Journeyman Electrician Exam
Motors Practice Questions
55 practice questions with detailed explanations — aligned to the Journeyman Electrician Exam.
Master Motors to boost your score on the Journeyman Electrician Exam. Each question below mirrors the style and difficulty of real exam questions, complete with detailed explanations so you understand the why behind every answer. Work through all 55 questions, review any that trip you up, and use the related topics below to round out your preparation.
Q1.When sizing conductors for a 3-phase motor, which current rating must be used?
A.The nameplate current ratingB.The Full Load Current (FLC) from NEC Tables 430.248 through 430.250C.The Locked Rotor CurrentD.The Service Factor Amps✓B. The Full Load Current (FLC) from NEC Tables 430.248 through 430.250Explanation: NEC 430.6(A)(1) requires that for general motor applications, the FLC values given in Tables 430.247 through 430.250 be used to determine the ampacity of conductors and switch ratings, not the nameplate current.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q2.What is the Table Full Load Current (FLC) for a 5 HP, 230V, single-phase motor?
A.24 AmpsB.28 AmpsC.30 AmpsD.15.2 Amps✓B. 28 AmpsExplanation: Referencing Table 430.248 for Single-Phase AC Motors: 5 HP at 230V corresponds to 28 Amps.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q3.Determine the minimum branch-circuit conductor ampacity for a 10 HP, 460V, 3-phase squirrel-cage motor with a nameplate FLA of 12.5A and a Table FLC of 14A.
A.14.0 AmpsB.15.6 AmpsC.17.5 AmpsD.12.5 Amps✓C. 17.5 AmpsExplanation: NEC 430.22 requires branch circuit conductors to be sized at 125% of the Table FLC (not nameplate). 14A x 1.25 = 17.5 Amps.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q4.A motor has a service factor (SF) of 1.15. What is the maximum setting permitted for the separate overload device as a percentage of the nameplate current rating?
A.100%B.115%C.125%D.140%✓C. 125%Explanation: NEC 430.32(A)(1) permits the overload device to be set at a maximum of 125% of the nameplate full-load current rating for motors with a marked service factor of 1.15 or greater.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q5.Using an Inverse Time Circuit Breaker, what is the maximum standard rating permitted for branch-circuit short-circuit protection for a 3-phase motor with an FLC of 40A?
A.60 AmpsB.80 AmpsC.100 AmpsD.125 Amps✓C. 100 AmpsExplanation: Table 430.52 allows an Inverse Time Breaker to be sized up to 250% of the motor FLC. 40A x 2.5 = 100A.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q6.A disconnecting means for a motor must be located:
A.Within 10 feet of the motorB.Within sight from the motor location and the machinery drivenC.In a separate control roomD.Within 25 feet of the motor✓B. Within sight from the motor location and the machinery drivenExplanation: NEC 430.102(B) requires the disconnecting means to be located in sight from the motor location and the driven machinery. 'In sight' is defined as visible and not more than 50 feet away.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q7.Calculate the minimum feeder conductor ampacity for two motors: Motor A (10 HP, 230V, 3-phase, FLC 28A) and Motor B (5 HP, 230V, 3-phase, FLC 15.2A).
A.43.2 AmpsB.50.2 AmpsC.54.0 AmpsD.60.0 Amps✓B. 50.2 AmpsExplanation: NEC 430.24 requires the feeder to be sized at 125% of the largest motor FLC plus the sum of the other motors. (28A x 1.25) + 15.2A = 35 + 15.2 = 50.2 Amps.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q8.For a motor with a nameplate temperature rise of 40°C, what is the maximum overload protection setting allowed?
A.115%B.125%C.130%D.140%✓B. 125%Explanation: NEC 430.32(A)(1) allows 125% of nameplate current for motors with a temperature rise of 40°C or less. (Others are 115%).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q9.What is the FLC for a 40 HP, 460V, 3-phase synchronous motor operating at unity power factor?
A.52 AmpsB.41 AmpsC.54 AmpsD.65 Amps✓A. 52 AmpsExplanation: Referring to Table 430.250 for 3-phase AC motors. Note the table usually covers squirrel cage and synchronous. For 40 HP at 460V, the value is 52 Amps.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q10.When using Instantaneous Trip Circuit Breakers (MCPs) for motor short-circuit protection, the initial setting shall not exceed _____ of the motor FLC.
A.250%B.300%C.800%D.1100%✓C. 800%Explanation: NEC 430.52(C)(3) allows Instantaneous Trip Breakers to be set up to 800% of the motor full-load current.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q11.A 1/2 HP motor that is not permanently installed is considered protected against overload if:
A.It is on a 20A circuit.B.The branch circuit device is rated 15A or less (and 125V).C.It has a heavy-duty cord.D.It is used for less than 1 hour a day.✓B. The branch circuit device is rated 15A or less (and 125V).Explanation: NEC 430.42(B) allows motors of 1 HP or less (non-permanently installed) to be protected by the branch circuit device if the device is not larger than 15A at 125V (or 10A at 250V).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q12.What is the minimum ampacity of conductors supplying a motor used for short-time duty (15-minute rated) service?
A.125% of nameplate ratingB.150% of nameplate ratingC.85% of nameplate ratingD.120% of nameplate rating✓C. 85% of nameplate ratingExplanation: NEC 430.22(E) and Table 430.22(E) allow for reduced conductor sizing for intermittent duty. For 15-minute rated motors, the percentage is 85% of the nameplate current.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q13.A motor controller enclosure installed outdoors must be:
A.NEMA 1B.NEMA 3R or 4C.Ventilated at the topD.Painted red✓B. NEMA 3R or 4Explanation: Equipment installed outdoors must be suitable for the environment. NEMA 3R (rainproof) or NEMA 4 (watertight) are standard outdoor ratings defined in Table 110.28.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q14.Torque motors shall have their branch-circuit conductors sized based on:
A.The FLC from Table 430.248B.The nameplate current rating (locked-rotor)C.125% of the breakdown torque currentD.The horsepower equivalent✓B. The nameplate current rating (locked-rotor)Explanation: NEC 430.6(B) states that for torque motors, the rated current shall be the nameplate current (which represents the locked-rotor condition for these motors).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q15.If a 20 HP, 208V 3-phase motor (FLC 59.4A) causes a 70A inverse time breaker to trip on startup, what is the maximum rating the breaker can be increased to?
A.100 AmpsB.125 AmpsC.175 AmpsD.225 Amps✓C. 175 AmpsExplanation: Per NEC 430.52(C)(1) Exception 2, if the standard 250% sizing (59.4A x 2.5 = 148.5A) is not sufficient for motor starting, an inverse time breaker can be increased up to 400% for motors with FLC of 100A or less. 59.4A x 4.0 = 237.6A maximum. The next standard size below this that exceeds the tripping 70A breaker is 175A.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q16.Calculate the maximum rating of a Dual Element (Time-Delay) Fuse for the branch-circuit protection of a 30 HP, 460V, 3-phase motor (FLC 40A).
A.50 AmpsB.60 AmpsC.70 AmpsD.80 Amps✓C. 70 AmpsExplanation: Table 430.52 allows Dual Element Fuses to be sized at 175% of FLC. 40A x 1.75 = 70 Amps.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q17.NEC 2026 Article 430.2 was amended to clarify that Adjustable Speed Drive (ASD) systems must also comply with the new general requirement for:
A.Load Calculations in Article 120B.Cybersecurity in Article 110.3(A)C.Reconditioned Equipment labeling in Article 110.21D.Medium Voltage definitions✓B. Cybersecurity in Article 110.3(A)Explanation: A key 2026 update involves ensuring that network-connected motor controllers and drives address cybersecurity (110.3(A)(8)).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q18.When a motor is supplied by a Variable Frequency Drive (VFD), the branch circuit conductors must be sized at _____ of the VFD's rated input current.
A.100%B.125%C.150%D.200%✓B. 125%Explanation: NEC 430.122(A) requires that branch circuit conductors supplying power conversion equipment (VFD) be sized at 125% of the drive's rated input current.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q19.Which of the following motors requires a manually operated switch that acts as a controller?
A.A 1/8 HP portable motorB.A 1/3 HP stationary motorC.A 2 HP or smaller motor operating at 300V or lessD.All motors regardless of size✓C. A 2 HP or smaller motor operating at 300V or lessExplanation: NEC 430.81(B) allows a stationary motor of 2 HP or less and 300V or less to be controlled by a general-use switch. (Larger motors require a rated controller).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q20.Capacitor conductors connected to a motor circuit shall have an ampacity of not less than _____ of the capacitor current rating.
