Storm Drainage Practice Questions

25 practice questions with detailed explanations — aligned to the Master / Journeyman Plumber Exam.

  1. Q1.Roof drains shall have domed strainers that extend not less than ___ inches above the surface of the roof.

    A.2
    B.3
    C.4
    D.6
    C4

    Explanation: IPC 1105.1 requires roof drain strainers to extend at least 4 inches above the roof surface to prevent debris blockage.

    Join 1,000+ users passing the Master / Journeyman Plumber

  2. Q2.Secondary (emergency) roof drains or scuppers are required:

    A.Only in hurricane zones
    B.Where the roof perimeter construction extends above the roof in such a manner that water will be entrapped (parapet walls)
    C.On all roofs regardless of design
    D.Only for flat roofs over 5,000 sq ft
    BWhere the roof perimeter construction extends above the roof in such a manner that water will be entrapped (parapet walls)

    Explanation: IPC 1101.7 requires secondary drainage where water can be trapped if the primary drains clog, preventing roof collapse.

    Join 1,000+ users passing the Master / Journeyman Plumber

  3. Q3.The size of vertical conductors and leaders is based on:

    A.The diameter of the drain
    B.The height of the building
    C.The maximum projected roof area and the rainfall rate
    D.The number of windows
    CThe maximum projected roof area and the rainfall rate

    Explanation: IPC 1106.1 sizes storm piping based on the square footage of the roof area served and the local 100-year hourly rainfall rate.

    Join 1,000+ users passing the Master / Journeyman Plumber

  4. Q4.A 'Leader' is defined as:

    A.An interior vertical drainage pipe
    B.An exterior drainage pipe for conveying storm water from roof or gutter drains
    C.The main storm sewer
    D.A horizontal pipe
    BAn exterior drainage pipe for conveying storm water from roof or gutter drains

    Explanation: IPC Definitions differentiate between a 'Conductor' (inside the building) and a 'Leader' (outside/exterior downspout).

    Join 1,000+ users passing the Master / Journeyman Plumber

  5. Q5.Storm water shall NOT be drained into:

    A.A storm sewer
    B.A combined sewer (where permitted)
    C.Sewers intended for sewage only (sanitary sewers)
    D.A dedicated drywell
    CSewers intended for sewage only (sanitary sewers)

    Explanation: IPC 1101.2 prohibits connecting storm water (rain) to sanitary sewers intended only for sewage, as it overloads the treatment plant.

    Join 1,000+ users passing the Master / Journeyman Plumber

  6. Q6.Secondary roof drain systems shall discharge:

    A.Into the primary storm drain
    B.To the sanitary sewer
    C.Separately from the primary system to a visible location (above grade)
    D.Into a sump pump
    CSeparately from the primary system to a visible location (above grade)

    Explanation: IPC 1101.7 requires secondary drains to discharge separately and visibly so building occupants become aware that the primary system is blocked.

    Join 1,000+ users passing the Master / Journeyman Plumber

  7. Q7.The area of the roof strainers (inlet area) must be at least ___ times the area of the conductor or leader to which it connects.

    A.1
    B.1.5
    C.2
    D.3
    B1.5

    Explanation: IPC 1105.1 states the inlet area above the roof must be not less than 1.5 times the area of the pipe inlet.

    Join 1,000+ users passing the Master / Journeyman Plumber

  8. Q8.Subsoil drains (French drains) shall be piped to:

    A.The sanitary sewer
    B.A storm drain, an approved watercourse, or a sump
    C.The street curb directly
    D.The water meter pit
    BA storm drain, an approved watercourse, or a sump

    Explanation: IPC 1113.1 requires subsoil drains to discharge to an approved location like a storm sewer or sump; never the sanitary sewer unless specifically approved.

    Join 1,000+ users passing the Master / Journeyman Plumber

  9. Q9.Scuppers used for secondary roof drainage shall have an opening dimension of not less than:

    A.2 inches
    B.3 inches
    C.4 inches
    D.6 inches
    C4 inches

    Explanation: IPC 1101.7 requires scupper openings to be at least 4 inches high.

    Join 1,000+ users passing the Master / Journeyman Plumber

  10. Q10.Sizing of storm drains is based on the rainfall rate of a storm of ___ duration and ___ return period.

    A.1 hour, 10 year
    B.1 hour, 100 year
    C.24 hour, 50 year
    D.15 minutes, 100 year
    B1 hour, 100 year

    Explanation: IPC 1106.1 bases calculations on the 100-year hourly rainfall rate.

    Join 1,000+ users passing the Master / Journeyman Plumber

  11. Q11.Controlled flow roof drain systems are permitted when:

    A.The roof structure is designed for the maximum retention water weight
    B.The pipes are too small
    C.It is a residential house
    D.The owner wants to save money
    AThe roof structure is designed for the maximum retention water weight

    Explanation: IPC 1110.1 allows controlled flow (slow drainage) only if the roof can structurally support the accumulated water load during a storm.

    Join 1,000+ users passing the Master / Journeyman Plumber

  12. Q12.When calculating roof area for storm drain sizing, vertical walls that drain onto the roof must be calculated as:

    A.Zero area
    B.50% of the wall area added to the roof area
    C.100% of the wall area added
    D.Only if they have windows
    B50% of the wall area added to the roof area

    Explanation: IPC 1106.4 requires 50% of the area of any vertical wall that diverts water to the roof to be added to the projected roof area calculation.

