Journeyman Electrician Exam
Conduit Fill Practice Questions
33 practice questions with detailed explanations — aligned to the Journeyman Electrician Exam.
Master Conduit Fill to boost your score on the Journeyman Electrician Exam. Each question below mirrors the style and difficulty of real exam questions, complete with detailed explanations so you understand the why behind every answer. Work through all 33 questions, review any that trip you up, and use the related topics below to round out your preparation.
Q1.When determining the number of conductors in a conduit, which Chapter 9 Table is used for the dimensions of the conductors?
A.Table 1B.Table 4C.Table 5D.Table 8✓C. Table 5Explanation: Chapter 9 Table 5 gives the specific dimensions (area) of insulated conductors (THHN, XHHW, etc.). Table 4 is for Conduit dimensions. Table 1 is percentages.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q2.What is the maximum fill percentage for a conduit containing only one conductor?
A.31%B.40%C.53%D.60%✓C. 53%Explanation: Chapter 9 Table 1 allows 53% fill for 1 conductor.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q3.When calculating conduit fill for three or more conductors, the maximum permitted fill is:
A.31%B.40%C.53%D.60%✓B. 40%Explanation: Chapter 9 Table 1 allows 40% fill for over 2 conductors.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q4.A conduit nipple (24 inches or less) can be filled to a maximum of:
A.40%B.53%C.60%D.31%✓C. 60%Explanation: Chapter 9 Table 1 Note 4 permits nipples not exceeding 24 inches to be filled to 60%.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q5.When three conductors of the same size and insulation are installed in a conduit, you should refer to:
A.Chapter 9, Table 1B.Chapter 9, Table 5C.Annex CD.Table 310.16✓C. Annex CExplanation: Annex C provides pre-calculated lookup tables for the maximum number of conductors of the same size and type in various conduits (based on the 40% rule).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q6.The 'Jam Ratio' warning applies when determining the number of conductors for:
A.Conduits with 3 conductorsB.Conduits with 2 conductorsC.NipplesD.Rectangular raceways✓A. Conduits with 3 conductorsExplanation: Chapter 9 Table 1 FPN No. 2 warns about the jam ratio when installing THREE conductors. If the ratio of conduit ID to conductor OD is between 2.8 and 3.2, jamming can occur.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q7.When calculating fill for a combination of different conductor sizes, you must use:
A.The pre-calculated tables in Annex CB.The specific dimensions from Tables 4 and 5C.The approximate diameter method (Area = D squared)D.The dimensions of the largest conductor for all✓B. The specific dimensions from Tables 4 and 5Explanation: For mixed wire sizes, you must calculate the total area using the specific conductor areas from Table 5 and compare it to the allowable area (40%) of the conduit from Table 4.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q8.Equipment grounding conductors are:
A.Ignored for conduit fill calculationsB.Counted for fill calculationsC.Counted as half a conductorD.Only counted if insulated✓B. Counted for fill calculationsExplanation: Chapter 9 Note 3 states that equipment grounding or bonding conductors, where installed, shall be included when calculating conduit fill.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q9.In a wireway, the maximum fill for conductors (sum of cross-sectional areas) is:
A.20%B.30%C.40%D.75%✓A. 20%Explanation: NEC 376.22(A) limits the sum of cross-sectional areas of all contained conductors in a wireway to 20% of the interior cross-sectional area of the wireway.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q10.If a multiconductor cable (like a fiber optic cable or tray cable) is installed in a conduit, how is its fill calculated?
A.Using the sum of the individual wiresB.Using the cross-sectional area of the entire cable assemblyC.It is treated as one conductor (53% fill allowed)D.It is exempt from fill rules✓B. Using the cross-sectional area of the entire cable assemblyExplanation: NEC Chapter 9, Note 9 states that a multiconductor cable, optical fiber cable, or flexible cord shall be treated as a single conductor when calculating conduit fill percentage. The cross-sectional area of the entire cable assembly is used as the area for that single entry in the fill calculation, compared against the applicable fill percentage from Table 1.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q11.For the purpose of conduit fill, Compact Stranded conductors:
A.Have the same area as standard strandedB.Have a specific Table 5A for dimensionsC.Are not permitted in conduitD.Are treated as solid wire✓B. Have a specific Table 5A for dimensionsExplanation: Chapter 9 Table 5A provides specific dimensions for Compact Stranded aluminum and copper conductors, which are smaller than standard concentric stranded conductors.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q12.When conductors are installed in surface metal raceways (Wiremold), if the raceway is used for splices (like a wireway), the fill must not exceed 20%. If it contains only conductors (no splices), the fill is:
A.20%B.40%C.53%D.75%✓B. 40%Explanation: NEC 386.22 invokes the standard conduit fill tables (40% for >2 conductors) unless the specific manufacturer listing says otherwise, but usually surface raceways follow standard fill or specific capacity tables provided by manufacturer. However, NEC 386.22 says 'shall not exceed the number... permitted in Table 1 of Chapter 9', which is 40%.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q13.Which conduit type generally has the largest internal diameter (and thus most fill capacity) for the same trade size?
A.Schedule 80 PVCB.Schedule 40 PVCC.EMTD.Flexible Metal Conduit✓C. EMTExplanation: EMT (thin wall) typically has a larger ID than Schedule 40 or 80 PVC (which have thicker walls). RMC is also thick. EMT is usually the 'roomiest' for fill among rigid types. (Comparing Table 4 data: 1 inch EMT Area = 0.864 sq in. 1 inch Sch 40 PVC = 0.829. 1 inch Sch 80 = 0.716).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q14.When conduit fill calculations result in a decimal of 0.8 or larger, you may:
A.Round down to the next lower whole numberB.Round up to the next higher whole numberC.Ignore the decimalD.Must use exact decimal✓B. Round up to the next higher whole numberExplanation: Chapter 9 Note 7 states that when the calculation results in a decimal of 0.8 or larger, it may be rounded to the next higher whole number.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q15.For a conduit containing 2 conductors, the maximum fill is:
A.31%B.40%C.53%D.60%✓A. 31%Explanation: Chapter 9 Table 1 limits fill for exactly 2 conductors to 31%.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q16.When calculating the number of conductors allowed in a conduit, if the conductors are all the same size (e.g., all 12 AWG THHN), is it permitted to use the Annex C tables instead of calculating area?
A.Yes, always.B.No, calculation is always required.C.Only for PVC conduit.D.Only for services.✓A. Yes, always.Explanation: Annex C is specifically provided for the common condition where all conductors in a raceway are of the same size and insulation type, allowing a direct lookup without manual calculation.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q17.The maximum fill for a Cellular Metal Floor Raceway containing splices at a junction box is:
A.20%B.40%C.75%D.100%✓C. 75%Explanation: NEC 374.56 states that conductors shall not fill the cellular metal floor raceway to more than 40% of the cross-sectional area, EXCEPT at junction boxes/splices where it is permitted to be filled to 75%.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q18.Which table should be used to find the actual cross-sectional area of a specific trade size of Electrical Metallic Tubing (EMT)?
A.Chapter 9, Table 4B.Chapter 9, Table 5C.Chapter 9, Table 8D.Annex C✓A. Chapter 9, Table 4Explanation: Chapter 9 Table 4 lists the dimensions and allowable fill areas for all raceway types (EMT, RMC, PVC, etc.).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q19.When installing conductors in a short section of conduit used to protect cables from physical damage (sleeve), the conduit fill is permitted to be:
A.40%B.53%C.60%D.100% (practicable)✓D. 100% (practicable)Explanation: Chapter 9 Table 1 Note 2 states that the table does not apply to short sections of conduit used to protect exposed wiring from physical damage (sleeves). Use is limited only by practicability (ability to pull without damage).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q20.Determine the maximum number of 12 AWG THHN conductors permitted in 1/2 inch EMT.
A.5B.9C.12D.16✓B. 9Explanation: Using Annex C, Table C.1 (EMT): For 1/2 inch EMT, 12 AWG THHN, the max number is 9.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q21.For Flexible Metal Conduit (FMC) containing 3 or more conductors, the maximum fill is:
A.31%B.40%C.53%D.60%✓B. 40%Explanation: FMC follows the standard Table 1 percentages: 40% for over 2 conductors.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q22.Strut-type channel raceways can be filled to _____ if they contain joiners but no splices.
A.20%B.25%C.40%D.75%✓C. 40%Explanation: NEC 384.22 allows 40% fill for strut-type channel raceways (standard raceway fill).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q23.When a conduit contains only lead-covered conductors, the maximum fill is:
A.30%B.38%C.40%D.55%✓B. 38%Explanation: Older editions of NEC Chapter 9 Table 1 specified a reduced fill percentage of 38% for conduits containing lead-covered conductors, to account for the additional bulk and rigidity of the lead sheathing. While modern NEC editions have streamlined Table 1 to use standard percentages, this 38% value remains the historically tested reference for lead-covered conductor fill calculations on many licensing exams.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q24.What is the area (sq in) of a 10 AWG THHN conductor?
A.0.0172 sq inB.0.0211 sq inC.0.0243 sq inD.0.0824 sq in✓B. 0.0211 sq inExplanation: Per NEC Chapter 9, Table 5, the cross-sectional area of a 10 AWG THHN/THWN conductor is 0.0211 square inches. This value is used when calculating conduit fill percentages. Table 5 is the standard reference for conductor areas in fill calculations for all commonly used conductor types and sizes.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q25.The cross-sectional area of a Scheduled 80 PVC conduit is _____ than that of a Schedule 40 PVC conduit of the same trade size.
A.LargerB.SmallerC.The sameD.Depends on temperature✓B. SmallerExplanation: Schedule 80 has a thicker wall for physical protection, which reduces the internal cross-sectional area available for conductors.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q26.When pulling three conductors into a raceway, if the ratio of the raceway diameter to the conductor diameter is approx 3.0, what problem may occur?
A.OverheatingB.JammingC.ArcingD.Voltage Drop✓B. JammingExplanation: This is the 'Jam Ratio' (FPN No 2 to Table 1). Conductors can align in a triangular formation and jam against the walls.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q27.Underfloor raceways (Article 390) combined with cables: The combined cross-sectional area of all conductors and cables shall not exceed:
A.20%B.40%C.50%D.75%✓B. 40%Explanation: NEC 390.22 states that the combined cross-sectional area of all conductors or cables shall not exceed 40% of the interior cross-sectional area of the raceway.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q28.For a 24-inch nipple, fill is allowed up to 60%. If the nipple is 25 inches long, the maximum fill is:
A.31%B.40%C.53%D.60%✓B. 40%Explanation: Once the conduit exceeds 24 inches, it is no longer a nipple under Note 4, and standard Table 1 rules apply (40% for 3+ wires).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q29.Liquidtight Flexible Metal Conduit (LFMC) of 3/8 inch trade size is permitted for:
A.ServicesB.Fixture tails (up to 6 ft) and motor terminalsC.General wiring in lengths over 100 ftD.Underground runs✓B. Fixture tails (up to 6 ft) and motor terminalsExplanation: NEC 350.20 (size) generally starts at 1/2 inch, but 350.20(A) Exception permits 3/8 inch for specific uses like enclosed leads of motors or luminaire whips (fixture tails) not exceeding 6 feet.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q30.When conductors are installed in an auxiliary gutter, the sum of the cross-sectional areas of all contained conductors shall not exceed _____ of the interior cross-sectional area.
A.20%B.40%C.50%D.75%✓A. 20%Explanation: NEC 366.22(A) limits the fill of sheet metal auxiliary gutters to 20%.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q31.For calculating fill, if a bare conductor is present, you should use:
A.Table 5 dimensions for THHNB.Table 8 dimensions for bare conductorsC.0.7854 x diameter squaredD.Zero area✓B. Table 8 dimensions for bare conductorsExplanation: Chapter 9 Note 8 states that for bare conductors, the dimensions in Table 8 shall be used.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q32.Per NEC Chapter 9, Table 1, what is the maximum conduit fill for a raceway containing more than two conductors?
A.31%B.40%C.53%D.60%✓B. 40%Explanation: Chapter 9, Table 1 sets fill limits of 53% for one conductor, 31% for two, and 40% for more than two conductors.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q33.How many 12 AWG THHN conductors may be installed in 1/2-inch EMT?
A.7B.9C.12D.16✓B. 9Explanation: 1/2-inch EMT has 0.304 sq in of area; 40% is 0.1216 sq in. A 12 AWG THHN conductor is 0.0133 sq in, so 0.1216 / 0.0133 = 9.1, rounded down to 9 (confirmed by Annex C, Table C.1).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
More Journeyman Electrician Exam Topics
Studying for the Journeyman Electrician exam? Read more about Electrician Prep →