Skip to main content

Journeyman Electrician Exam

Conductors & Ampacity Practice Questions

57 practice questions with detailed explanations — aligned to the Journeyman Electrician Exam.

Master Conductors & Ampacity to boost your score on the Journeyman Electrician Exam. Each question below mirrors the style and difficulty of real exam questions, complete with detailed explanations so you understand the why behind every answer. Work through all 57 questions, review any that trip you up, and use the related topics below to round out your preparation.

  1. Q1.What is the allowable ampacity of a 10 AWG THHN copper conductor at 30°C ambient temperature?

    A.30 Amps
    B.35 Amps
    C.40 Amps
    D.55 Amps
    C40 Amps

    Explanation: Per NEC Table 310.16, a 10 AWG THHN copper conductor has an ampacity of 40 Amps in the 90°C column. THHN is rated at 90°C, and when the termination temperature rating permits, this full ampacity applies. Note that NEC 240.4(D) limits overcurrent protection for 10 AWG copper to 30A, but the conductor ampacity itself is 40A.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  2. Q2.When applying temperature correction factors, which column of Table 310.16 is used for THWN-2 conductors?

    A.60°C
    B.75°C
    C.90°C
    D.105°C
    C90°C

    Explanation: THWN-2 is a 90°C rated conductor (wet or dry). Therefore, the 90°C column is used for ampacity and derating calculations (though termination limits apply at the end).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  3. Q3.If 4 current-carrying conductors are installed in a raceway, the allowable ampacity must be reduced to ____ of the values in Table 310.16.

    A.80%
    B.70%
    C.50%
    D.40%
    A80%

    Explanation: NEC Table 310.15(C)(1) requires an 80% adjustment factor for 4-6 current-carrying conductors.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  4. Q4.What is the minimum size copper conductor permitted for a 200A service dwelling unit using the 83% rule (Table 310.12)?

    A.3/0 AWG
    B.2/0 AWG
    C.1/0 AWG
    D.4/0 AWG
    B2/0 AWG

    Explanation: NEC 310.12 allows dwelling services to be sized at 83% of the service rating. 200 * 0.83 = 166A. Table 310.16 (75°C) shows 2/0 AWG copper is rated 175A. (So 2/0 is correct).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  5. Q5.Terminations for circuits rated over 100A are generally assumed to be rated for ____ unless marked otherwise.

    A.60°C
    B.75°C
    C.90°C
    D.105°C
    B75°C

    Explanation: NEC 110.14(C)(1)(b) states that for circuits rated over 100A, conductors shall be used at the 75°C ampacity.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  6. Q6.What is the ampacity adjustment factor for 8 current-carrying conductors installed in a single raceway?

    A.80%
    B.70%
    C.50%
    D.40%
    B70%

    Explanation: NEC Table 310.15(C)(1) requires a 70% adjustment factor for 7-9 current-carrying conductors.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  7. Q7.The neutral conductor of a 3-wire circuit consisting of two phase wires and the neutral of a 4-wire, 3-phase, Wye-connected system is considered a current-carrying conductor.

    A.True
    B.False
    C.Only if harmonics are present
    D.Only if it is bare
    ATrue

    Explanation: NEC 310.15(E)(2) states that in a 3-wire circuit consisting of 2 phase conductors and the neutral of a 4-wire, 3-phase wye system, the common conductor (neutral) carries approximately the same current as the line-to-neutral load and **shall be counted**.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  8. Q8.What is the minimum size copper conductor permitted to be connected in parallel?

    A.1 AWG
    B.1/0 AWG
    C.2/0 AWG
    D.250 kcmil
    B1/0 AWG

    Explanation: NEC 310.10(G)(1) requires that conductors connected in parallel be 1/0 AWG or larger.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  9. Q9.On a 4-wire, delta-connected system where the midpoint of one phase winding is grounded (High-Leg Delta), the conductor with the higher phase voltage to ground must be identified by _____ color.