    Join 1,000+ users passing the Master / Journeyman Plumber

  13. Q13.Which material is acceptable for inside storm conductor piping?

    A.PVC (Schedule 40)
    B.Cast Iron
    C.ABS
    D.All of the above
    DAll of the above

    Explanation: IPC Table 1102.4 lists PVC, ABS, Cast Iron, Copper, and others as approved materials for building storm sewers and conductors.

    Join 1,000+ users passing the Master / Journeyman Plumber

  14. Q14.Are cleanouts required on storm drain systems?

    A.No, never
    B.Yes, the same as sanitary systems (every 100 feet, change of direction)
    C.Only at the base of stacks
    D.Only on the roof
    BYes, the same as sanitary systems (every 100 feet, change of direction)

    Explanation: IPC 1104.1 requires cleanouts on storm drainage systems essentially following the same rules as sanitary drainage (708).

    Join 1,000+ users passing the Master / Journeyman Plumber

  15. Q15.Backwater valves are required in storm drainage systems when:

    A.The roof is flat
    B.The storm sewer is combined with sanitary
    C.Piping is subject to backflow from the public sewer system
    D.Always required
    CPiping is subject to backflow from the public sewer system

    Explanation: IPC 1101.9 requires backwater valves where the system is subject to backflow/surcharge from the public sewer.

    Join 1,000+ users passing the Master / Journeyman Plumber

  16. Q16.A flat roof has a total area of 4,000 sq ft. The rainfall rate is 3 inches/hour. What is the equivalent GPM load?

    A.100 GPM
    B.125 GPM
    C.200 GPM
    D.400 GPM
    B125 GPM

    Explanation: Formula: GPM = (Area x Rainfall) / 96. (4000 x 3) / 96 = 12000 / 96 = 125 GPM.

    Join 1,000+ users passing the Master / Journeyman Plumber

  17. Q17.Secondary roof drains must discharge at a point:

    A.Below the primary drain
    B.Above grade and visible to building occupants
    C.Into the sanitary sewer
    D.Into a drywell
    BAbove grade and visible to building occupants

    Explanation: The discharge must be visible so maintenance personnel know a blockage exists in the primary system.

    Join 1,000+ users passing the Master / Journeyman Plumber

  18. Q18.When connecting a subsoil drain to a storm drain, it must connect through:

    A.A backwater valve
    B.A cleanout
    C.An open sump
    D.A wye fitting only
    AA backwater valve

    Explanation: IPC 1113.1.3: Subsoil drains connecting to a storm sewer shall be protected by a backwater valve to prevent the sewer from flooding the foundation.

    Join 1,000+ users passing the Master / Journeyman Plumber

  19. Q19.The minimum size of a subsoil drain pipe is:

    A.2 inches
    B.3 inches
    C.4 inches
    D.6 inches
    C4 inches

    Explanation: IPC 1111.1 requires subsoil drains (foundation drains) to be not less than 4 inches in diameter.

    Join 1,000+ users passing the Master / Journeyman Plumber

  20. Q20.Are traps required on storm drains?

    A.Yes, always
    B.No, traps are prohibited
    C.Traps are required only if the drain connects to a combined sewer or where sewer gas could escape
    D.Only on roof drains
    CTraps are required only if the drain connects to a combined sewer or where sewer gas could escape

    Explanation: IPC 1103.1 states storm drains do not require traps unless they connect to a combined sewer (carrying sanitary waste) or where necessary to prevent sewer gas escape.

    Join 1,000+ users passing the Master / Journeyman Plumber

  21. Q21.Roof drains must be spaced not more than ___ feet apart?

    A.20
    B.50
    C.100
    D.There is no specific spacing requirement in the IPC, sizing is based on area
    DThere is no specific spacing requirement in the IPC, sizing is based on area

    Explanation: The IPC dictates sizing based on area and flow, not arbitrary spacing distances. Placement depends on roof slope and structural design.

    Join 1,000+ users passing the Master / Journeyman Plumber

  22. Q22.Vertical conductors and leaders shall be sized based on:

    A.IPC Table 1106.2(1)
    B.The size of the gutter
    C.The height of the building
    D.Always 4 inches
    AIPC Table 1106.2(1)

    Explanation: Sizing is strictly tabular based on the max roof area and rainfall rate (Table 1106.2(1)).

    Join 1,000+ users passing the Master / Journeyman Plumber

  23. Q23.Which material is prohibited for underground storm building sewers?

    A.ABS Plastic
    B.Cast Iron
    C.Aluminum
    D.PVC
    CAluminum

    Explanation: Aluminum piping is prohibited in soils due to rapid corrosion.

    Join 1,000+ users passing the Master / Journeyman Plumber

  24. Q24.The sizing of gutters (semicircular) is based on:

    A.Slope, Roof Area, and Rainfall Rate
    B.Depth only
    C.Length only
    D.Color
    ASlope, Roof Area, and Rainfall Rate

    Explanation: IPC Table 1106.6 requires knowing the slope, the roof area being drained, and the rainfall rate to select the diameter.

    Join 1,000+ users passing the Master / Journeyman Plumber

  25. Q25.When a combined sewer system is used, the building storm drain and building sanitary drain must:

    A.Combine inside the building
    B.Combine outside the building (at the property line or building sewer)
    C.Never combine
    D.Use an AAV
    BCombine outside the building (at the property line or building sewer)

    Explanation: Typically, storm and sanitary building drains remain separate inside the building and combine only at the building sewer or public sewer connection point to prevent sewer gas backup into storm drains inside.

    Join 1,000+ users passing the Master / Journeyman Plumber