  1. Q1.When sizing conductors for a 3-phase motor, which current rating must be used?

    A.The nameplate current rating
    B.The Full Load Current (FLC) from NEC Tables 430.248 through 430.250
    C.The Locked Rotor Current
    D.The Service Factor Amps
    BThe Full Load Current (FLC) from NEC Tables 430.248 through 430.250

    Explanation: NEC 430.6(A)(1) requires that for general motor applications, the FLC values given in Tables 430.247 through 430.250 be used to determine the ampacity of conductors and switch ratings, not the nameplate current.

    Join 1,000+ users passing the Journeyman Electrician

  2. Q2.What is the Table Full Load Current (FLC) for a 5 HP, 230V, single-phase motor?

    A.24 Amps
    B.28 Amps
    C.30 Amps
    D.15.2 Amps
    B28 Amps

    Explanation: Referencing Table 430.248 for Single-Phase AC Motors: 5 HP at 230V corresponds to 28 Amps.

    Join 1,000+ users passing the Journeyman Electrician

  3. Q3.Determine the minimum branch-circuit conductor ampacity for a 10 HP, 460V, 3-phase squirrel-cage motor with a nameplate FLA of 12.5A and a Table FLC of 14A.

    A.14.0 Amps
    B.15.6 Amps
    C.17.5 Amps
    D.12.5 Amps
    C17.5 Amps

    Explanation: NEC 430.22 requires branch circuit conductors to be sized at 125% of the Table FLC (not nameplate). 14A x 1.25 = 17.5 Amps.

    Join 1,000+ users passing the Journeyman Electrician

  4. Q4.A motor has a service factor (SF) of 1.15. What is the maximum setting permitted for the separate overload device as a percentage of the nameplate current rating?

    A.100%
    B.115%
    C.125%
    D.140%
    C125%

    Explanation: NEC 430.32(A)(1) permits the overload device to be set at a maximum of 125% of the nameplate full-load current rating for motors with a marked service factor of 1.15 or greater.

    Join 1,000+ users passing the Journeyman Electrician

  5. Q5.Using an Inverse Time Circuit Breaker, what is the maximum standard rating permitted for branch-circuit short-circuit protection for a 3-phase motor with an FLC of 40A?

    A.60 Amps
    B.80 Amps
    C.100 Amps
    D.125 Amps
    C100 Amps

    Explanation: Table 430.52 allows an Inverse Time Breaker to be sized up to 250% of the motor FLC. 40A x 2.5 = 100A.

    Join 1,000+ users passing the Journeyman Electrician

  6. Q6.A disconnecting means for a motor must be located:

    A.Within 10 feet of the motor
    B.Within sight from the motor location and the machinery driven
    C.In a separate control room
    D.Within 25 feet of the motor
    BWithin sight from the motor location and the machinery driven

    Explanation: NEC 430.102(B) requires the disconnecting means to be located in sight from the motor location and the driven machinery. 'In sight' is defined as visible and not more than 50 feet away.

    Join 1,000+ users passing the Journeyman Electrician

  7. Q7.Calculate the minimum feeder conductor ampacity for two motors: Motor A (10 HP, 230V, 3-phase, FLC 28A) and Motor B (5 HP, 230V, 3-phase, FLC 15.2A).

    A.43.2 Amps
    B.50.2 Amps
    C.54.0 Amps
    D.60.0 Amps
    B50.2 Amps

    Explanation: NEC 430.24 requires the feeder to be sized at 125% of the largest motor FLC plus the sum of the other motors. (28A x 1.25) + 15.2A = 35 + 15.2 = 50.2 Amps.

    Join 1,000+ users passing the Journeyman Electrician

  8. Q8.For a motor with a nameplate temperature rise of 40°C, what is the maximum overload protection setting allowed?

    A.115%
    B.125%
    C.130%
    D.140%
    B125%

    Explanation: NEC 430.32(A)(1) allows 125% of nameplate current for motors with a temperature rise of 40°C or less. (Others are 115%).

    Join 1,000+ users passing the Journeyman Electrician

  9. Q9.What is the FLC for a 40 HP, 460V, 3-phase synchronous motor operating at unity power factor?

    A.52 Amps
    B.41 Amps
    C.54 Amps
    D.65 Amps
    A52 Amps

    Explanation: Referring to Table 430.250 for 3-phase AC motors. Note the table usually covers squirrel cage and synchronous. For 40 HP at 460V, the value is 52 Amps.