    A.Red
    B.Black
    C.Orange
    D.Blue
    COrange

    Explanation: NEC 110.15 requires the 'high leg' (208V to ground on a 120/240V delta) to be identified by an orange outer finish or effective means.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  10. Q10.Unless specifically permitted, the overcurrent protection for 12 AWG copper wire shall not exceed:

    A.15 Amps
    B.20 Amps
    C.25 Amps
    D.30 Amps
    B20 Amps

    Explanation: NEC 240.4(D)(5) restricts the overcurrent protection for 12 AWG copper small conductors to 20 Amps, regardless of the higher ampacity values in Table 310.16.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  11. Q11.Determine the corrected ampacity of a 6 AWG THWN-2 copper conductor (90°C rated) installed in an ambient temperature of 125°F (52°C).

    A.55.0 Amps
    B.57.0 Amps
    C.75.0 Amps
    D.40.5 Amps
    B57.0 Amps

    Explanation: Step 1: Table 310.16 Ampacity for 6 AWG THWN-2 (90°C col) = 75A. Step 2: Table 310.15(B)(1) Correction Factor for 51-55°C (123-131°F) in 90°C column is 0.76. Step 3: 75A * 0.76 = 57.0 Amps.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  12. Q12.Which insulation type is suitable for use in wet locations at 90°C?

    A.THHN
    B.THHW
    C.THWN-2
    D.TBS
    CTHWN-2

    Explanation: Table 310.4(A) lists THWN-2 as suitable for dry and wet locations at 90°C. Standard THWN is 75°C wet. THHN is dry only.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  13. Q13.Conductors installed in raceways must be stranded if they are size _____ or larger.

    A.10 AWG
    B.8 AWG
    C.6 AWG
    D.4 AWG
    B8 AWG

    Explanation: NEC 310.3(A) requires conductors 8 AWG and larger to be stranded when installed in raceways.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  14. Q14.What is the maximum operating temperature for Type TW insulation?

    A.60°C
    B.75°C
    C.90°C
    D.105°C
    A60°C

    Explanation: Table 310.4(A) lists Type TW insulation with a maximum operating temperature of 60°C.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  15. Q15.Where raceways are exposed to direct sunlight on a roof, the ampacity adjustment requires:

    A.Adding 30°F to the ambient temperature.
    B.Adding 60°F to the ambient temperature.
    C.Using the ambient temperature inside the conduit only.
    D.No specific adder; use the actual outdoor ambient temperature.
    DNo specific adder; use the actual outdoor ambient temperature.

    Explanation: The specific 'temperature adder' table for rooftop conduits was removed in NEC 2020. NEC 2023 310.15(B)(2) simply requires using the ambient temperature (which on a roof is the outdoor temp, potentially very high, but no fixed adder table is used anymore).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  16. Q16.A grounded conductor (neutral) of size 6 AWG or smaller must be identified by:

    A.A continuous white or gray outer finish.
    B.Phase tape at the termination.
    C.Stripping the insulation.
    D.A green stripe.
    AA continuous white or gray outer finish.

    Explanation: NEC 200.6(A) requires grounded conductors 6 AWG and smaller to be identified by a continuous white or gray outer finish (or three white stripes). Tape is allowed only for larger wires.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  17. Q17.If you have 6 current-carrying 10 AWG THHN copper conductors in a conduit at 30°C, what is the allowable ampacity of each?

    A.32 Amps
    B.28 Amps
    C.35 Amps
    D.40 Amps
    A32 Amps

    Explanation: 10 AWG THHN ampacity = 40A (90°C col). Adjustment for 6 conductors (Table 310.15(C)(1)) is 80%. 40A * 0.80 = 32 Amps.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  18. Q18.Calculate the voltage drop for a 20A load on a 120V circuit using 12 AWG solid copper wire (approx 2 ohms/1000 ft) with a one-way distance of 100 feet.

    A.2 Volts
    B.4 Volts
    C.8 Volts
    D.10 Volts
    C8 Volts

    Explanation: Formula: VD = 2 * K * L * I / CM (or using R). VD = 2 * I * R. Resistance for 100 ft (one way) -> Total wire length is 200 ft (hot + neutral). 200 ft * (2 ohms/1000 ft) = 0.4 ohms. V = I * R = 20A * 0.4 ohms = 8 Volts.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  19. Q19.Service-entrance conductors shall not be smaller than _____ copper.

