for a 4-inch building sewer is:

    A.1/16 inch per foot
    B.1/8 inch per foot
    C.1/4 inch per foot
    D.1/2 inch per foot
    B1/8 inch per foot

    Explanation: IPC 704.1 allows 1/8 inch per foot for pipes 3 inches (where approved) or 4 inches and larger. Standard practice often targets 1/4 inch, but 1/8 inch is the code minimum for 4 inch.

    Join 1,000+ users passing the Master / Journeyman Plumber

  6. Q6.No building sewer shall be installed in the same trench as water service piping unless:

    A.They are the same material
    B.The water pipe is at least 12 inches above the top of the sewer and placed on a solid shelf
    C.They are painted blue and green
    D.The trench is 6 feet deep
    BThe water pipe is at least 12 inches above the top of the sewer and placed on a solid shelf

    Explanation: IPC 603.2 allows common trenching only if this separation and shelf requirement is met to protect the water supply from sewage leaks.

    Join 1,000+ users passing the Master / Journeyman Plumber

  7. Q7.When a building sewer is installed in filled or unstable ground, it shall be made of:

    A.PVC
    B.Cast Iron
    C.Concrete
    D.Any approved material, but laid on a concrete pad or piles
    DAny approved material, but laid on a concrete pad or piles

    Explanation: IPC 306.2 requires piping in unstable ground to be supported on a concrete pad, piles, or other approved methods to prevent settling and breakage.

    Join 1,000+ users passing the Master / Journeyman Plumber

  8. Q8.Under UPC, the building sewer must have a cleanout located within ___ feet of the property line.

    A.2
    B.5
    C.10
    D.It is not required
    A2

    Explanation: UPC 719.1 requires a cleanout within 2 feet of the property line (often called a property line cleanout or test tee).

    Join 1,000+ users passing the Master / Journeyman Plumber

  9. Q9.Existing building sewers may be used for new building plumbing ONLY if:

    A.They are cast iron
    B.They are inspected and tested to show they are in good condition and adequate size
    C.The owner requests it
    D.They are less than 10 years old
    BThey are inspected and tested to show they are in good condition and adequate size

    Explanation: IPC 701.2 allows reuse of existing sewers only after examination and testing confirm they comply with code requirements.

    Join 1,000+ users passing the Master / Journeyman Plumber

  10. Q10.Backwater valves used in a building sewer must be:

    A.Accessible
    B.Buried permanently
    C.Made of lead
    D.Normally closed
    AAccessible

    Explanation: IPC 715.5 requires backwater valves to be accessible for inspection and maintenance (cleaning).

    Join 1,000+ users passing the Master / Journeyman Plumber

  11. Q11.The connection of the building sewer to the public sewer must be made:

    A.At a 90-degree angle
    B.At the manhole only
    C.Using a wye or other approved fitting to direct flow
    D.By drilling a hole and gluing
    CUsing a wye or other approved fitting to direct flow

    Explanation: Connections must use fittings that direct flow (wyes/saddles) and must be gas-tight and watertight.

    Join 1,000+ users passing the Master / Journeyman Plumber

  12. Q12.For testing a building sewer with water, the static water head must be at least:

    A.5 feet
    B.10 feet
    C.15 feet
    D.20 feet
    B10 feet

    Explanation: IPC 312.6 requires a 10-foot head of water for testing gravity sewer piping.

    Join 1,000+ users passing the Master / Journeyman Plumber

  13. Q13.Forced main sewers (pumped sewage) piping shall be:

    A.Larger than gravity sewers
    B.Pressure rated pipe (e.g., PVC SDR 21 or 26)
    C.Standard DWV Schedule 40
    D.Copper only
    BPressure rated pipe (e.g., PVC SDR 21 or 26)

    Explanation: Pump discharge piping must be pressure rated to handle the pump head pressure; standard foam-core DWV is generally not acceptable for pressure.

    Join 1,000+ users passing the Master / Journeyman Plumber

  14. Q14.If the public sewer is not available, the building sewer shall connect to:

    A.A storm drain
    B.A drywell
    C.A private sewage disposal system (septic system)
    D.A holding tank
    CA private sewage disposal system (septic system)

    Explanation: IPC 701.2 requires connection to an approved private sewage disposal system (septic) if public sewer is unavailable.

    Join 1,000+ users passing the Master / Journeyman Plumber

  15. Q15.Can a building sewer run under another building?

    A.Yes, always
    B.No, building sewers cannot pass under or through another building unless they serve that building
    C.Only if encased in concrete
    D.Only if it is cast iron
    BNo, building sewers cannot pass under or through another building unless they serve that building

    Explanation: Typically, codes prohibit running one building's sewer under another building due to maintenance and easement issues.

    Join 1,000+ users passing the Master / Journeyman Plumber

  16. Q16.Tracer wire is required for:

    A.Cast iron sewers
    B.Non-metallic (plastic) underground sanitary sewers
    C.Copper water lines
    D.Vent stacks
    BNon-metallic (plastic) underground sanitary sewers

    Explanation: While mandated heavily for gas, many local amendments and good practice (often referenced in IPC 306) require tracer wire for plastic sewers to allow locating them later.

    Join 1,000+ users passing the Master / Journeyman Plumber

  17. Q17.The minimum cover (burial depth) for a building sewer is:

    A.6 inches
    B.12 inches
    C.Determined by the local code official (frost depth protection)
    D.36 inches
    CDetermined by the local code official (frost depth protection)

    Explanation: IPC 305.4.1 leaves the specific depth to the local jurisdiction (to be inserted in the code text) based on local frost lines.

    Join 1,000+ users passing the Master / Journeyman Plumber

  18. Q18.Mechanical joints in underground sewer piping (e.g., ferncos with shear rings) must be:

    A.Supported properly to prevent shear
    B.Left loose
    C.Glued
    D.Wrapped in tape
    ASupported properly to prevent shear

    Explanation: Underground couplings, especially shielded ones, need proper bedding and support to prevent the weight of the earth from shearing the pipe connection.

    Join 1,000+ users passing the Master / Journeyman Plumber

  19. Q19.Sewer lines must be laid on:

    A.Rocks
    B.A firm bed of approved granular material
    C.Wood blocks
    D.Frozen ground
    BA firm bed of approved granular material

    Explanation: IPC 306.2.3 requires proper bedding (sand, gravel) to support the pipe along its entire length.

    Join 1,000+ users passing the Master / Journeyman Plumber

  20. Q20.In the IPC, a building sewer cleanout is required for changes of direction greater than:

    A.22.5 degrees
    B.45 degrees
    C.60 degrees
    D.90 degrees
    B45 degrees

    Explanation: IPC 708.1.4 requires cleanouts at changes of direction greater than 45 degrees.

    Join 1,000+ users passing the Master / Journeyman Plumber

  21. Q21.Relining existing sewers (CIPP) requires:

    A.Approval by the code official
    B.Removing the old pipe
    C.A structural engineer
    D.Nothing, it's unregulated
    AApproval by the code official

    Explanation: Rehabilitation of piping systems (relining) is permitted but subject to approval (IPC 716) to ensure the reduced diameter still meets flow requirements.

    Join 1,000+ users passing the Master / Journeyman Plumber

  22. Q22.Septic tanks must be sized based on:

    A.The lot size
    B.The number of bedrooms and soil percolation rate
    C.The number of bathrooms only
    D.The water pressure
    BThe number of bedrooms and soil percolation rate

    Explanation: Private sewage disposal sizing (IPC Chapter 13 or local health code) is typically based on the potential occupant load (bedrooms) and the soil's ability to absorb effluent.

    Join 1,000+ users passing the Master / Journeyman Plumber

  23. Q23.When transitioning from Building Drain to Building Sewer, the fitting used is typically a:

    A.Sanitary Tee
    B.Cleanout Tee or Wye
    C.Reducer
    D.Check Valve
    BCleanout Tee or Wye

    Explanation: A cleanout is required at the junction (IPC 708.1.1), so a cleanout fitting is installed.

    Join 1,000+ users passing the Master / Journeyman Plumber

  24. Q24.Using IPC Table 710.1(1), what is the DFU capacity of a 6-inch building sewer sloped at 1/4 inch per foot?

    A.500 DFU
    B.620 DFU
    C.840 DFU
    D.No limit
    C840 DFU

    Explanation: This specific value may vary by exact table edition, but typically a 6-inch sewer at 1/4 inch slope carries approx 840 DFU.

    Join 1,000+ users passing the Master / Journeyman Plumber

  25. Q25.Leak testing of a building sewer with air requires a pressure of:

    A.5 psi
    B.10 psi
    C.50 psi
    D.Air testing plastic piping is prohibited in some jurisdictions, but generally 5 psi for 15 minutes if allowed
    A5 psi

    Explanation: IPC 312.3 allows air tests at 5 psi for 15 minutes (though many manufacturers prohibit air testing PVC due to shrapnel risk).