A.100%B.125%C.135%D.150%✓C. 135%Explanation: NEC 460.8 requires capacitor circuit conductors to be sized at not less than 135% of the rated current of the capacitor.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q21.A motor has a Code Letter 'D' marked on the nameplate. This letter is used to determine which of the following?
A.The full load efficiencyB.The locked-rotor current (kVA per HP)C.The service factorD.The maximum ambient temperature✓B. The locked-rotor current (kVA per HP)Explanation: NEC 430.7(B) states that code letters marked on motor nameplates indicate the locked-rotor kilovolt-amperes per horsepower, used for determining locked-rotor current.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q22.Calculate the maximum rating of the feeder short-circuit and ground-fault protection device for a group of two motors: Motor A (50 HP, 460V, FLC 65A) and Motor B (20 HP, 460V, FLC 27A). Both use Inverse Time Breakers.
A.150 AmpsB.175 AmpsC.200 AmpsD.190 Amps✓D. 190 AmpsExplanation: NEC 430.62(A) sets the max feeder protection to the largest branch-circuit protection rating plus the sum of the other motor FLCs. Branch A (Inverse Time): 65A * 2.5 = 162.5A -> 175A (next standard size per 430.52 exception/standard usage). Branch B: 27A. Feeder Max = 162.5A (calculated max setting allowed) + 27A = 189.5A. The standard size is not required to be used for the *feeder limit calculation* itself, it's the specific rating. However, if we use the standard breaker size for Motor A (175A), then 175 + 27 = 202A -> 200A breaker. BUT, 430.62(A) says 'rating or setting... shall not be greater than'. The calculation is generally: (Largest Branch Device) + Sum of Others. Max Branch A = 175A. 175 + 27 = 202A. A 200A device is the largest standard size below 202A. However, if the question asks for the calculated maximum (exact), it depends on interpretation of 'rating'. Let's calculate strictly: Largest FLC (65A) * 2.5 = 162.5A. Next standard up is 175A. Total = 175 + 27 = 202A. The largest standard rating *not exceeding* this is 200A. If options are 190 (non-standard) or 200... Let's check if 190 is relevant. 162.5 + 27 = 189.5A. 175A is the *device* used. So 175 + 27 = 202A. Max standard device is 200A. Option 200 is correct.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q23.A manually operated motor controller is NOT required to be horsepower rated if it controls which of the following?
A.A 5 HP motor operating at 480VB.A 3 HP motor operating at 240VC.A 2 HP or smaller motor operating at 300V or lessD.A 10 HP motor✓C. A 2 HP or smaller motor operating at 300V or lessExplanation: NEC 430.83(C)(1) allows a general-use snap switch or similar device (not HP rated) to serve as the controller for stationary motors of 2 HP or less and 300 Volts or less.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q24.What is the minimum size copper equipment grounding conductor required for a 75 HP, 460V, 3-phase motor circuit protected by a 250A circuit breaker?
A.6 AWGB.4 AWGC.3 AWGD.2 AWG✓B. 4 AWGExplanation: The EGC is sized based on the overcurrent device rating (250A). Table 250.122 requires a 4 AWG copper conductor for devices rated 201-300A.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q25.For a stationary motor of 1/8 HP, the branch circuit overcurrent device is permitted to serve as the controller.
A.TrueB.FalseC.Only if the motor is DCD.Only if voltage is under 50V✓A. TrueExplanation: NEC 430.81(A) states that for stationary motors of 1/8 HP or less that are normally left running (like a clock), the branch-circuit overcurrent device is permitted to serve as the controller.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q26.When one or more motors are supplied by a feeder tap, the tap conductors must terminate in a branch-circuit protective device and must be protected from physical damage. If the tap is 20 feet long, its ampacity must be at least:
A.1/10 of the feeder ratingB.1/3 of the feeder ratingC.125% of the motor FLCD.The full rating of the feeder✓B. 1/3 of the feeder ratingExplanation: NEC 430.28(2) applies the '25-foot tap rule' logic to motor feeder taps: if the tap is over 10 feet but not over 25 feet, the conductor ampacity must be at least 1/3 of the feeder conductor ampacity.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q27.A motor disconnect must be capable of interrupting:
A.The full load current onlyB.The locked-rotor currentC.The service factor currentD.The short-circuit current✓B. The locked-rotor currentExplanation: NEC 430.110(A) requires the disconnecting means for a motor to have an ampere rating of at least 115% of the full-load current rating, but fundamentally, per 430.109(A)(1), an HP-rated switch is tested to interrupt the locked-rotor current.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q28.Using Table 430.52, what is the maximum rating for a Nontime Delay Fuse for a 3-phase AC motor?
A.175% of FLCB.250% of FLCC.300% of FLCD.400% of FLC✓C. 300% of FLCExplanation: Table 430.52 specifies the maximum percentage for Nontime Delay Fuses is 300% of the Full Load Current.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q29.A motor with a Service Factor (SF) of 1.0 requires overload protection set at no more than _____ of the nameplate current.
A.100%B.115%C.125%D.140%✓B. 115%Explanation: NEC 430.32(A)(1) states that for motors with a Service Factor of less than 1.15 (e.g., 1.0) and temperature rise > 40°C, the overload protection max is 115% of the nameplate rating.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q30.Liquidtight Flexible Metal Conduit (LFMC) used for motor connection is permitted to serve as the Equipment Grounding Conductor if the current is 60A or less and the length is not over:
A.3 feetB.6 feetC.10 feetD.25 feet✓B. 6 feetExplanation: NEC 250.118(6) allows LFMC to serve as the EGC if the length is 6 feet or less (and other conditions are met).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q31.Which Article governs the installation of Hermetic Refrigerant Motor-Compressors?
A.Article 430B.Article 440C.Article 445D.Article 450✓B. Article 440Explanation: Article 440 specifically covers Hermetic Refrigerant Motor-Compressors, although it references Article 430 for general motor rules not modified by 440.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q32.For a multispeed motor, the branch-circuit conductor ampacity is based on:
A.The lowest FLC ratingB.The highest of the full-load current ratings shown on the nameplateC.The average FLC ratingD.The locked-rotor current✓B. The highest of the full-load current ratings shown on the nameplateExplanation: NEC 430.22(B) states that for multispeed motors, the selection of branch-circuit conductors on the line side of the controller shall be based on the highest of the full-load current ratings shown on the motor nameplate.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q33.The minimum size disconnect for a motor rated over 100 HP is:
A.A general-use switch with twice the amperage ratingB.A circuit breaker onlyC.A general-use isolation switchD.A horsepower rated switch or circuit breaker✓C. A general-use isolation switchExplanation: NEC 430.109(E) states that for motors rated over 100 HP, a general-use or isolating switch is permitted as the disconnecting means (marked 'Do Not Open Under Load'), as HP rated switches are rare above 100 HP.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q34.A motor is installed in a Class I, Division 1 hazardous location. The motor must be identified for:
A.Class I, Division 2B.Class I, Division 1C.Class II, Division 1D.General Purpose use✓B. Class I, Division 1Explanation: NEC 501.125(A) requires motors in Class I, Division 1 locations to be identified (listed) for Class I, Division 1, or be totally enclosed pipe-ventilated/pressurized.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q35.When calculating the conductor size for a Wye-Start, Delta-Run motor, the ampacity of the conductors between the controller and the motor is based on:
A.58% of the motor FLCB.72% of the motor FLCC.100% of the motor FLCD.125% of the motor FLC✓A. 58% of the motor FLCExplanation: NEC 430.22(C) states that for Wye-Start, Delta-Run motors, the conductors between the controller and the motor are sized at 58% of the full-load current (as they carry phase current, not line current).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q36.If a motor has a temperature rise of 45°C and a Service Factor of 1.0, what is the maximum overload setting allowed?
A.115%B.125%C.135%D.140%✓A. 115%Explanation: NEC 430.32(A)(1). Motors with Temp Rise > 40°C and SF < 1.15 fall into 'All other motors', which is 115%.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q37.For a 3-phase, 208V, 7.5 HP motor, find the FLC from the NEC tables.
A.22 AmpsB.24.2 AmpsC.30.8 AmpsD.16.7 Amps✓B. 24.2 AmpsExplanation: NEC Table 430.250 lists full-load currents for three-phase AC motors. For a 7.5 HP motor operating at 208V, the full-load current is 24.2 Amps. For reference, a 5 HP motor at 208V is 16.7A and a 10 HP motor at 208V is 30.8A.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q38.Calculate the feeder demand factor for a group of 10 elevators.
A.100%B.85%C.79%D.72%✓C. 79%Explanation: This is often tested under motors/special equipment. NEC Table 620.14 provides demand factors for elevators. For 10 elevators, the demand factor is 0.79.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q39.Are separate overload devices required for a 1 HP motor that is manually started and within sight of the controller?
A.Yes, always.B.No, if the branch circuit protection is non-time delay.C.No, if the motor is not permanently installed.D.No, if it is continuous duty.✓C. No, if the motor is not permanently installed.Explanation: NEC 430.32(B)(1) or (D). 1 HP or less, manually started, within sight: overload protection is not required if it's not permanently installed. If permanently installed, it requires protection.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q40.Two motors are fed from a single branch circuit. This is permitted if:
A.Both motors are over 1 HP.B.The rating of the branch-circuit protective device does not exceed the rating marked on any of the controllers.C.The total current exceeds 100A.D.They are not within sight of each other.✓B. The rating of the branch-circuit protective device does not exceed the rating marked on any of the controllers.Explanation: NEC 430.53(A) and (B) allow multiple motors on one branch circuit under specific conditions. 430.53(C) is for group installations. A key constraint is that the branch circuit device must not exceed the rating marked on the controllers or overload relays.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q41.Control circuit transformers (integral to the motor controller) sized less than _____ VA are not required to have primary overcurrent protection if installed within the controller enclosure.
A.50 VAB.100 VAC.500 VAD.1000 VA✓A. 50 VAExplanation: NEC 430.72(C)(1) Exception 1 states that control circuit transformers rated less than 50 VA do not require primary protection if they are an integral part of the motor controller.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q42.The motor branch-circuit short-circuit and ground-fault protective device for a fire pump motor shall be capable of carrying:
A.125% of the motor FLC indefinitelyB.The locked-rotor current indefinitelyC.The locked-rotor current for the time required to accelerate the motorD.300% of the motor FLC✓B. The locked-rotor current indefinitelyExplanation: NEC 695.4(B)(2)(a)(1) requires the overcurrent device for a fire pump to hold the locked-rotor current indefinitely (or be set to not trip at LRC).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q43.A motor installed in a Class II, Division 1 location (combustible dust) must be:
A.Totally enclosed pipe-ventilatedB.Open drip-proofC.Weather-protected Type ID.Guarded✓A. Totally enclosed pipe-ventilatedExplanation: NEC 502.125(A) requires motors in Class II, Division 1 locations to be totally enclosed pipe-ventilated, totally enclosed fan-cooled, or dust-ignitionproof.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q44.What is the minimum ampacity of conductors supplying a 10 HP, 480V, 3-phase motor (FLC 14A) used for varying duty?
A.14 AmpsB.17.5 AmpsC.28 AmpsD.200% of the nameplate current✓D. 200% of the nameplate currentExplanation: NEC 430.22(E) Table 430.22(E) sets the ampacity for varying duty motors at 200% of the nameplate current rating.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q45.Calculate the locked-rotor current for a 3-phase, 460V, 50 HP motor with Code Letter G.
A.350 - 399 AmpsB.280 - 315 AmpsC.150 - 180 AmpsD.400 - 450 Amps✓A. 350 - 399 AmpsExplanation: Table 430.7(B) gives Code G range as 5.6 - 6.29 kVA/HP. Max kVA = 50 * 6.29 = 314.5 kVA. I = kVA / (Volts * 1.732). 314,500 / (460 * 1.732) = 314,500 / 796.7 = 394.7 Amps. Min kVA = 50 * 5.6 = 280. I = 280,000 / 796.7 = 351 Amps. Range is roughly 351-395A.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q46.For a part-winding motor, the branch-circuit fuses shall be sized based on:
A.50% of the motor FLCB.The full load current of the motor winding being protectedC.150% of the full motor FLCD.The locked-rotor current divided by two✓C. 150% of the full motor FLCExplanation: NEC 430.52(C)(5) addresses overcurrent protection for part-winding motors. Where separate overcurrent devices are used for each half of a part-winding motor, each device shall be rated at not more than 150% of the motor full-load current. This is derived by taking the standard Table 430.52 non-time delay fuse value of 300% and applying the required one-half factor for part-winding protection.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q47.If a motor is provided with a thermal protector integral with the motor, the ultimate trip current must not exceed _____ of the motor full-load current for a motor with FLC > 20A.
A.140%B.156%C.170%D.125%✓A. 140%Explanation: NEC 430.32(A)(2) requires integral thermal protectors to trip at not more than 140% of FLC for motors with FLC exceeding 20 Amperes (156% for 9A or less, 140% for 9.1-20A, 140% for >20A).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q48.A disconnecting means is not required to be within sight of the motor if:
A.The motor is over 100 HP.B.The disconnecting means is capable of being locked in the open position.C.The voltage is over 600V.D.The motor is submerged.✓B. The disconnecting means is capable of being locked in the open position.Explanation: NEC 430.102(B) generally requires the disconnecting means to be within sight of the motor. The exception permits the disconnect to be out of sight if it is capable of being locked in the open position. This lockable disconnect provision is the standard exam-tested exception that eliminates the line-of-sight requirement.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q49.In NEC 2026, where can the method for calculating the ampacity of conductors for a single motor be found if the general load calculation requirements are now in Article 120?
A.Article 120.5B.Article 430.22C.Article 220.14D.Article 310.15✓B. Article 430.22Explanation: While Article 120 takes General Requirements, specific equipment calculations remain in their respective articles. Motor conductor sizing remains in Article 430.22.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q50.NEC 2026 Article 430.130 requires that for circuits containing power conversion equipment (drives), the ground-fault protection shall be:
A.Type B GFCIB.Compatible with the specific waveform output of the driveC.Set at 5mAD.Located at the motor terminals✓B. Compatible with the specific waveform output of the driveExplanation: New nuances in NEC 2026 emphasize that protection devices must be compatible with the non-sinusoidal waveforms generated by drives to function correctly.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q51.The ampacity of conductors supplying a motor used in a continuous duty application shall be not less than:
A.100% of motor nameplate ratingB.125% of motor nameplate ratingC.125% of motor FLC from NEC tablesD.150% of motor FLC from NEC tables✓C. 125% of motor FLC from NEC tablesExplanation: NEC 430.22 states that conductors for a single motor used in a continuous duty application shall have an ampacity of not less than 125% of the motor's full-load current rating as determined by 430.6(A)(1) (Tables).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q52.When a motor is supplied by a 100 ft run of 10 AWG copper wire, and the voltage drop is 5%, what is the most appropriate action?
A.Increase the breaker size.B.Increase the wire size to 8 AWG.C.Reduce the load.D.Voltage drop is not a code violation, so do nothing.✓B. Increase the wire size to 8 AWG.Explanation: While Voltage Drop (FPN) recommends max 3%, high voltage drop causes motor overheating. The practical and exam-correct answer for a dedicated motor circuit with high drop is to increase conductor size. (Calculations would show 8 AWG reduces resistance).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q53.NEC 2026 classifies a 'Fault-Managed Power' motor circuit under:
A.Article 725B.Article 726C.Article 430 Part XIIID.Article 760✓B. Article 726Explanation: Article 726 is the new home for Fault-Managed Power Systems (Class 4), which can include specific motor applications utilizing this technology.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q54.The rating of a branch-circuit short-circuit protective device for a DC motor using an Inverse Time Breaker shall not exceed:
A.150% of FLCB.200% of FLCC.250% of FLCD.300% of FLC✓A. 150% of FLCExplanation: Table 430.52 shows that for DC Motors (Constant Voltage), the max Inverse Time Breaker setting is 150% of FLC.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q55.A motor control center (MCC) has a horizontal bus rating of 600A. The vertical bus rating is required to be:
A.300AB.600AC.Evaluated by the manufacturer (Listed)D.125% of the largest motor✓C. Evaluated by the manufacturer (Listed)Explanation: Internal bus ratings of listed equipment like MCCs are determined by the listing standard (UL 845), not a specific NEC calculation field calculation.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
More Journeyman Electrician Exam Topics
Studying for the Journeyman Electrician exam? Read more about Electrician Prep →