    A.10 AWG
    B.8 AWG
    C.6 AWG
    D.4 AWG
    B8 AWG

    Explanation: NEC 230.23(B) states that the minimum size for service-drop conductors is 8 AWG copper (or 6 AWG aluminum).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  20. Q20.When parallel conductors are used, they must be:

    A.The same color
    B.The same length, material, size, and insulation type
    C.Installed in separate raceways
    D.Sized 2/0 AWG or larger
    BThe same length, material, size, and insulation type

    Explanation: NEC 310.10(G)(2) lists the characteristics that must be identical for parallel conductors: same length, same conductor material, same size in circular mil area, same insulation type, and same termination manner.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  21. Q21.What is the ampacity of 1/0 AWG Aluminum XHHW-2 at 75°C termination rating?

    A.120 Amps
    B.135 Amps
    C.150 Amps
    D.100 Amps
    A120 Amps

    Explanation: Table 310.16. 1/0 Aluminum. 75°C column: 120 Amps. (90°C is 135A, but question specifies 75°C termination rating applicability).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  22. Q22.Flexible cords and cables shall be protected against overcurrent in accordance with their ampacities as specified in:

    A.Table 310.16
    B.Table 400.5(A)(1)
    C.Table 310.15(B)(1)
    D.Table 250.122
    BTable 400.5(A)(1)

    Explanation: NEC 240.5(A) refers to Table 400.5(A)(1) (and (A)(2)) for the ampacity of flexible cords and cables.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  23. Q23.Type USE cable is identified for:

    A.Underground Service Entrance
    B.Underground Sub-Feed
    C.Universal Service Entrance
    D.Utility Service Entry
    AUnderground Service Entrance

    Explanation: NEC 338.2 defines Type USE as Underground Service-Entrance cable.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  24. Q24.When derating for more than 3 current-carrying conductors, which of the following is NOT counted?

    A.A grounding electrode conductor
    B.A neutral conductor carrying unbalanced current only
    C.A phase conductor
    D.A neutral conductor in a circuit with high harmonic currents
    BA neutral conductor carrying unbalanced current only

    Explanation: NEC 310.15(E)(1) states that a neutral conductor that carries only the unbalanced current from other conductors of the same circuit shall not be required to be counted.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  25. Q25.For a 100A feeder supplying a non-continuous load, what is the minimum size copper THHN conductor (75°C terminations)?

    A.4 AWG
    B.3 AWG
    C.2 AWG
    D.1 AWG
    B3 AWG

    Explanation: Table 310.16. 3 AWG Copper (75°C) is rated 100 Amps. 4 AWG is rated 85 Amps.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  26. Q26.The ampacity of Type NM cable (Romex) shall be determined in accordance with the _____ column of Table 310.16.

    A.60°C
    B.75°C
    C.90°C
    D.105°C
    A60°C

    Explanation: NEC 334.80 states that the ampacity of Type NM cable shall be determined in accordance with the 60°C column of Table 310.16 (even though the conductors are rated 90°C).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  27. Q27.Underground Feeder and Branch-Circuit Cable (Type UF) used as an interior wiring method in a dry location must be installed in accordance with which Article?

    A.Article 340
    B.Article 334
    C.Article 338
    D.Article 310
    BArticle 334

    Explanation: NEC 340.10(4) states that Type UF cable installed as nonmetallic-sheathed cable (interior) shall comply with Article 334 (NM Cable).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  28. Q28.What is the minimum bending radius for a 3-inch diameter shielded conductor (Medium Voltage)?

    A.8 times the outer diameter
    B.12 times the outer diameter
    C.10 times the outer diameter
    D.5 times the outer diameter
    B12 times the outer diameter

    Explanation: NEC 300.34 requires a minimum bending radius of 12 times the overall diameter for shielded conductors.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  29. Q29.When calculating ampacity for a bundle of cables 24 inches long (a nipple), what adjustment factor applies?

    A.60%
    B.50%
    C.40%
    D.No adjustment factor is required
    DNo adjustment factor is required

    Explanation: NEC 310.15(C)(1) Note 2 (or Exception) states that adjustment factors do not apply to nipples that do not exceed 24 inches in length.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  30. Q30.A 500 kcmil copper conductor is terminated in a switchboard. What is the minimum wire-bending space required at the terminal?