    Join 1,000+ users passing the Journeyman Electrician

  10. Q10.When using Instantaneous Trip Circuit Breakers (MCPs) for motor short-circuit protection, the initial setting shall not exceed _____ of the motor FLC.

    A.250%
    B.300%
    C.800%
    D.1100%
    C800%

    Explanation: NEC 430.52(C)(3) allows Instantaneous Trip Breakers to be set up to 800% of the motor full-load current.

    Join 1,000+ users passing the Journeyman Electrician

  11. Q11.A 1/2 HP motor that is not permanently installed is considered protected against overload if:

    A.It is on a 20A circuit.
    B.The branch circuit device is rated 15A or less (and 125V).
    C.It has a heavy-duty cord.
    D.It is used for less than 1 hour a day.
    BThe branch circuit device is rated 15A or less (and 125V).

    Explanation: NEC 430.42(B) allows motors of 1 HP or less (non-permanently installed) to be protected by the branch circuit device if the device is not larger than 15A at 125V (or 10A at 250V).

    Join 1,000+ users passing the Journeyman Electrician

  12. Q12.What is the minimum ampacity of conductors supplying a motor used for short-time duty (15-minute rated) service?

    A.125% of nameplate rating
    B.150% of nameplate rating
    C.85% of nameplate rating
    D.120% of nameplate rating
    C85% of nameplate rating

    Explanation: NEC 430.22(E) and Table 430.22(E) allow for reduced conductor sizing for intermittent duty. For 15-minute rated motors, the percentage is 85% of the nameplate current.

    Join 1,000+ users passing the Journeyman Electrician

  13. Q13.A motor controller enclosure installed outdoors must be:

    A.NEMA 1
    B.NEMA 3R or 4
    C.Ventilated at the top
    D.Painted red
    BNEMA 3R or 4

    Explanation: Equipment installed outdoors must be suitable for the environment. NEMA 3R (rainproof) or NEMA 4 (watertight) are standard outdoor ratings defined in Table 110.28.

    Join 1,000+ users passing the Journeyman Electrician

  14. Q14.Torque motors shall have their branch-circuit conductors sized based on:

    A.The FLC from Table 430.248
    B.The nameplate current rating (locked-rotor)
    C.125% of the breakdown torque current
    D.The horsepower equivalent
    BThe nameplate current rating (locked-rotor)

    Explanation: NEC 430.6(B) states that for torque motors, the rated current shall be the nameplate current (which represents the locked-rotor condition for these motors).

    Join 1,000+ users passing the Journeyman Electrician

  15. Q15.If a 20 HP, 208V 3-phase motor (FLC 59.4A) causes a 70A inverse time breaker to trip on startup, what is the maximum rating the breaker can be increased to?

    A.100 Amps
    B.125 Amps
    C.175 Amps
    D.225 Amps
    C175 Amps

    Explanation: Per NEC 430.52(C)(1) Exception 2, if the standard 250% sizing (59.4A x 2.5 = 148.5A) is not sufficient for motor starting, an inverse time breaker can be increased up to 400% for motors with FLC of 100A or less. 59.4A x 4.0 = 237.6A maximum. The next standard size below this that exceeds the tripping 70A breaker is 175A.

    Join 1,000+ users passing the Journeyman Electrician

  16. Q16.Calculate the maximum rating of a Dual Element (Time-Delay) Fuse for the branch-circuit protection of a 30 HP, 460V, 3-phase motor (FLC 40A).

    A.50 Amps
    B.60 Amps
    C.70 Amps
    D.80 Amps
    C70 Amps

    Explanation: Table 430.52 allows Dual Element Fuses to be sized at 175% of FLC. 40A x 1.75 = 70 Amps.

    Join 1,000+ users passing the Journeyman Electrician

  17. Q17.NEC 2026 Article 430.2 was amended to clarify that Adjustable Speed Drive (ASD) systems must also comply with the new general requirement for:

    A.Load Calculations in Article 120
    B.Cybersecurity in Article 110.3(A)
    C.Reconditioned Equipment labeling in Article 110.21
    D.Medium Voltage definitions
    BCybersecurity in Article 110.3(A)

    Explanation: A key 2026 update involves ensuring that network-connected motor controllers and drives address cybersecurity (110.3(A)(8)).

    Join 1,000+ users passing the Journeyman Electrician

  18. Q18.When a motor is supplied by a Variable Frequency Drive (VFD), the branch circuit conductors must be sized at _____ of the VFD's rated input current.

    A.100%
    B.125%
    C.150%
    D.200%
    B125%

    Explanation: NEC 430.122(A) requires that branch circuit conductors supplying power conversion equipment (VFD) be sized at 125% of the drive's rated input current.

    Join 1,000+ users passing the Journeyman Electrician

  19. Q19.Which of the following motors requires a manually operated switch that acts as a controller?

    A.A 1/8 HP portable motor
    B.A 1/3 HP stationary motor
    C.A 2 HP or smaller motor operating at 300V or less
    D.All motors regardless of size
    CA 2 HP or smaller motor operating at 300V or less

    Explanation: NEC 430.81(B) allows a stationary motor of 2 HP or less and 300V or less to be controlled by a general-use switch. (Larger motors require a rated controller).

    Join 1,000+ users passing the Journeyman Electrician

  20. Q20.Capacitor conductors connected to a motor circuit shall have an ampacity of not less than _____ of the capacitor current rating.

    A.100%
    B.125%
    C.135%
    D.150%
    C135%

    Explanation: NEC 460.8 requires capacitor circuit conductors to be sized at not less than 135% of the rated current of the capacitor.

    Join 1,000+ users passing the Journeyman Electrician

  21. Q21.A motor has a Code Letter 'D' marked on the nameplate. This letter is used to determine which of the following?

    A.The full load efficiency
    B.The locked-rotor current (kVA per HP)
    C.The service factor
    D.The maximum ambient temperature
    BThe locked-rotor current (kVA per HP)

    Explanation: NEC 430.7(B) states that code letters marked on motor nameplates indicate the locked-rotor kilovolt-amperes per horsepower, used for determining locked-rotor current.

    Join 1,000+ users passing the Journeyman Electrician

  22. Q22.Calculate the maximum rating of the feeder short-circuit and ground-fault protection device for a group of two motors: Motor A (50 HP, 460V, FLC 65A) and Motor B (20 HP, 460V, FLC 27A). Both use Inverse Time Breakers.

    A.150 Amps
    B.175 Amps
    C.200 Amps
    D.190 Amps
    D190 Amps

    Explanation: NEC 430.62(A) sets the max feeder protection to the largest branch-circuit protection rating plus the sum of the other motor FLCs. Branch A (Inverse Time): 65A * 2.5 = 162.5A -> 175A (next standard size per 430.52 exception/standard usage). Branch B: 27A. Feeder Max = 162.5A (calculated max setting allowed) + 27A = 189.5A. The standard size is not required to be used for the *feeder limit calculation* itself, it's the specific rating. However, if we use the standard breaker size for Motor A (175A), then 175 + 27 = 202A -> 200A breaker. BUT, 430.62(A) says 'rating or setting... shall not be greater than'. The calculation is generally: (Largest Branch Device) + Sum of Others. Max Branch A = 175A. 175 + 27 = 202A. A 200A device is the largest standard size below 202A. However, if the question asks for the calculated maximum (exact), it depends on interpretation of 'rating'. Let's calculate strictly: Largest FLC (65A) * 2.5 = 162.5A. Next standard up is 175A. Total = 175 + 27 = 202A. The largest standard rating *not exceeding* this is 200A. If options are 190 (non-standard) or 200... Let's check if 190 is relevant. 162.5 + 27 = 189.5A. 175A is the *device* used. So 175 + 27 = 202A. Max standard device is 200A. Option 200 is correct.

    Join 1,000+ users passing the Journeyman Electrician

  23. Q23.A manually operated motor controller is NOT required to be horsepower rated if it controls which of the following?

    A.A 5 HP motor operating at 480V
    B.A 3 HP motor operating at 240V
    C.A 2 HP or smaller motor operating at 300V or less
    D.A 10 HP motor
    CA 2 HP or smaller motor operating at 300V or less

    Explanation: NEC 430.83(C)(1) allows a general-use snap switch or similar device (not HP rated) to serve as the controller for stationary motors of 2 HP or less and 300 Volts or less.

    Join 1,000+ users passing the Journeyman Electrician

  24. Q24.What is the minimum size copper equipment grounding conductor required for a 75 HP, 460V, 3-phase motor circuit protected by a 250A circuit breaker?

    A.6 AWG
    B.4 AWG
    C.3 AWG
    D.2 AWG
    B4 AWG

    Explanation: The EGC is sized based on the overcurrent device rating (250A). Table 250.122 requires a 4 AWG copper conductor for devices rated 201-300A.

    Join 1,000+ users passing the Journeyman Electrician

  25. Q25.For a stationary motor of 1/8 HP, the branch circuit overcurrent device is permitted to serve as the controller.

    A.True
    B.False
    C.Only if the motor is DC
    D.Only if voltage is under 50V
    ATrue

    Explanation: NEC 430.81(A) states that for stationary motors of 1/8 HP or less that are normally left running (like a clock), the branch-circuit overcurrent device is permitted to serve as the controller.

    Join 1,000+ users passing the Journeyman Electrician

  26. Q26.When one or more motors are supplied by a feeder tap, the tap conductors must terminate in a branch-circuit protective device and must be protected from physical damage. If the tap is 20 feet long, its ampacity must be at least:

    A.1/10 of the feeder rating
    B.1/3 of the feeder rating
    C.125% of the motor FLC
    D.The full rating of the feeder
    B1/3 of the feeder rating

    Explanation: NEC 430.28(2) applies the '25-foot tap rule' logic to motor feeder taps: if the tap is over 10 feet but not over 25 feet, the conductor ampacity must be at least 1/3 of the feeder conductor ampacity.

    Join 1,000+ users passing the Journeyman Electrician

  27. Q27.A motor disconnect must be capable of interrupting:

    A.The full load current only
    B.The locked-rotor current
    C.The service factor current
    D.The short-circuit current
    BThe locked-rotor current

    Explanation: NEC 430.110(A) requires the disconnecting means for a motor to have an ampere rating of at least 115% of the full-load current rating, but fundamentally, per 430.109(A)(1), an HP-rated switch is tested to interrupt the locked-rotor current.

    Join 1,000+ users passing the Journeyman Electrician

  28. Q28.Using Table 430.52, what is the maximum rating for a Nontime Delay Fuse for a 3-phase AC motor?

    A.175% of FLC
    B.250% of FLC
    C.300% of FLC
    D.400% of FLC
    C300% of FLC

    Explanation: Table 430.52 specifies the maximum percentage for Nontime Delay Fuses is 300% of the Full Load Current.

    Join 1,000+ users passing the Journeyman Electrician

  29. Q29.A motor with a Service Factor (SF) of 1.0 requires overload protection set at no more than _____ of the nameplate current.

    A.100%
    B.115%
    C.125%
    D.140%
    B115%

    Explanation: NEC 430.32(A)(1) states that for motors with a Service Factor of less than 1.15 (e.g., 1.0) and temperature rise > 40°C, the overload protection max is 115% of the nameplate rating.

    Join 1,000+ users passing the Journeyman Electrician

  30. Q30.Liquidtight Flexible Metal Conduit (LFMC) used for motor connection is permitted to serve as the Equipment Grounding Conductor if the current is 60A or less and the length is not over:

    A.3 feet
    B.6 feet
    C.10 feet
    D.25 feet
    B6 feet

    Explanation: NEC 250.118(6) allows LFMC to serve as the EGC if the length is 6 feet or less (and other conditions are met).

    Join 1,000+ users passing the Journeyman Electrician

  31. Q31.Which Article governs the installation of Hermetic Refrigerant Motor-Compressors?

    A.Article 430
    B.Article 440
    C.Article 445
    D.Article 450
    BArticle 440

    Explanation: Article 440 specifically covers Hermetic Refrigerant Motor-Compressors, although it references Article 430 for general motor rules not modified by 440.

    Join 1,000+ users passing the Journeyman Electrician

  32. Q32.For a multispeed motor, the branch-circuit conductor ampacity is based on:

    A.The lowest FLC rating
    B.The highest of the full-load current ratings shown on the nameplate
    C.The average FLC rating
    D.The locked-rotor current
    BThe highest of the full-load current ratings shown on the nameplate

    Explanation: NEC 430.22(B) states that for multispeed motors, the selection of branch-circuit conductors on the line side of the controller shall be based on the highest of the full-load current ratings shown on the motor nameplate.

    Join 1,000+ users passing the Journeyman Electrician

  33. Q33.The minimum size disconnect for a motor rated over 100 HP is:

    A.A general-use switch with twice the amperage rating
    B.A circuit breaker only
    C.A general-use isolation switch
    D.A horsepower rated switch or circuit breaker
    CA general-use isolation switch

    Explanation: NEC 430.109(E) states that for motors rated over 100 HP, a general-use or isolating switch is permitted as the disconnecting means (marked 'Do Not Open Under Load'), as HP rated switches are rare above 100 HP.

    Join 1,000+ users passing the Journeyman Electrician

  34. Q34.A motor is installed in a Class I, Division 1 hazardous location. The motor must be identified for:

    A.Class I, Division 2
    B.Class I, Division 1
    C.Class II, Division 1
    D.General Purpose use
    BClass I, Division 1

    Explanation: NEC 501.125(A) requires motors in Class I, Division 1 locations to be identified (listed) for Class I, Division 1, or be totally enclosed pipe-ventilated/pressurized.

    Join 1,000+ users passing the Journeyman Electrician

  35. Q35.When calculating the conductor size for a Wye-Start, Delta-Run motor, the ampacity of the conductors between the controller and the motor is based on:

    A.58% of the motor FLC
    B.72% of the motor FLC
    C.100% of the motor FLC
    D.125% of the motor FLC
    A58% of the motor FLC

    Explanation: NEC 430.22(C) states that for Wye-Start, Delta-Run motors, the conductors between the controller and the motor are sized at 58% of the full-load current (as they carry phase current, not line current).

    Join 1,000+ users passing the Journeyman Electrician

  36. Q36.If a motor has a temperature rise of 45°C and a Service Factor of 1.0, what is the maximum overload setting allowed?

    A.115%
    B.125%
    C.135%
    D.140%
    A115%

    Explanation: NEC 430.32(A)(1). Motors with Temp Rise > 40°C and SF < 1.15 fall into 'All other motors', which is 115%.

    Join 1,000+ users passing the Journeyman Electrician

  37. Q37.For a 3-phase, 208V, 7.5 HP motor, find the FLC from the NEC tables.

    A.22 Amps
    B.24.2 Amps
    C.30.8 Amps
    D.16.7 Amps
    B24.2 Amps

    Explanation: Table 430.250 for 3-phase, 208V. 7.5 HP = 24.2 Amps. (Note: 5 HP is 16.7A, 10 HP is 30.8A).

    Join 1,000+ users passing the Journeyman Electrician

  38. Q38.Calculate the feeder demand factor for a group of 10 elevators.

    A.100%
    B.85%
    C.79%
    D.72%
    C79%

    Explanation: This is often tested under motors/special equipment. NEC Table 620.14 provides demand factors for elevators. For 10 elevators, the demand factor is 0.79.

    Join 1,000+ users passing the Journeyman Electrician

  39. Q39.Are separate overload devices required for a 1 HP motor that is manually started and within sight of the controller?

    A.Yes, always.
    B.No, if the branch circuit protection is non-time delay.
    C.No, if the motor is not permanently installed.
    D.No, if it is continuous duty.
    CNo, if the motor is not permanently installed.

    Explanation: NEC 430.32(B)(1) or (D). 1 HP or less, manually started, within sight: overload protection is not required if it's not permanently installed. If permanently installed, it requires protection.

    Join 1,000+ users passing the Journeyman Electrician

  40. Q40.Two motors are fed from a single branch circuit. This is permitted if:

    A.Both motors are over 1 HP.
    B.The rating of the branch-circuit protective device does not exceed the rating marked on any of the controllers.
    C.The total current exceeds 100A.
    D.They are not within sight of each other.
    BThe rating of the branch-circuit protective device does not exceed the rating marked on any of the controllers.

    Explanation: NEC 430.53(A) and (B) allow multiple motors on one branch circuit under specific conditions. 430.53(C) is for group installations. A key constraint is that the branch circuit device must not exceed the rating marked on the controllers or overload relays.

    Join 1,000+ users passing the Journeyman Electrician

  41. Q41.Control circuit transformers (integral to the motor controller) sized less than _____ VA are not required to have primary overcurrent protection if installed within the controller enclosure.

    A.50 VA
    B.100 VA
    C.500 VA
    D.1000 VA
    A50 VA

    Explanation: NEC 430.72(C)(1) Exception 1 states that control circuit transformers rated less than 50 VA do not require primary protection if they are an integral part of the motor controller.

    Join 1,000+ users passing the Journeyman Electrician

  42. Q42.The motor branch-circuit short-circuit and ground-fault protective device for a fire pump motor shall be capable of carrying:

    A.125% of the motor FLC indefinitely
    B.The locked-rotor current indefinitely
    C.The locked-rotor current for the time required to accelerate the motor
    D.300% of the motor FLC
    BThe locked-rotor current indefinitely

    Explanation: NEC 695.4(B)(2)(a)(1) requires the overcurrent device for a fire pump to hold the locked-rotor current indefinitely (or be set to not trip at LRC).

    Join 1,000+ users passing the Journeyman Electrician

  43. Q43.A motor installed in a Class II, Division 1 location (combustible dust) must be:

    A.Totally enclosed pipe-ventilated
    B.Open drip-proof
    C.Weather-protected Type I
    D.Guarded
    ATotally enclosed pipe-ventilated

    Explanation: NEC 502.125(A) requires motors in Class II, Division 1 locations to be totally enclosed pipe-ventilated, totally enclosed fan-cooled, or dust-ignitionproof.

    Join 1,000+ users passing the Journeyman Electrician

  44. Q44.What is the minimum ampacity of conductors supplying a 10 HP, 480V, 3-phase motor (FLC 14A) used for varying duty?

    A.14 Amps
    B.17.5 Amps
    C.28 Amps
    D.200% of the nameplate current
    D200% of the nameplate current

    Explanation: NEC 430.22(E) Table 430.22(E) sets the ampacity for varying duty motors at 200% of the nameplate current rating.

    Join 1,000+ users passing the Journeyman Electrician

  45. Q45.Calculate the locked-rotor current for a 3-phase, 460V, 50 HP motor with Code Letter G.

    A.350 - 399 Amps
    B.280 - 315 Amps
    C.150 - 180 Amps
    D.400 - 450 Amps
    A350 - 399 Amps

    Explanation: Table 430.7(B) gives Code G range as 5.6 - 6.29 kVA/HP. Max kVA = 50 * 6.29 = 314.5 kVA. I = kVA / (Volts * 1.732). 314,500 / (460 * 1.732) = 314,500 / 796.7 = 394.7 Amps. Min kVA = 50 * 5.6 = 280. I = 280,000 / 796.7 = 351 Amps. Range is roughly 351-395A.

    Join 1,000+ users passing the Journeyman Electrician

  46. Q46.For a part-winding motor, the branch-circuit fuses shall be sized based on:

    A.50% of the motor FLC
    B.The full load current of the motor winding being protected
    C.150% of the full motor FLC
    D.The locked-rotor current divided by two
    C150% of the full motor FLC

    Explanation: NEC 430.52(C)(5) states that where separate overcurrent devices are used for each half of a part-winding motor, they shall be sized at not more than 150% of the motor full-load current (the standard percentages are modified for part-winding). Wait, let's verify. 430.52(C)(5) says 'shall not exceed one-half the values specified in Table 430.52'. The Table value for Nontime Delay is 300%. Half is 150%. Correct.

    Join 1,000+ users passing the Journeyman Electrician

  47. Q47.If a motor is provided with a thermal protector integral with the motor, the ultimate trip current must not exceed _____ of the motor full-load current for a motor with FLC > 20A.

    A.140%
    B.156%
    C.170%
    D.125%
    A140%

    Explanation: NEC 430.32(A)(2) requires integral thermal protectors to trip at not more than 140% of FLC for motors with FLC exceeding 20 Amperes (156% for 9A or less, 140% for 9.1-20A, 140% for >20A).

    Join 1,000+ users passing the Journeyman Electrician

  48. Q48.A disconnecting means is not required to be within sight of the motor if:

    A.The motor is over 100 HP.
    B.The disconnecting means is capable of being locked in the open position.
    C.The voltage is over 600V.
    D.The motor is submerged.
    BThe disconnecting means is capable of being locked in the open position.

    Explanation: NEC 430.102(B) Exception allows the disconnect to be out of sight if it is capable of being locked in the open position and its location is impracticable or introduces additional hazards (industrial only) - BUT wait, the general rule 430.102(B)(2) Exception allows it if capable of being locked in the open position for *any* motor? No, check 2023 text. The exception typically requires that 'the disconnecting means shall be capable of being locked in the open position' AND usually applies to industrial/hazards. However, for everyday exams, the lockable disconnect is the key exception condition.

    Join 1,000+ users passing the Journeyman Electrician

  49. Q49.In NEC 2026, where can the method for calculating the ampacity of conductors for a single motor be found if the general load calculation requirements are now in Article 120?

    A.Article 120.5
    B.Article 430.22
    C.Article 220.14
    D.Article 310.15
    BArticle 430.22

    Explanation: While Article 120 takes General Requirements, specific equipment calculations remain in their respective articles. Motor conductor sizing remains in Article 430.22.

    Join 1,000+ users passing the Journeyman Electrician

  50. Q50.NEC 2026 Article 430.130 requires that for circuits containing power conversion equipment (drives), the ground-fault protection shall be:

    A.Type B GFCI
    B.Compatible with the specific waveform output of the drive
    C.Set at 5mA
    D.Located at the motor terminals
    BCompatible with the specific waveform output of the drive

    Explanation: New nuances in NEC 2026 emphasize that protection devices must be compatible with the non-sinusoidal waveforms generated by drives to function correctly.

    Join 1,000+ users passing the Journeyman Electrician

  51. Q51.The ampacity of conductors supplying a motor used in a continuous duty application shall be not less than:

    A.100% of motor nameplate rating
    B.125% of motor nameplate rating
    C.125% of motor FLC from NEC tables
    D.150% of motor FLC from NEC tables
    C125% of motor FLC from NEC tables

    Explanation: NEC 430.22 states that conductors for a single motor used in a continuous duty application shall have an ampacity of not less than 125% of the motor's full-load current rating as determined by 430.6(A)(1) (Tables).

    Join 1,000+ users passing the Journeyman Electrician

  52. Q52.When a motor is supplied by a 100 ft run of 10 AWG copper wire, and the voltage drop is 5%, what is the most appropriate action?

    A.Increase the breaker size.
    B.Increase the wire size to 8 AWG.
    C.Reduce the load.
    D.Voltage drop is not a code violation, so do nothing.
    BIncrease the wire size to 8 AWG.

    Explanation: While Voltage Drop (FPN) recommends max 3%, high voltage drop causes motor overheating. The practical and exam-correct answer for a dedicated motor circuit with high drop is to increase conductor size. (Calculations would show 8 AWG reduces resistance).

    Join 1,000+ users passing the Journeyman Electrician

  53. Q53.NEC 2026 classifies a 'Fault-Managed Power' motor circuit under:

    A.Article 725
    B.Article 726
    C.Article 430 Part XIII
    D.Article 760
    BArticle 726

    Explanation: Article 726 is the new home for Fault-Managed Power Systems (Class 4), which can include specific motor applications utilizing this technology.

    Join 1,000+ users passing the Journeyman Electrician

  54. Q54.The rating of a branch-circuit short-circuit protective device for a DC motor using an Inverse Time Breaker shall not exceed:

    A.150% of FLC
    B.200% of FLC
    C.250% of FLC
    D.300% of FLC
    A150% of FLC

    Explanation: Table 430.52 shows that for DC Motors (Constant Voltage), the max Inverse Time Breaker setting is 150% of FLC.

    Join 1,000+ users passing the Journeyman Electrician

  55. Q55.A motor control center (MCC) has a horizontal bus rating of 600A. The vertical bus rating is required to be:

    A.300A
    B.600A
    C.Evaluated by the manufacturer (Listed)
    D.125% of the largest motor
    CEvaluated by the manufacturer (Listed)

    Explanation: Internal bus ratings of listed equipment like MCCs are determined by the listing standard (UL 845), not a specific NEC calculation field calculation.