Load Calculations Practice Questions

70 practice questions with detailed explanations — aligned to the Journeyman Electrician Exam.

Master Load Calculations to boost your score on the Journeyman Electrician Exam. Each question below mirrors the style and difficulty of real exam questions, complete with detailed explanations so you understand the why behind every answer. Work through all 70 questions, review any that trip you up, and use the related topics below to round out your preparation.

  1. Q1.According to NEC 2026, which article now contains the general requirements for calculating floor area?

    A.Article 220
    B.Article 120
    C.Article 310
    D.Article 100
    BArticle 120

    Explanation: NEC 2026 moved the general calculation requirements, including floor area determination, to the new Article 120.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  2. Q2.What is the general lighting load for a 4,000 sq. ft. Bank?

    A.5,200 VA
    B.14,000 VA
    C.9,600 VA
    D.10,000 VA
    D10,000 VA

    Explanation: NEC 2023 Table 220.12 lists Banks at 2.5 VA per square foot. For a 4,000 sq ft bank: 4,000 × 2.5 = 10,000 VA. Note that the 2020 NEC listed banks at 3.5 VA/sq ft; always confirm which NEC edition your jurisdiction has adopted.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  3. Q3.What is the general lighting load for a 3,000 sq. ft. Dwelling Unit?

    A.3,000 VA
    B.4,500 VA
    C.9,000 VA
    D.10,500 VA
    C9,000 VA

    Explanation: Per NEC 2020 Table 220.12, Dwelling Units are calculated at 3.0 VA per sq ft. 3,000 sq ft × 3.0 = 9,000 VA. (NEC 2023 moved dwelling unit lighting load calculation to 220.41, but the 3.0 VA/sq ft value remains the standard reference used on most state journeyman exams.)

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  4. Q4.For a single-family dwelling, the small-appliance branch circuit load is calculated at:

    A.1,500 VA total
    B.1,500 VA for each 2-wire circuit
    C.3,000 VA total regardless of circuit count
    D.180 VA per outlet
    B1,500 VA for each 2-wire circuit

    Explanation: NEC 220.52(A) requires that for each 2-wire small-appliance branch circuit, a load of 1,500 VA shall be included.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  5. Q5.Calculate the feeder demand load for a 14 kW electric range.

    A.8 kW
    B.8.8 kW
    C.9.6 kW
    D.14 kW
    B8.8 kW

    Explanation: Table 220.55 Col C for one range: 8 kW is for ranges up to 12 kW. For 14 kW (which is 2 kW over 12), increase 8 kW by 5% for each kW over 12. 2 kW over. 2 x 5% = 10%. 8 kW x 1.10 = 8.8 kW.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  6. Q6.A commercial building has 50 duplex receptacles. What is the calculated load before demand factors?

    A.5,000 VA
    B.9,000 VA
    C.10,000 VA
    D.12,500 VA
    B9,000 VA

    Explanation: NEC 220.14(I) assigns 180 VA per receptacle strap. 50 * 180 = 9,000 VA.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  7. Q7.What is the calculated load for 50 linear feet of show window in a retail store?

    A.2,500 VA
    B.5,000 VA
    C.10,000 VA
    D.12,500 VA
    C10,000 VA

    Explanation: NEC 220.14(G) requires show windows to be calculated at 200 VA per linear foot. 50 ft * 200 VA/ft = 10,000 VA.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  8. Q8.Calculate the feeder load for 40 feet of lighting track in a commercial showroom.

    A.1,500 VA
    B.3,000 VA
    C.4,000 VA
    D.6,000 VA
    B3,000 VA

    Explanation: NEC 220.43(B) assigns a load of 150 VA for every 2 feet of track. 40 ft / 2 = 20 units. 20 * 150 VA = 3,000 VA.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  9. Q9.A restaurant kitchen has the following electric equipment: dishwasher, booster heater, oven, and fryer. What demand factor may be applied to the total load?

    A.65%
    B.70%
    C.80%
    D.90%
    C80%

    Explanation: NEC Table 220.56 allows a demand factor of 80% for commercial kitchen equipment when there are 4 units.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  10. Q10.When calculating the Neutral Load for a household electric dryer, what percentage of the dryer load is permitted to be used?