    A.4 inches
    B.5 inches
    C.6 inches
    D.8 inches
    C6 inches

    Explanation: Table 312.6(B) requires 6 inches of wire-bending space for a single 500 kcmil conductor per terminal.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  31. Q31.Conductors with insulation marked 'sunlight resistant' are required for:

    A.All outdoor installations
    B.All exposed outdoor installations
    C.Conductors exposed to direct rays of the sun
    D.Underground installations
    CConductors exposed to direct rays of the sun

    Explanation: NEC 310.10(D) states that conductors and cables exposed to direct rays of the sun must be listed/marked as 'sunlight resistant'.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  32. Q32.What is the ampacity of a 12 AWG THHN copper conductor in a raceway with 9 current-carrying conductors at 30°C?

    A.21 Amps
    B.24 Amps
    C.30 Amps
    D.20 Amps
    A21 Amps

    Explanation: Per NEC Table 310.16, a 12 AWG THHN copper conductor has a base ampacity of 30A at 90°C. When a raceway contains 7 to 9 current-carrying conductors, NEC Table 310.15(C)(1) requires an adjustment factor of 70%. Adjusted ampacity: 30A × 0.70 = 21 Amps. The overcurrent device is limited to 20A per NEC 240.4(D), but the calculated ampacity of the conductors is 21A.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  33. Q33.Aluminum conductors shall be terminated with:

    A.Standard copper lugs
    B.Connectors marked 'AL/CU'
    C.Connectors marked 'CU' only
    D.Twist-on wire nuts not rated for AL
    BConnectors marked 'AL/CU'

    Explanation: NEC 110.14 requires terminals used with aluminum conductors to be identified for the material (marked AL or AL/CU).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  34. Q34.Is it permissible to install control conductors (voltage < 600V) in the same raceway as power conductors (< 600V)?

    A.No, never.
    B.Yes, if all conductors have an insulation rating equal to at least the maximum circuit voltage applied to any conductor.
    C.Yes, if there is a divider.
    D.Yes, if the control conductors are shielded.
    BYes, if all conductors have an insulation rating equal to at least the maximum circuit voltage applied to any conductor.

    Explanation: NEC 300.3(C)(1) permits conductors of different systems (600V or less) to occupy the same enclosure or raceway if all conductors have an insulation rating equal to at least the maximum circuit voltage applied to any conductor.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  35. Q35.Calculate the circular mils required for a conductor to carry 100A given a specific resistance. The formula CM = (K * I * L) / VD is used for:

    A.Voltage Drop
    B.Ampacity Derating
    C.Short Circuit Current
    D.Conduit Fill
    AVoltage Drop

    Explanation: This is the standard Voltage Drop formula (rearranged to solve for Circular Mils).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  36. Q36.NEC 2026 Article 310.3(D) was updated to require that conductors 8 AWG and larger installed in a raceway must be stranded, EXCEPT for:

    A.Service conductors
    B.Grounding electrode conductors where specifically permitted
    C.Conductors in flexible conduit
    D.Aluminum conductors
    BGrounding electrode conductors where specifically permitted

    Explanation: NEC 2026 Article 310.3(D) requires conductors 8 AWG and larger to be stranded. A key exception applies to grounding electrode conductors where specifically permitted under Article 250 (see NEC 250.62), which allows solid conductors in certain GEC applications. This exception recognizes that GECs serve a different function than current-carrying conductors.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  37. Q37.What is the maximum operating temperature of XHHW-2 insulation?

    A.60°C
    B.75°C
    C.90°C
    D.105°C
    C90°C

    Explanation: Table 310.4(A) lists XHHW-2 as 90°C rated for wet and dry locations.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  38. Q38.The minimum size conductor for a voltage of 5,000 Volts is:

    A.14 AWG
    B.10 AWG
    C.8 AWG
    D.6 AWG
    D6 AWG

    Explanation: For conductors operating at voltages above 2,000V (medium voltage), NEC Article 310 and specifically NEC 310.60 govern cable requirements. Medium voltage cables are governed by product standards that set the minimum conductor size at 8 AWG copper or 6 AWG aluminum. For a 5,000V system, 6 AWG is the applicable minimum size referenced in NEC Table 310.60 product tables and Article 310.3 for conductors over 2,000V.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  39. Q39.Which conductor insulation is rated for 90°C in dry locations but only 75°C in wet locations?

