36 practice questions with detailed explanations — aligned to the Journeyman Electrician Exam.

Master GFCI/AFCI to boost your score on the Journeyman Electrician Exam. Each question below mirrors the style and difficulty of real exam questions, complete with detailed explanations so you understand the why behind every answer. Work through all 36 questions, review any that trip you up, and use the related topics below to round out your preparation.

  1. Q1.GFCI protection is required for all 125V through 250V receptacles supplied by single-phase branch circuits rated 150V or less to ground in which of the following dwelling unit locations?

    A.Bedrooms
    B.Kitchens
    C.Dining Rooms
    D.Hallways
    BKitchens

    Explanation: NEC 210.8(A)(6) requires GFCI protection for receptacles in dwelling unit kitchens (where serving countertop surfaces, and now generally all kitchen receptacles in 2023 update).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  2. Q2.For a dwelling unit, a receptacle installed in a finished basement must have GFCI protection.

    A.True
    B.False
    C.Only if it is near a sink
    D.Only if unfinished
    ATrue

    Explanation: NEC 210.8(A)(5) requires GFCI protection for all receptacles in basements of dwelling units, including both finished and unfinished basements. This requirement applies regardless of how the basement is used or finished. The 2020 NEC expanded this requirement to cover all basement receptacles, and the 2023 NEC retains this broader coverage.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  3. Q3.Which appliance requires GFCI protection regardless of whether it is hard-wired or cord-and-plug connected?

    A.Refrigerator
    B.Dishwasher
    C.Trash Compactor
    D.Electric Range
    BDishwasher

    Explanation: NEC 210.8(D) specifically lists dwelling unit dishwashers as requiring GFCI protection.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  4. Q4.Receptacles located outdoors at a dwelling unit must be GFCI protected. An exception applies to:

    A.Receptacles for snow-melting equipment that are not readily accessible
    B.Receptacles for holiday lights
    C.Receptacles on a porch
    D.Receptacles for EV charging
    AReceptacles for snow-melting equipment that are not readily accessible

    Explanation: NEC 210.8(A)(3) Exception to (3): Receptacles that are not readily accessible and are supplied by a branch circuit dedicated to electric snow-melting, deicing, or pipeline and vessel heating equipment shall be permitted to be installed in accordance with 426.28 or 427.22, as applicable (which use GFPE, not Class A GFCI).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  5. Q5.AFCI protection is required for branch circuits supplying outlets in which of the following dormitory unit areas?

    A.Bedrooms and Living Rooms
    B.Bathrooms
    C.Garages
    D.Mechanical Rooms
    ABedrooms and Living Rooms

    Explanation: NEC 210.12(B) requires AFCI protection for outlets in dormitory unit bedrooms, living rooms, hallways, closets, and similar rooms.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  6. Q6.All 125V through 250V receptacles supplied by single-phase branch circuits rated 150V or less to ground installed in commercial kitchens must have GFCI protection. A 'kitchen' is defined as an area with a sink and:

    A.A refrigerator
    B.Permanent provisions for food preparation and cooking
    C.A microwave
    D.A floor drain
    BPermanent provisions for food preparation and cooking

    Explanation: NEC 210.8(B)(2) requires GFCI in non-dwelling unit kitchens. Article 100 defines a kitchen as an area with a sink and permanent provisions for food preparation and cooking.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  7. Q7.GFCI protection is required for outdoor outlets (not just receptacles) for dwelling units that are supplied by single-phase branch circuits rated 150V or less to ground and _____ or less.

    A.20 Amps
    B.30 Amps
    C.50 Amps
    D.60 Amps
    C50 Amps

    Explanation: NEC 210.8(F) requires GFCI protection for outdoor outlets (e.g., hardwired AC units) on dwelling units for circuits rated 50A or less.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  8. Q8.In a commercial building (non-dwelling), GFCI protection is required for receptacles in:

    A.Conference rooms
    B.Offices
    C.Bathrooms
    D.Hallways
    CBathrooms

    Explanation: NEC 210.8(B)(1) requires GFCI protection for receptacles in bathrooms of other than dwelling units.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  9. Q9.Are GFCI receptacles permitted to be installed in a standard octagon box?

    A.Yes, always.
    B.No, only rectangular boxes are permitted.
    C.Yes, if using a listed cover providing a rectangular opening.
    D.No, unless the box is 4 inches deep.
    CYes, if using a listed cover providing a rectangular opening.

    Explanation: NEC 314.25 requires covers to be compatible with the box and device. A round/octagon box is permitted if a cover (mud ring/industrial cover) adapts it to the device.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  10. Q10.Vending machines connected by cord and plug must be:

    A.Hard-wired only
    B.GFCI protected
    C.Located indoors
    D.Supplied by a dedicated 20A circuit
    BGFCI protected

    Explanation: NEC 422.51 requires cord-and-plug-connected vending machines to have GFCI protection (often integral to the cord, or via the receptacle).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  11. Q11.When replacing a receptacle in a location that now requires GFCI protection (but didn't when built), the replacement receptacle must be:

    A.A standard receptacle
    B.A GFCI protected receptacle
    C.A twist-lock receptacle
    D.Marked 'No Equipment Ground'
    BA GFCI protected receptacle

    Explanation: NEC 406.4(D)(3) requires that where a receptacle is replaced in a location where GFCI protection is currently required, the replacement must be GFCI protected.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  12. Q12.AFCI protection is required for which of the following locations in a Guest Room of a Hotel?

    A.Bathroom only
    B.Kitchenette only
    C.All 120V, 15A and 20A branch circuits supplying outlets in the room
    D.Not required for hotels
    CAll 120V, 15A and 20A branch circuits supplying outlets in the room

    Explanation: NEC 210.12(C) extends the AFCI requirements of dwelling units to guest rooms and guest suites of hotels and motels.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  13. Q13.Receptacles in crawl spaces at or below grade level require GFCI protection:

    A.Only in dwellings
    B.Only in commercial buildings
    C.In both dwelling and non-dwelling units
    D.Never
    CIn both dwelling and non-dwelling units

    Explanation: NEC 210.8(A)(4) (Dwellings) and 210.8(B)(9) (Other than dwellings) both require GFCI protection for crawl space receptacles.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  14. Q14.Electric drinking fountains connected by cord and plug require:

    A.AFCI protection
    B.GFCI protection
    C.A dedicated circuit
    D.Twist-lock plugs
    BGFCI protection

    Explanation: NEC 422.52 requires GFCI protection for electric drinking fountains.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  15. Q15.In a dwelling unit, a receptacle installed within _____ of the outside edge of a sink requires GFCI protection.

    A.3 feet
    B.4 feet
    C.6 feet
    D.8 feet
    C6 feet

    Explanation: NEC 210.8(A)(7) requires GFCI protection for receptacles installed within 6 feet (1.8 m) of the top inside edge of the bowl of the sink.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  16. Q16.If a branch circuit is modified, replaced, or extended in a dwelling unit bedroom, AFCI protection must be provided if the extension is longer than:

    A.1 foot
    B.3 feet
    C.6 feet
    D.Any length
    C6 feet

    Explanation: NEC 210.12(D) Exception: AFCI is not required if the extension is less than 6 feet and does not include any additional outlets or devices. If > 6 ft or adding outlet, AFCI is required.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  17. Q17.Boat hoists installed at dwelling unit docking facilities must have:

    A.AFCI protection
    B.GFCI protection
    C.Disconnects within 5 feet
    D.Emergency stops
    BGFCI protection

    Explanation: NEC 210.8(F) (or formerly 210.8(C)) requires GFCI protection for outlets supplying boat hoists.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  18. Q18.In other than dwelling units, GFCI protection is required for indoor receptacles located within _____ of the outside edge of a bathtub or shower stall.

    A.3 feet
    B.4 feet
    C.6 feet
    D.10 feet
    C6 feet

    Explanation: NEC 210.8(B)(11) requires GFCI protection for receptacles within 6 feet of the outside edge of the bathtub or shower stall in non-dwelling units (added in recent codes to match dwelling rules).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  19. Q19.Which method is permitted to provide AFCI protection?

    A.A listed combination-type AFCI circuit breaker
    B.An outlet branch-circuit type AFCI receptacle as the first outlet (with metal conduit to panel)
    C.A supplemental AFCI breaker
    D.Both A and B
    DBoth A and B

    Explanation: NEC 210.12(A) allows multiple methods, including a Combination-Type AFCI breaker (A) or an Outlet Branch-Circuit AFCI receptacle (B) if the home run is protected (e.g., metal raceway or concrete encasement).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  20. Q20.High-pressure spray washing machines connected by cord and plug must have:

    A.Factory installed GFCI
    B.A twist lock plug
    C.Double insulation
    D.An emergency switch
    AFactory installed GFCI

    Explanation: NEC 422.49 requires high-pressure spray washers to have a factory-installed GFCI (integral to the plug or cord).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  21. Q21.GFCI protection shall be provided for lighting outlets in crawl spaces.

    A.True
    B.False
    C.Only if LED
    D.Only if switched
    ATrue

    Explanation: NEC 210.8(C) requires GFCI protection for lighting outlets in crawl spaces (dwelling and non-dwelling).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  22. Q22.A receptacle for a gas range in a dwelling unit kitchen requires GFCI protection.

    A.True
    B.False
    ATrue

    Explanation: NEC 210.8(A)(6) requires GFCI protection for receptacles in kitchens. No exception exists for the range receptacle (gas ignition/clock). (Older codes limited it to countertops, current code is ALL kitchen receptacles).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  23. Q23.Tire inflation machines (automotive vacuum machines) provided for public use must be GFCI protected.

    A.True
    B.False
    ATrue

    Explanation: NEC 422.51 (and similar 422 sections) requires GFCI for tire inflation/vacuum machines for public use.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  24. Q24.Wall-mounted control units for in-floor radiant heating in bathrooms must be GFCI protected.

    A.True
    B.False
    BFalse

    Explanation: NEC 424.44(E) requires GFCI protection for the heating cables in floor heating systems installed in bathrooms, but this requirement applies to the heating element circuit, not to the wall-mounted control unit or thermostat itself. Unless the control unit incorporates a receptacle outlet or is otherwise covered by a separate GFCI requirement, the wall-mounted thermostat is not independently required to have GFCI protection.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  25. Q25.Sump pumps installed in dwelling unit basements require GFCI protection.

    A.True, always
    B.False, never
    C.Only if cord and plug connected
    D.Only if in a finished basement
    ATrue, always

    Explanation: NEC 210.8(A)(5) requires GFCI protection for receptacles in basements. There is NO exception for sump pumps (single outlet exception was removed years ago).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  26. Q26.Three-phase receptacles (up to 250V) in commercial kitchens require GFCI protection.

    A.True
    B.False
    ATrue

    Explanation: NEC 210.8(B) requires GFCI for single-phase receptacles (50A or less) AND three-phase receptacles (100A or less) in locations like kitchens.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  27. Q27.A Class A ground-fault circuit interrupter (GFCI) is designed to trip when the ground-fault current reaches what range?

    A.2–3 mA
    B.4–6 mA
    C.15–20 mA
    D.30–50 mA
    B4–6 mA

    Explanation: A Class A GFCI is designed to trip when the ground-fault current is 4 to 6 mA (nominally 5 mA). This threshold is set to protect people from electric shock and is the device referenced throughout NEC 210.8.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  28. Q28.Per NEC 210.8, 125-volt, 15- and 20-ampere receptacles installed in a dwelling-unit bathroom must have what protection?

    A.AFCI only
    B.GFCI
    C.Surge protection only
    D.No special protection
    BGFCI

    Explanation: NEC 210.8(A) requires GFCI protection for 125-volt, 15- and 20-ampere receptacles in dwelling bathrooms because of their proximity to water.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  29. Q29.NEC 210.8 requires GFCI protection for receptacles located within how many feet of the outside edge of a sink?

    A.3 feet
    B.6 feet
    C.10 feet
    D.Distance is not a factor
    B6 feet

    Explanation: NEC 210.8 requires GFCI protection for 125-volt receptacles located within 6 feet of the outside edge of a sink, in addition to the specific room-based requirements.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  30. Q30.Which dwelling location requires GFCI protection for 125-volt, 15- and 20-ampere receptacles under NEC 210.8(A)?

    A.A finished living-room wall
    B.An unfinished basement
    C.A second-floor hallway
    D.Inside a bedroom closet
    BAn unfinished basement

    Explanation: NEC 210.8(A) lists unfinished basements among the dwelling areas requiring GFCI protection for 125-volt, 15- and 20-ampere receptacles.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  31. Q31.What type of fault is an arc-fault circuit interrupter (AFCI) designed to detect?

    A.Ground faults that shock people
    B.Arcing faults that can start fires
    C.Overloads from too many appliances
    D.Voltage drop on long conductor runs
    BArcing faults that can start fires

    Explanation: An AFCI detects dangerous arcing faults from damaged or loose wiring that can ignite fires. This differs from a GFCI, which detects ground-fault current to protect people from shock. AFCI requirements are found in NEC 210.12.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  32. Q32.NEC 210.12 requires AFCI protection for 120-volt branch circuits supplying outlets in which dwelling-unit areas?

    A.Only outdoor receptacles
    B.Bedrooms and most habitable rooms
    C.Only the kitchen
    D.Only bathrooms
    BBedrooms and most habitable rooms

    Explanation: NEC 210.12 requires AFCI protection for 120-volt, 15- and 20-ampere branch circuits supplying outlets and devices in dwelling-unit kitchens, bedrooms, living rooms, and most other habitable rooms.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  33. Q33.Receptacles serving dwelling kitchen countertop surfaces are required to have what protection?

    A.AFCI only
    B.GFCI
    C.Neither GFCI nor AFCI
    D.Isolated-ground only
    BGFCI

    Explanation: NEC 210.8(A) requires GFCI protection for receptacles serving kitchen countertop surfaces in a dwelling because of their proximity to the sink and water.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  34. Q34.Which statement best describes the difference between GFCI and AFCI protection?

    A.They are the same device with two names
    B.GFCI protects against shock; AFCI protects against arcing fires
    C.GFCI protects against fire; AFCI protects against shock
    D.Both protect only equipment, not people
    BGFCI protects against shock; AFCI protects against arcing fires

    Explanation: A GFCI protects people from shock by tripping on small ground-fault currents (4–6 mA). An AFCI protects against fire by detecting dangerous arcing in wiring. A dual-function breaker combines both.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  35. Q35.Per NEC 210.8(A), 125-volt, 15- and 20-ampere receptacles in a dwelling-unit garage require:

    A.AFCI only
    B.GFCI
    C.No protection if used for a freezer
    D.Only a weather-resistant cover
    BGFCI

    Explanation: NEC 210.8(A) requires GFCI protection for 125-volt, 15- and 20-ampere receptacles in dwelling garages and accessory buildings. Older exceptions for dedicated appliance receptacles have largely been removed in recent code cycles.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  36. Q36.Under NEC 210.8(A), outdoor 125-volt, 15- and 20-ampere receptacles at a dwelling require what protection?

    A.No special protection
    B.GFCI
    C.AFCI only
    D.Protection only above 250 volts
    BGFCI

    Explanation: NEC 210.8(A) requires GFCI protection for outdoor 125-volt, 15- and 20-ampere receptacles at dwellings, since outdoor locations are exposed to moisture.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime