Journeyman Electrician Exam
GFCI/AFCI Practice Questions
36 practice questions with detailed explanations — aligned to the Journeyman Electrician Exam.
Master GFCI/AFCI to boost your score on the Journeyman Electrician Exam. Each question below mirrors the style and difficulty of real exam questions, complete with detailed explanations so you understand the why behind every answer. Work through all 36 questions, review any that trip you up, and use the related topics below to round out your preparation.
Q1.GFCI protection is required for all 125V through 250V receptacles supplied by single-phase branch circuits rated 150V or less to ground in which of the following dwelling unit locations?
A.BedroomsB.KitchensC.Dining RoomsD.Hallways✓B. KitchensExplanation: NEC 210.8(A)(6) requires GFCI protection for receptacles in dwelling unit kitchens (where serving countertop surfaces, and now generally all kitchen receptacles in 2023 update).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q2.For a dwelling unit, a receptacle installed in a finished basement must have GFCI protection.
A.TrueB.FalseC.Only if it is near a sinkD.Only if unfinished✓A. TrueExplanation: NEC 210.8(A)(5) requires GFCI protection for all receptacles in basements of dwelling units, including both finished and unfinished basements. This requirement applies regardless of how the basement is used or finished. The 2020 NEC expanded this requirement to cover all basement receptacles, and the 2023 NEC retains this broader coverage.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q3.Which appliance requires GFCI protection regardless of whether it is hard-wired or cord-and-plug connected?
A.RefrigeratorB.DishwasherC.Trash CompactorD.Electric Range✓B. DishwasherExplanation: NEC 210.8(D) specifically lists dwelling unit dishwashers as requiring GFCI protection.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q4.Receptacles located outdoors at a dwelling unit must be GFCI protected. An exception applies to:
A.Receptacles for snow-melting equipment that are not readily accessibleB.Receptacles for holiday lightsC.Receptacles on a porchD.Receptacles for EV charging✓A. Receptacles for snow-melting equipment that are not readily accessibleExplanation: NEC 210.8(A)(3) Exception to (3): Receptacles that are not readily accessible and are supplied by a branch circuit dedicated to electric snow-melting, deicing, or pipeline and vessel heating equipment shall be permitted to be installed in accordance with 426.28 or 427.22, as applicable (which use GFPE, not Class A GFCI).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q5.AFCI protection is required for branch circuits supplying outlets in which of the following dormitory unit areas?
A.Bedrooms and Living RoomsB.BathroomsC.GaragesD.Mechanical Rooms✓A. Bedrooms and Living RoomsExplanation: NEC 210.12(B) requires AFCI protection for outlets in dormitory unit bedrooms, living rooms, hallways, closets, and similar rooms.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q6.All 125V through 250V receptacles supplied by single-phase branch circuits rated 150V or less to ground installed in commercial kitchens must have GFCI protection. A 'kitchen' is defined as an area with a sink and:
A.A refrigeratorB.Permanent provisions for food preparation and cookingC.A microwaveD.A floor drain✓B. Permanent provisions for food preparation and cookingExplanation: NEC 210.8(B)(2) requires GFCI in non-dwelling unit kitchens. Article 100 defines a kitchen as an area with a sink and permanent provisions for food preparation and cooking.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q7.GFCI protection is required for outdoor outlets (not just receptacles) for dwelling units that are supplied by single-phase branch circuits rated 150V or less to ground and _____ or less.
A.20 AmpsB.30 AmpsC.50 AmpsD.60 Amps✓C. 50 AmpsExplanation: NEC 210.8(F) requires GFCI protection for outdoor outlets (e.g., hardwired AC units) on dwelling units for circuits rated 50A or less.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q8.In a commercial building (non-dwelling), GFCI protection is required for receptacles in:
A.Conference roomsB.OfficesC.BathroomsD.Hallways✓C. BathroomsExplanation: NEC 210.8(B)(1) requires GFCI protection for receptacles in bathrooms of other than dwelling units.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q9.Are GFCI receptacles permitted to be installed in a standard octagon box?
A.Yes, always.B.No, only rectangular boxes are permitted.C.Yes, if using a listed cover providing a rectangular opening.D.No, unless the box is 4 inches deep.✓C. Yes, if using a listed cover providing a rectangular opening.Explanation: NEC 314.25 requires covers to be compatible with the box and device. A round/octagon box is permitted if a cover (mud ring/industrial cover) adapts it to the device.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q10.Vending machines connected by cord and plug must be:
A.Hard-wired onlyB.GFCI protectedC.Located indoorsD.Supplied by a dedicated 20A circuit✓B. GFCI protectedExplanation: NEC 422.51 requires cord-and-plug-connected vending machines to have GFCI protection (often integral to the cord, or via the receptacle).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q11.When replacing a receptacle in a location that now requires GFCI protection (but didn't when built), the replacement receptacle must be:
A.A standard receptacleB.A GFCI protected receptacleC.A twist-lock receptacleD.Marked 'No Equipment Ground'✓B. A GFCI protected receptacleExplanation: NEC 406.4(D)(3) requires that where a receptacle is replaced in a location where GFCI protection is currently required, the replacement must be GFCI protected.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q12.AFCI protection is required for which of the following locations in a Guest Room of a Hotel?
A.Bathroom onlyB.Kitchenette onlyC.All 120V, 15A and 20A branch circuits supplying outlets in the roomD.Not required for hotels✓C. All 120V, 15A and 20A branch circuits supplying outlets in the roomExplanation: NEC 210.12(C) extends the AFCI requirements of dwelling units to guest rooms and guest suites of hotels and motels.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q13.Receptacles in crawl spaces at or below grade level require GFCI protection:
A.Only in dwellingsB.Only in commercial buildingsC.In both dwelling and non-dwelling unitsD.Never✓C. In both dwelling and non-dwelling unitsExplanation: NEC 210.8(A)(4) (Dwellings) and 210.8(B)(9) (Other than dwellings) both require GFCI protection for crawl space receptacles.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q14.Electric drinking fountains connected by cord and plug require:
A.AFCI protectionB.GFCI protectionC.A dedicated circuitD.Twist-lock plugs✓B. GFCI protectionExplanation: NEC 422.52 requires GFCI protection for electric drinking fountains.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q15.In a dwelling unit, a receptacle installed within _____ of the outside edge of a sink requires GFCI protection.
A.3 feetB.4 feetC.6 feetD.8 feet✓C. 6 feetExplanation: NEC 210.8(A)(7) requires GFCI protection for receptacles installed within 6 feet (1.8 m) of the top inside edge of the bowl of the sink.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q16.If a branch circuit is modified, replaced, or extended in a dwelling unit bedroom, AFCI protection must be provided if the extension is longer than:
A.1 footB.3 feetC.6 feetD.Any length✓C. 6 feetExplanation: NEC 210.12(D) Exception: AFCI is not required if the extension is less than 6 feet and does not include any additional outlets or devices. If > 6 ft or adding outlet, AFCI is required.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q17.Boat hoists installed at dwelling unit docking facilities must have:
A.AFCI protectionB.GFCI protectionC.Disconnects within 5 feetD.Emergency stops✓B. GFCI protectionExplanation: NEC 210.8(F) (or formerly 210.8(C)) requires GFCI protection for outlets supplying boat hoists.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q18.In other than dwelling units, GFCI protection is required for indoor receptacles located within _____ of the outside edge of a bathtub or shower stall.
A.3 feetB.4 feetC.6 feetD.10 feet✓C. 6 feetExplanation: NEC 210.8(B)(11) requires GFCI protection for receptacles within 6 feet of the outside edge of the bathtub or shower stall in non-dwelling units (added in recent codes to match dwelling rules).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q19.Which method is permitted to provide AFCI protection?
A.A listed combination-type AFCI circuit breakerB.An outlet branch-circuit type AFCI receptacle as the first outlet (with metal conduit to panel)C.A supplemental AFCI breakerD.Both A and B✓D. Both A and BExplanation: NEC 210.12(A) allows multiple methods, including a Combination-Type AFCI breaker (A) or an Outlet Branch-Circuit AFCI receptacle (B) if the home run is protected (e.g., metal raceway or concrete encasement).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q20.High-pressure spray washing machines connected by cord and plug must have:
A.Factory installed GFCIB.A twist lock plugC.Double insulationD.An emergency switch✓A. Factory installed GFCIExplanation: NEC 422.49 requires high-pressure spray washers to have a factory-installed GFCI (integral to the plug or cord).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q21.GFCI protection shall be provided for lighting outlets in crawl spaces.
A.TrueB.FalseC.Only if LEDD.Only if switched✓A. TrueExplanation: NEC 210.8(C) requires GFCI protection for lighting outlets in crawl spaces (dwelling and non-dwelling).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q22.A receptacle for a gas range in a dwelling unit kitchen requires GFCI protection.
A.TrueB.False✓A. TrueExplanation: NEC 210.8(A)(6) requires GFCI protection for receptacles in kitchens. No exception exists for the range receptacle (gas ignition/clock). (Older codes limited it to countertops, current code is ALL kitchen receptacles).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q23.Tire inflation machines (automotive vacuum machines) provided for public use must be GFCI protected.
A.TrueB.False✓A. TrueExplanation: NEC 422.51 (and similar 422 sections) requires GFCI for tire inflation/vacuum machines for public use.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q24.Wall-mounted control units for in-floor radiant heating in bathrooms must be GFCI protected.
A.TrueB.False✓B. FalseExplanation: NEC 424.44(E) requires GFCI protection for the heating cables in floor heating systems installed in bathrooms, but this requirement applies to the heating element circuit, not to the wall-mounted control unit or thermostat itself. Unless the control unit incorporates a receptacle outlet or is otherwise covered by a separate GFCI requirement, the wall-mounted thermostat is not independently required to have GFCI protection.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q25.Sump pumps installed in dwelling unit basements require GFCI protection.
A.True, alwaysB.False, neverC.Only if cord and plug connectedD.Only if in a finished basement✓A. True, alwaysExplanation: NEC 210.8(A)(5) requires GFCI protection for receptacles in basements. There is NO exception for sump pumps (single outlet exception was removed years ago).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q26.Three-phase receptacles (up to 250V) in commercial kitchens require GFCI protection.
A.TrueB.False✓A. TrueExplanation: NEC 210.8(B) requires GFCI for single-phase receptacles (50A or less) AND three-phase receptacles (100A or less) in locations like kitchens.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q27.A Class A ground-fault circuit interrupter (GFCI) is designed to trip when the ground-fault current reaches what range?
A.2–3 mAB.4–6 mAC.15–20 mAD.30–50 mA✓B. 4–6 mAExplanation: A Class A GFCI is designed to trip when the ground-fault current is 4 to 6 mA (nominally 5 mA). This threshold is set to protect people from electric shock and is the device referenced throughout NEC 210.8.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q28.Per NEC 210.8, 125-volt, 15- and 20-ampere receptacles installed in a dwelling-unit bathroom must have what protection?
A.AFCI onlyB.GFCIC.Surge protection onlyD.No special protection✓B. GFCIExplanation: NEC 210.8(A) requires GFCI protection for 125-volt, 15- and 20-ampere receptacles in dwelling bathrooms because of their proximity to water.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q29.NEC 210.8 requires GFCI protection for receptacles located within how many feet of the outside edge of a sink?
A.3 feetB.6 feetC.10 feetD.Distance is not a factor✓B. 6 feetExplanation: NEC 210.8 requires GFCI protection for 125-volt receptacles located within 6 feet of the outside edge of a sink, in addition to the specific room-based requirements.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q30.Which dwelling location requires GFCI protection for 125-volt, 15- and 20-ampere receptacles under NEC 210.8(A)?
A.A finished living-room wallB.An unfinished basementC.A second-floor hallwayD.Inside a bedroom closet✓B. An unfinished basementExplanation: NEC 210.8(A) lists unfinished basements among the dwelling areas requiring GFCI protection for 125-volt, 15- and 20-ampere receptacles.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q31.What type of fault is an arc-fault circuit interrupter (AFCI) designed to detect?
A.Ground faults that shock peopleB.Arcing faults that can start firesC.Overloads from too many appliancesD.Voltage drop on long conductor runs✓B. Arcing faults that can start firesExplanation: An AFCI detects dangerous arcing faults from damaged or loose wiring that can ignite fires. This differs from a GFCI, which detects ground-fault current to protect people from shock. AFCI requirements are found in NEC 210.12.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q32.NEC 210.12 requires AFCI protection for 120-volt branch circuits supplying outlets in which dwelling-unit areas?
A.Only outdoor receptaclesB.Bedrooms and most habitable roomsC.Only the kitchenD.Only bathrooms✓B. Bedrooms and most habitable roomsExplanation: NEC 210.12 requires AFCI protection for 120-volt, 15- and 20-ampere branch circuits supplying outlets and devices in dwelling-unit kitchens, bedrooms, living rooms, and most other habitable rooms.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q33.Receptacles serving dwelling kitchen countertop surfaces are required to have what protection?
A.AFCI onlyB.GFCIC.Neither GFCI nor AFCID.Isolated-ground only✓B. GFCIExplanation: NEC 210.8(A) requires GFCI protection for receptacles serving kitchen countertop surfaces in a dwelling because of their proximity to the sink and water.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q34.Which statement best describes the difference between GFCI and AFCI protection?
A.They are the same device with two namesB.GFCI protects against shock; AFCI protects against arcing firesC.GFCI protects against fire; AFCI protects against shockD.Both protect only equipment, not people✓B. GFCI protects against shock; AFCI protects against arcing firesExplanation: A GFCI protects people from shock by tripping on small ground-fault currents (4–6 mA). An AFCI protects against fire by detecting dangerous arcing in wiring. A dual-function breaker combines both.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q35.Per NEC 210.8(A), 125-volt, 15- and 20-ampere receptacles in a dwelling-unit garage require:
A.AFCI onlyB.GFCIC.No protection if used for a freezerD.Only a weather-resistant cover✓B. GFCIExplanation: NEC 210.8(A) requires GFCI protection for 125-volt, 15- and 20-ampere receptacles in dwelling garages and accessory buildings. Older exceptions for dedicated appliance receptacles have largely been removed in recent code cycles.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q36.Under NEC 210.8(A), outdoor 125-volt, 15- and 20-ampere receptacles at a dwelling require what protection?
A.No special protectionB.GFCIC.AFCI onlyD.Protection only above 250 volts✓B. GFCIExplanation: NEC 210.8(A) requires GFCI protection for outdoor 125-volt, 15- and 20-ampere receptacles at dwellings, since outdoor locations are exposed to moisture.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
More Journeyman Electrician Exam Topics
Studying for the Journeyman Electrician exam? Read more about Electrician Prep →