    A.THWN-2
    B.XHHW-2
    C.THHW
    D.THHN
    CTHHW

    Explanation: THHW is rated 90°C dry and 75°C wet. (THHN is 90°C dry / damp only. THWN-2 is 90°C wet/dry).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  40. Q40.When bare conductors are installed with insulated conductors, the ampacity of the bare conductor is considered to be:

    A.The same as the insulated conductors
    B.The same as the lowest rated insulated conductor in the same raceway
    C.125% of the insulated conductor
    D.Half the ampacity
    BThe same as the lowest rated insulated conductor in the same raceway

    Explanation: NEC 310.15(A)(2) (or B) states that the ampacity of bare or covered conductors shall be considered the same as the ampacity of the insulated conductor of the lowest temperature rating with which they are associated.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  41. Q41.A 3-phase, 4-wire circuit supplies a panelboard. The neutral conductor is considered 'current-carrying' if:

    A.The circuit supplies only balanced loads
    B.The major portion of the load consists of nonlinear loads
    C.It is bonded to the enclosure
    D.It is smaller than the phase conductors
    BThe major portion of the load consists of nonlinear loads

    Explanation: NEC 310.15(E)(3) states that on a 4-wire, 3-phase wye circuit where the major portion of the load consists of nonlinear loads, harmonic currents are present in the neutral, and it shall be considered a current-carrying conductor.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  42. Q42.What is the kcmil area of a 4/0 AWG conductor?

    A.133,100
    B.167,800
    C.211,600
    D.250,000
    C211,600

    Explanation: Chapter 9, Table 8 lists the properties of conductors. 4/0 AWG is 211,600 circular mils.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  43. Q43.Stranded conductors inserted into wire-binding screws must be:

    A.Soldered
    B.Identified for use with stranded conductors or spliced to solid wire
    C.Twisted tightly
    D.Covered with tape
    BIdentified for use with stranded conductors or spliced to solid wire

    Explanation: NEC 110.14(A) requires that terminals for more than one conductor or for stranded wire must be identified for such use, or the strands must be made solid (spliced/soldered) before insertion.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  44. Q44.The minimum cover requirement for direct buried cable (like UF) in a residential trench is typically:

    A.6 inches
    B.12 inches
    C.18 inches
    D.24 inches
    D24 inches

    Explanation: NEC Table 300.5 Column 1 specifies the minimum cover requirements for direct buried cables. The general minimum is 24 inches of cover. A reduced depth of 12 inches is allowed only for residential branch circuits rated 120V or less with GFCI protection and overcurrent protection not exceeding 20 amps. The standard requirement is 24 inches.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  45. Q45.When multiple cables are bundled longer than 24 inches, the ampacity adjustment factors apply to:

    A.Only the inner cables
    B.All current-carrying conductors in the bundle
    C.Only the outer cables
    D.Cables over 100A only
    BAll current-carrying conductors in the bundle

    Explanation: NEC 310.15(C)(1) applies to all current-carrying conductors in the raceway or cable bundle.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  46. Q46.For a 120/240V single-phase dwelling service, what is the maximum load current for a 4/0 AWG Aluminum service conductor?

    A.150 Amps
    B.180 Amps
    C.200 Amps
    D.225 Amps
    C200 Amps

    Explanation: NEC 310.12 (Dwelling Services) allows 4/0 Aluminum to serve a 200A dwelling service rating.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  47. Q47.Conductors used for direct burial applications must be identified for such use. Which marking indicates this suitability?

    A.SR
    B.VW-1
    C.DIR BUR
    D.LS
    CDIR BUR

    Explanation: Type UF cable or conductors listed for direct burial are marked 'DIR BUR' (Direct Burial).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  48. Q48.Where installed in raceways, conductors of size _____ and larger shall be stranded.

    A.10 AWG
    B.8 AWG
    C.6 AWG
    D.4 AWG
    B8 AWG

    Explanation: NEC 310.3(A) requires conductors 8 AWG and larger to be stranded when installed in raceways.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  49. Q49.What is the minimum wire-bending space for a 3/0 AWG conductor entering a panelboard terminal (one wire per terminal)?

    A.3 inches
    B.4 inches
    C.5 inches
    D.6 inches
    B4 inches

    Explanation: Table 312.6(B) requires 4 inches of bending space for a 3/0 AWG conductor.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  50. Q50.When calculating ampacity, if a single conduit contains both power conductors and control conductors (that do not carry continuous load), are the control conductors counted for derating?

    A.Yes, always.
    B.No, never.
    C.Yes, if they carry more than 50% of their rated ampacity.
    D.No, provided the control conductors are 10% or less of the fill.
    AYes, always.

    Explanation: NEC 310.15(C)(1) requires derating when more than three current-carrying conductors are installed in a raceway. Power control conductors that carry current are counted as current-carrying conductors for derating purposes. Unless they qualify as non-current-carrying under NEC 310.15(E) or fall under specific Article 725 Class 2/3 exemptions, control conductors in a shared raceway with power conductors are included in the count and subject to derating.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  51. Q51.Which of the following locations is considered a 'Wet Location' for conductor selection?

    A.Indoor dry rooms
    B.Installations underground in direct contact with the earth
    C.Attics
    D.Suspended ceilings
    BInstallations underground in direct contact with the earth

    Explanation: NEC 100 'Location, Wet' includes installations underground or in concrete slabs in direct contact with the earth.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  52. Q52.For a 3-phase, 4-wire, Wye system supplying non-linear loads, the neutral conductor must be capable of carrying:

    A.Only the unbalanced current
    B.The full phase current
    C.125% of the phase current
    D.140% of the phase current
    AOnly the unbalanced current

    Explanation: The neutral must be sized to carry the maximum unbalanced current (220.61). However, if non-linear, it counts for derating (310.15(E)(3)). The *sizing* rule (220.61) says it must handle the unbalance, but due to harmonics, the unbalance might equal or exceed phase current. The most precise Code requirement is that it must carry the unbalanced load.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  53. Q53.NEC 2026 Article 310.16 (Ampacity Table) retains the 90°C column, but clarifies that it is primarily used for:

    A.Final termination ampacity
    B.Derating (adjustment) calculations
    C.Old work only
    D.Aluminum conductors only
    BDerating (adjustment) calculations

    Explanation: The Code continues to emphasize that while 90°C wire (THHN/THWN-2) is common, the 90°C column is used for ampacity adjustment (temperature/fill), while the final ampacity is limited by the 75°C termination rating (110.14(C)).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  54. Q54.Shielding is required for solid dielectric insulated conductors operated above:

    A.600 Volts
    B.1000 Volts
    C.2000 Volts
    D.2400 Volts
    C2000 Volts

    Explanation: NEC 310.10(E) requires shielding for solid dielectric insulated conductors operated above 2000 Volts.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  55. Q55.Calculate the ampacity of three 8 AWG THHN copper conductors in a conduit on a roof where the ambient temperature is 45°C (113°F).

    A.40 Amps
    B.55 Amps
    C.47.8 Amps
    D.50 Amps
    C47.8 Amps

    Explanation: 8 AWG THHN (90°C) = 55A. Temp correction for 45°C (113°F) in 90°C column (Table 310.15(B)(1)) is 0.87. 55 * 0.87 = 47.85 Amps.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  56. Q56.When terminating fine stranded conductors (Class K, M, etc.), what must be verified?

    A.That the lug is identified for the specific conductor class
    B.That the wire is tinned
    C.That the insulation is stripped back 1 inch
    D.That a washer is used
    AThat the lug is identified for the specific conductor class

    Explanation: NEC 110.14 requires that connectors used with fine stranded conductors must be identified for the specific conductor class, as standard lugs may not clamp them securely.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  57. Q57.Parallel conductors must be installed in:

    A.A single raceway
    B.Separate raceways with one phase per raceway
    C.Separate raceways containing all phases and neutral in each raceway
    D.PVC conduit only
    CSeparate raceways containing all phases and neutral in each raceway

    Explanation: NEC 300.3(B)(1) requires that all conductors of the same circuit (phases and neutral) be in the same raceway. If run in parallel in separate raceways, EACH raceway must contain a complete set (A, B, C, N).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

More Journeyman Electrician Exam Topics

Studying for the Journeyman Electrician exam? Read more about Electrician Prep