    A.50%
    B.70%
    C.80%
    D.100%
    B70%

    Explanation: NEC 220.61(B)(1) permits the neutral load for household electric ranges and dryers to be calculated at 70% of the load determined by Article 220.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  11. Q11.A building has a 10 kW heating load and a 15 kVA air conditioning load. The system prevents them from operating simultaneously. Which load is used in the feeder calculation?

    A.Both loads (25 kVA)
    B.The AC load only (15 kVA)
    C.The Heating load only (10 kW)
    D.125% of the larger load
    BThe AC load only (15 kVA)

    Explanation: NEC 220.60 (Noncoincident Loads) states that where two loads are unlikely to be used simultaneously, only the larger of the two needs to be used. 15 kVA > 10 kW.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  12. Q12.In NEC 2026, the 'Standard Method' for calculating branch circuit, feeder, and service loads is primarily detailed in which article?

    A.Article 120
    B.Article 220
    C.Article 240
    D.Article 310
    BArticle 220

    Explanation: While Article 120 covers General Requirements, Article 220 remains the home for the specific Standard Method calculations for Branch Circuits and Feeders.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  13. Q13.What is the minimum load assignment for a required commercial sign outlet?

    A.600 VA
    B.1,000 VA
    C.1,200 VA
    D.1,500 VA
    C1,200 VA

    Explanation: NEC 220.14(F) requires a sign outlet to be calculated at a minimum of 1,200 VA.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  14. Q14.Using the Standard Method, what is the feeder demand for two 12 kW household electric ranges?

    A.11 kW
    B.12 kW
    C.16 kW
    D.24 kW
    A11 kW

    Explanation: NEC Table 220.55 Column C shows that the demand load for 2 ranges is 11 kW.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  15. Q15.Fixed electric space heating loads shall be calculated at ____ of the total connected load.

    A.80%
    B.100%
    C.125%
    D.150%
    B100%

    Explanation: NEC 220.51 states that fixed electric space heating loads shall be calculated at 100% of the total connected load.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  16. Q16.For an office building with 200 duplex receptacles (standard 180VA each), totaling 36,000 VA, what is the demand load allowed by Table 220.44?

    A.18,000 VA
    B.23,000 VA
    C.36,000 VA
    D.10,000 VA
    B23,000 VA

    Explanation: Table 220.44 allows the first 10 kVA to be calculated at 100%, and the remainder at 50%. 36,000 - 10,000 = 26,000. 26,000 * 0.5 = 13,000. 10,000 + 13,000 = 23,000 VA.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  17. Q17.In a dwelling unit, four separate fixed appliances (water heater, disposal, dishwasher, trash compactor) are on the same feeder. A demand factor of ____ may be applied.

    A.65%
    B.75%
    C.80%
    D.100%
    B75%

    Explanation: NEC 220.53 allows a demand factor of 75% for four or more appliances fastened in place (excluding ranges, clothes dryers, space heating, and AC).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  18. Q18.What is the unit load per square foot for general lighting in a School?

    A.1.3 VA
    B.3.0 VA
    C.4.5 VA
    D.1.2 VA
    B3.0 VA

    Explanation: Table 220.12 (NEC 2023) lists Schools at 3.0 VA/sq. ft.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  19. Q19.Using the Optional Method (220.82) for a dwelling unit, the first 10 kVA of the general load is calculated at 100%, and the remainder is calculated at:

    A.40%
    B.50%
    C.60%
    D.75%
    A40%

    Explanation: NEC 220.82(B) Optional Calculation: First 10 kVA at 100%, remainder at 40%.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  20. Q20.According to NEC 2026, Article 120.4(A) allows the load calculation to be reduced when which of the following is installed?

    A.Energy Management System (EMS)
    B.Solar Photovoltaic System
    C.High-efficiency transformers
    D.Power Factor Correction Capacitors
    AEnergy Management System (EMS)

    Explanation: NEC 2026 Article 120.4(A) (formerly in 220) explicitly allows Energy Management Systems to control the maximum load, permitting the calculation to be based on the setpoint of the EMS.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  21. Q21.Heavy-duty lampholders shall be calculated at a minimum of _____ per lampholder.

    A.180 VA
    B.300 VA
    C.600 VA
    D.750 VA
    C600 VA

    Explanation: NEC 220.14(E) assigns a unit load of 600 VA for heavy-duty lampholders.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  22. Q22.For a Farm Service, the load for the largest motor is calculated at:

    A.100%
    B.125%
    C.150%
    D.200%
    B125%

    Explanation: NEC 220.103 (Farm Loads) requires the largest motor to be calculated at 125% of its full-load current rating, similar to standard motor feeders.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  23. Q23.A hotel has 100 guest rooms. The general lighting demand factor for the first 20,000 VA is 50%. What is the demand factor for the next 80,000 VA?

    A.30%
    B.40%
    C.50%
    D.100%
    B40%

    Explanation: NEC Table 220.42 (Hotels/Motels): First 20,000 VA @ 50%, Next 80,000 VA @ 40%, Remainder @ 30%.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  24. Q24.Under NEC 2026, where would you find the requirements for calculating the load of Electric Vehicle Supply Equipment (EVSE)?

    A.Article 220.57
    B.Article 120.6
    C.Article 625.41
    D.Article 310.12
    AArticle 220.57

    Explanation: The specific calculation for EVSE loads is located in Article 220 (Branch Circuits/Feeders), specifically 220.57 (New/Revised), though Article 625 contains the equipment rules. 220.57 requires 100% of the rating.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  25. Q25.What is the feeder demand load for a 5 kW household electric clothes dryer?

    A.4,000 VA
    B.5,000 VA
    C.5,500 VA
    D.3,500 VA
    B5,000 VA

    Explanation: NEC 220.54 requires a minimum of 5,000 VA or the nameplate rating, whichever is larger. Since the dryer is 5 kW (5,000 VA), the load is 5,000 VA.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  26. Q26.Calculate the service load for a Marina with 20 boat slips.

    A.60% of total receptacles
    B.70% of total receptacles
    C.80% of total receptacles
    D.100% of total receptacles
    B70% of total receptacles

    Explanation: NEC Table 555.4 provides demand factors for marinas and boatyards. For 15-30 slips, the demand factor is 70%. The 60% factor applies to 31-100 slips.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  27. Q27.For a multifamily dwelling, the house loads (hallway lighting, outdoor lighting, etc.) are calculated based on:

    A.The optional method for dwellings
    B.The standard method for commercial lighting
    C.3 watts per square foot
    D.The number of dwelling units
    BThe standard method for commercial lighting

    Explanation: Common area loads in multifamily dwellings (corridors, lobbies, etc.) are calculated using the commercial lighting rules (Table 220.12) and cannot be included in the dwelling unit demand factors.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  28. Q28.Using the Optional Method (220.82), a heat pump without supplemental heat is calculated at _____ of the nameplate rating.

    A.65%
    B.100%
    C.125%
    D.40%
    B100%

    Explanation: NEC 220.82(C)(2) requires heat pumps without supplemental electric heat to be calculated at 100% of the nameplate rating.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  29. Q29.Calculate the supply conductor ampacity for a resistance welder with a 50% duty cycle and a primary current of 60A.

    A.30 Amps
    B.42 Amps
    C.60 Amps
    D.75 Amps
    B42 Amps

    Explanation: NEC 630.31(A)(2) states the multiplier for a 50% duty cycle is 0.71. 60A * 0.71 = 42.6A (approx 42-43A).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  30. Q30.In an office building, what demand factor can be applied to receptacle loads in excess of 10 kVA?

    A.40%
    B.50%
    C.70%
    D.100%
    B50%

    Explanation: NEC Table 220.44 allows a demand factor of 50% for receptacle loads over 10 kVA in other than dwelling units.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  31. Q31.A 3-phase, 4-wire feeder supplies a non-linear load (harmonics present). How must the neutral conductor be sized?

    A.It can be reduced to 70%
    B.It must be capable of carrying the maximum unbalanced load without reduction
    C.It must be 125% of the phase conductors
    D.It can be sized at 50% of the phase conductors
    BIt must be capable of carrying the maximum unbalanced load without reduction

    Explanation: NEC 220.61(C) prohibits the reduction of the neutral capacity for that portion of the load that consists of nonlinear loads (which produce harmonic currents that add in the neutral).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  32. Q32.Under NEC 2026, Article 120.2 includes definitions specifically applicable to load calculations. Which term is newly defined or clarified here for calculation purposes?

    A.Continuous Load
    B.Floor Area
    C.Demand Factor
    D.Coincident Load
    BFloor Area

    Explanation: NEC 2026 explicitly defines the method for determining 'Floor Area' in Article 120, standardizing how measurements are taken (outside dimensions, excluding garages/open porches).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  33. Q33.Track lighting in a single-family dwelling is calculated at:

    A.150 VA per 2 feet
    B.75 VA per foot
    C.Zero (It is part of the general lighting load)
    D.Maximum wattage of the track
    CZero (It is part of the general lighting load)

    Explanation: NEC 220.43(B) Exception states that track lighting in dwelling units is not calculated separately; it is considered covered by the 3 VA/sq. ft. general lighting load.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  34. Q34.What is the maximum number of duplex receptacles allowed on a 20A, 120V branch circuit in a commercial office building (assuming continuous load is not a factor)?

    A.10
    B.13
    C.16
    D.No limit
    B13

    Explanation: Commercial receptacles are calculated at 180 VA each. Circuit capacity = 120V * 20A = 2400 VA. 2400 / 180 = 13.33. Max is 13 receptacles.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  35. Q35.A dwelling unit has a dishwasher (1200 VA), disposal (900 VA), and trash compactor (1000 VA). Can the 75% demand factor be applied to these appliances?

    A.Yes
    B.No
    C.Only if they are on different circuits
    D.Only if the service is over 200A
    BNo

    Explanation: NEC 220.53 requires FOUR or more appliances fastened in place to apply the 75% demand factor. There are only three here.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  36. Q36.When sizing a service for a building with 100A of non-continuous load and 50A of continuous load, the minimum service rating must be at least:

    A.150 Amps
    B.162.5 Amps
    C.175 Amps
    D.200 Amps
    B162.5 Amps

    Explanation: NEC 215.2(A)(1) / 230.42 require service conductors to be sized at 100% of non-continuous load + 125% of continuous load. 100 + (50 * 1.25) = 100 + 62.5 = 162.5 Amps.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  37. Q37.What is the general lighting load per square foot for a Warehouse?

    A.0.5 VA
    B.1.0 VA
    C.1.5 VA
    D.0.25 VA
    D0.25 VA

    Explanation: NEC Table 220.12 (2023 edition) lists storage spaces such as warehouses at 0.25 VA per square foot. This value was updated in the 2020/2023 cycle from higher prior editions, reflecting that storage areas have minimal lighting demands compared to occupied commercial spaces.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  38. Q38.For a Recreational Vehicle (RV) Park, what is the demand factor for a service supplying 15 sites?

    A.100%
    B.75%
    C.50%
    D.45%
    D45%

    Explanation: NEC Table 551.73(A) gives the demand factor for 13-15 RV sites as 45%.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  39. Q39.Mobile home park services are calculated based on the number of mobile homes. For a park with 25 mobile homes, what is the demand factor?

    A.25%
    B.24%
    C.23%
    D.22%
    B24%

    Explanation: NEC Table 550.31: For 25 mobile homes, the demand factor is 24%.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  40. Q40.Calculate the demand load for one 10 kW range and one 16 kW range in a dwelling unit.

    A.11 kW
    B.11.55 kW
    C.12.65 kW
    D.13.0 kW
    B11.55 kW

    Explanation: Per NEC Table 220.55 Note 2, for ranges of unequal ratings, calculate based on the average rating. Average = (10 + 16) / 2 = 13 kW. Column C demand for 2 appliances is 11 kW. Since 13 kW exceeds 12 kW by 1 kW, increase the 11 kW demand by 5% per kW over 12. 11 kW x 1.05 = 11.55 kW.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  41. Q41.Calculate the demand load for a single household electric range rated at 16 kW.

    A.8.0 kW
    B.9.6 kW
    C.11.2 kW
    D.16.0 kW
    B9.6 kW

    Explanation: NEC Table 220.55 Note 1: For ranges over 12 kW, increase the 8 kW demand by 5% for each kW over 12. 16 - 12 = 4 kW excess. 4 * 5% = 20%. 8 kW * 1.20 = 9.6 kW.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  42. Q42.When calculating the feeder for a 3-phase, 480V system with a total load of 100 kVA, what is the current in Amperes?

    A.120 Amps
    B.208 Amps
    C.240 Amps
    D.100 Amps
    A120 Amps

    Explanation: Amps = VA / (Volts * 1.732). 100,000 / (480 * 1.732) = 100,000 / 831.4 = 120.2 Amps.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  43. Q43.Recessed lighting fixtures for a commercial building must be calculated based on:

    A.60 watts per fixture
    B.The maximum volt-ampere rating of the equipment and lamps
    C.180 VA per fixture
    D.The actual installed bulb wattage
    BThe maximum volt-ampere rating of the equipment and lamps

    Explanation: NEC 220.14(D) requires the load to be calculated based on the maximum volt-ampere rating of the equipment and lamps for which the luminaire is rated.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  44. Q44.What is the minimum service rating for a single-family dwelling with six or more 2-wire branch circuits?

    A.60 Amps
    B.100 Amps
    C.125 Amps
    D.200 Amps
    B100 Amps

    Explanation: NEC 230.79(C) requires a minimum 100-ampere rating for a single-family dwelling service.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  45. Q45.When adding loads to an existing service, NEC 220.87 permits the calculation to be based on the maximum demand data for a 1-year period. If such data is not available, a ____ period can be used.

    A.30-day
    B.60-day
    C.90-day
    D.6-month
    A30-day

    Explanation: NEC 220.87 Exception allows a 30-day period of recording demand data if 1-year data is not available.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  46. Q46.In NEC 2026, Article 625 (EVs) mandates that Energy Management Systems (EMS) used to control EV loads must be:

    A.Wireless only
    B.Listed
    C.Manually operated
    D.Connected to the utility meter
    BListed

    Explanation: A key safety enforcement in 2026 is that EMS controlling EV loads (to reduce service calculations) must be Listed equipment to ensure reliability.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  47. Q47.What is the minimum feeder load for a 120V circuit supplying a continuous lighting load of 16A?

    A.16 Amps
    B.20 Amps
    C.24 Amps
    D.30 Amps
    B20 Amps

    Explanation: Continuous loads are calculated at 125%. 16A * 1.25 = 20 Amps.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  48. Q48.For a multifamily dwelling using the Standard Method, a demand factor of 75% may be applied to:

    A.The total lighting load
    B.Four or more fixed appliances fastened in place
    C.The heating and air conditioning load
    D.The dryer load
    BFour or more fixed appliances fastened in place

    Explanation: NEC 220.53 permits a demand factor of 75% for four or more appliances fastened in place (other than ranges, dryers, space heating, and AC) served by the same feeder.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  49. Q49.Calculate the feeder neutral load for a household electric range rated 14 kW.

    A.8.8 kW
    B.6.16 kW
    C.9.6 kW
    D.14.0 kW
    B6.16 kW

    Explanation: Step 1: Feeder demand (hot) for 14 kW range = 8.8 kW (Table 220.55 Col C). Step 2: Neutral demand is 70% of feeder demand. 8.8 kW * 0.70 = 6.16 kW.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  50. Q50.A commercial kitchen has three pieces of thermostatic electric cooking equipment. What demand factor is applied?

    A.65%
    B.70%
    C.80%
    D.90%
    D90%

    Explanation: NEC Table 220.56: For 3 units of kitchen equipment, the demand factor is 90%.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  51. Q51.In the Optional Method for multifamily dwellings (220.84), the house loads must be calculated using:

    A.Article 220.84 demand factors
    B.Standard Method (Part III of Article 220)
    C.Optional Method (220.82)
    D.A flat rate of 5000 VA
    BStandard Method (Part III of Article 220)

    Explanation: NEC 220.84(A)(3) requires that house loads (common areas) be calculated in accordance with Part III of Article 220 (Standard Method) and added to the dwelling unit loads.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  52. Q52.Using the Optional Method (220.82) for a single dwelling, how is the air conditioning load calculated?

    A.100% of nameplate rating
    B.40% of nameplate rating
    C.125% of nameplate rating
    D.50% of nameplate rating
    A100% of nameplate rating

    Explanation: NEC 220.82(C)(1) requires air conditioning to be calculated at 100% of the nameplate rating.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  53. Q53.What is the minimum unit load for a heavy-duty lampholder used in a calculation?

    A.180 VA
    B.360 VA
    C.600 VA
    D.1200 VA
    C600 VA

    Explanation: NEC 220.14(E) sets the minimum load for heavy-duty lampholders at 600 volt-amperes.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  54. Q54.When calculating the load for a hospital, the general lighting load is:

    A.1.3 VA/sq ft
    B.1.6 VA/sq ft
    C.2.0 VA/sq ft
    D.3.5 VA/sq ft
    B1.6 VA/sq ft

    Explanation: NEC Table 220.12 (2023) lists 'Hospital' at 1.6 VA per square foot.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  55. Q55.A feeder supplies 5 household dryers. What is the demand factor?

    A.80%
    B.85%
    C.100%
    D.70%
    B85%

    Explanation: NEC Table 220.54: For 5 dryers, the demand factor is 85%.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  56. Q56.The load for a recessed luminaire is based on:

    A.The wattage of the lamp installed
    B.The maximum VA rating of the equipment
    C.60 watts
    D.100 watts
    BThe maximum VA rating of the equipment

    Explanation: NEC 220.14(D) requires the calculation to be based on the maximum VA rating of the equipment and lamps for which the luminaire is rated.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  57. Q57.Calculate the amperage for a 3-phase, 208V load of 50 kVA.

    A.139 Amps
    B.240 Amps
    C.416 Amps
    D.120 Amps
    A139 Amps

    Explanation: I = VA / (V * 1.732). 50,000 / (208 * 1.732) = 50,000 / 360.25 = 138.8 Amps (Round to 139).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  58. Q58.For a service upgrade where 1-year demand data is used (220.87), the new load is added to the maximum demand at ____ of the new load's rating.

    A.100%
    B.125%
    C.80%
    D.150%
    B125%

    Explanation: NEC 220.87(2) requires the new load to be added at 125% of the continuous load plus the noncontinuous load (or essentially calculated per code rules, often 125% if continuous). However, the text says 'The new load... shall be added'. It implies adding the calculated load. Standard calculation rules apply (125% continuous).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  59. Q59.Calculate the general lighting load for a 12,000 sq. ft. Office Building.

    A.15,600 VA
    B.36,000 VA
    C.42,000 VA
    D.12,000 VA
    A15,600 VA

    Explanation: NEC Table 220.12 (2023) lists Office at 1.3 VA/sq ft. 12,000 * 1.3 = 15,600 VA.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  60. Q60.A motor-generator arc welder has a duty cycle of 60%. What is the multiplier for the supply conductors?

    A.0.78
    B.0.63
    C.1.00
    D.0.89
    A0.78

    Explanation: NEC Table 630.11(A): For a motor-generator welder with a 60% duty cycle, the multiplier is 0.78.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  61. Q61.Which of the following loads is considered a Continuous Load?

    A.A household range
    B.Lighting in a commercial store
    C.A bathroom receptacle
    D.A garbage disposal
    BLighting in a commercial store

    Explanation: NEC 100 defines Continuous Load as max current for 3 hours or more. Commercial lighting is generally considered continuous. Household appliances are intermittent.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  62. Q62.When using the Optional Method for a new restaurant (220.88), if the total connected load is 300 kVA, the first 200 kVA is calculated at 80% and the remainder at:

    A.50%
    B.60%
    C.70%
    D.40%
    A50%

    Explanation: NEC 220.88 (New Restaurants) Table: First 200 kVA @ 80%, Remainder @ 50%.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  63. Q63.NEC 2026 Article 220.53 (Appliance Demand Factors) was revised. Which appliance is now explicitly EXCLUDED from the 75% demand factor group?

    A.Dishwasher
    B.Electric Vehicle Supply Equipment (EVSE)
    C.Trash Compactor
    D.Water Heater
    BElectric Vehicle Supply Equipment (EVSE)

    Explanation: NEC 2026 clarifies that EVSE cannot be grouped with standard household appliances for the 75% demand factor; it has its own section (220.57).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  64. Q64.Under NEC 2026, Article 120.4(B) states that if a building is designed for future expansion, the calculated load:

    A.Must include the projected future load
    B.Shall only include the current connected load
    C.Shall include 125% of the spare capacity
    D.Is not required to address future load
    AMust include the projected future load

    Explanation: NEC 2026 Art 120.4(B) explicitly permits (and in some design contexts requires consideration of) future expansion loads to be included in the calculation if specified.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  65. Q65.In NEC 2026, where is the requirement for calculating the load of a 'Limited Energy System' (like PoE) located?

    A.Article 725
    B.Article 220.14(M)
    C.Article 722
    D.Article 120
    CArticle 722

    Explanation: While 220 covers general power, NEC 2026 Article 722 (Cables for Power-Limited Circuits) and associated articles for Class 4 systems govern the specifics of these loads.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  66. Q66.NEC 2026 220.57 mandates that EVSE loads be calculated at:

    A.100% of the rating
    B.125% of the rating
    C.80% of the rating
    D.Based on the EMS setting only
    A100% of the rating

    Explanation: NEC 2026 Section 220.57 requires that EVSE loads be calculated at 100% of the nameplate rating. While EVSE circuits are typically continuous loads and must be sized at 125% for conductor and overcurrent protection purposes, the load calculation value used in the service or feeder demand calculation is the full nameplate rating. Energy management system reductions may apply under 220.57 when an EMS is installed.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  67. Q67.According to NEC 2026 Article 120.3, when measuring the floor area of a dwelling unit, which area is NOT included?

    A.Habitable rooms
    B.Open porches and garages
    C.Bathrooms
    D.Hallways
    BOpen porches and garages

    Explanation: Article 120.3 (Standardizing 220.11) reiterates that open porches, garages, and unused or unfinished spaces are not included in the floor area calculation.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  68. Q68.Using the 2023 NEC, what is the general lighting and receptacle load for a 2,000 sq ft single-family dwelling before demand factors?

    A.4,000 VA
    B.6,000 VA
    C.8,000 VA
    D.10,500 VA
    B6,000 VA

    Explanation: The 2023 NEC general lighting and general-use receptacle load for a dwelling is 3 VA per square foot: 2,000 x 3 = 6,000 VA. (In the 2026 NEC this drops to 2 VA per square foot.)

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  69. Q69.After adding two small-appliance circuits and one laundry circuit, a dwelling has 10,500 VA of general load. What is the load after applying the standard demand factors?

    A.3,675 VA
    B.5,625 VA
    C.7,350 VA
    D.10,500 VA
    B5,625 VA

    Explanation: The standard method counts the first 3,000 VA at 100% and the remainder at 35%: 3,000 + (7,500 x 0.35 = 2,625) = 5,625 VA (Table 220.42).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  70. Q70.Under the 2026 NEC, the dwelling general lighting load for feeder and service calculations changed to how many VA per square foot?

    A.1 VA
    B.2 VA
    C.3 VA
    D.3.5 VA
    B2 VA

    Explanation: The 2026 NEC reduces the dwelling general lighting/receptacle load from 3 VA to 2 VA per square foot, and relocates load-calculation rules from Article 220 to a new Article 120.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime