20 practice questions with detailed explanations — aligned to the Journeyman Electrician Exam.

  1. Q1.A location where flammable gases or vapors are present in the air in quantities sufficient to produce explosive or ignitible mixtures is classified as:

    A.Class I
    B.Class II
    C.Class III
    D.Unclassified
    AClass I

    Explanation: NEC 500.5(B) defines Class I locations as those where flammable gases, flammable liquid-produced vapors, or combustible liquid-produced vapors are present.

    Join 1,000+ users passing the Journeyman Electrician

  2. Q2.Which classification applies to areas where combustible dust is present?

    A.Class I
    B.Class II
    C.Class III
    D.Class IV
    BClass II

    Explanation: NEC 500.5(C) defines Class II locations as those hazardous due to the presence of combustible dust.

    Join 1,000+ users passing the Journeyman Electrician

  3. Q3.A conduit seal shall be installed within _____ of the enclosure for an explosionproof enclosure containing a switch.

    A.6 inches
    B.12 inches
    C.18 inches
    D.24 inches
    C18 inches

    Explanation: NEC 501.15(A)(1) requires a conduit seal within 18 inches of an enclosure containing apparatus that may produce arcs, sparks, or high temperatures (Class I, Div 1).

    Join 1,000+ users passing the Journeyman Electrician

  4. Q4.Threaded rigid metal conduit installed in a Class I, Division 1 location must be engaged with at least _____ full threads.

    A.3
    B.4
    C.5
    D.6
    C5

    Explanation: NEC 500.8(E) requires that threaded entries into explosionproof equipment be made up with at least 5 threads fully engaged.

    Join 1,000+ users passing the Journeyman Electrician

  5. Q5.In a Commercial Garage (repair shop), the area up to 18 inches above the floor is classified as:

    A.Class I, Division 1
    B.Class I, Division 2
    C.Class II, Division 1
    D.Unclassified
    BClass I, Division 2

    Explanation: NEC 511.3(C) classifies the floor area (up to 18 inches) in major repair garages as Class I, Division 2 (unless ventilation allows for unclassified, but the standard unventilated default is Class I Div 2).

    Join 1,000+ users passing the Journeyman Electrician

  6. Q6.Which wiring method is permitted in a Class I, Division 1 location?

    A.Electrical Metallic Tubing (EMT)
    B.Rigid Metal Conduit (RMC) with threaded fittings
    C.PVC Conduit (Schedule 80)
    D.Type NM Cable
    BRigid Metal Conduit (RMC) with threaded fittings

    Explanation: NEC 501.10(A) permits Threaded Rigid Metal Conduit (RMC) and Threaded Steel Intermediate Metal Conduit (IMC). EMT and PVC are generally not permitted in Div 1.

    Join 1,000+ users passing the Journeyman Electrician

  7. Q7.Intrinsically safe systems are permitted in:

    A.Class I locations only
    B.Class II locations only
    C.Class III locations only
    D.All Hazardous (Classified) Locations
    DAll Hazardous (Classified) Locations

    Explanation: NEC 504.10 permits Intrinsically Safe systems in any hazardous (classified) location for which they are approved.

    Join 1,000+ users passing the Journeyman Electrician

  8. Q8.In an aircraft hangar, the pit in the floor is classified as:

    A.Class I, Division 1
    B.Class I, Division 2
    C.Class II, Division 1
    D.Unclassified
    AClass I, Division 1

    Explanation: NEC 513.3(A) classifies any pit or depression below the level of the hangar floor as Class I, Division 1.

    Join 1,000+ users passing the Journeyman Electrician

  9. Q9.The sealing compound in a conduit seal must be at least _____ thick.

    A.3/8 inch
    B.1/2 inch
    C.5/8 inch
    D.The trade size of the conduit, but not less than 5/8 inch
    DThe trade size of the conduit, but not less than 5/8 inch

    Explanation: NEC 501.15(C)(3) requires the thickness of the sealing compound to be not less than the trade size of the conduit and in no case less than 5/8 inch.

    Join 1,000+ users passing the Journeyman Electrician

  10. Q10.Equipment installed in a Class III location (Ignitible Fibers/Flyings) must be designed to:

    A.Withstand an internal explosion
    B.Prevent the entry of fibers and flyings
    C.Be submerged in oil
    D.Vent gases to the outside
    BPrevent the entry of fibers and flyings

    Explanation: NEC 500.5(D) / 503. Equipment in Class III locations must be dusttight to prevent the entry of ignitible fibers/flyings.

    Join 1,000+ users passing the Journeyman Electrician

  11. Q11.For a gasoline dispensing station, the area within 18 inches horizontally of the dispenser enclosure and extending to 4 feet vertically is:

    A.Class I, Division 1
    B.Class I, Division 2
    C.Unclassified
    D.Class II, Division 1
    BClass I, Division 2

    Explanation: Table 514.3(B)(1): The area 18 inches horizontally from the dispenser enclosure extending 4 feet up is Class I, Division 2. (Inside the enclosure up to 4 ft is Div 1).

    Join 1,000+ users passing the Journeyman Electrician

  12. Q12.A 'Zone 0' classification is most similar to:

    A.Class I, Division 1 (Continuous hazard)
    B.Class I, Division 2
    C.Class II, Division 1
    D.Unclassified
    AClass I, Division 1 (Continuous hazard)

    Explanation: NEC 505.5(B)(1): Zone 0 is an area where ignitible concentrations of flammable gases are present continuously or for long periods (similar to the most severe part of Div 1).

    Join 1,000+ users passing the Journeyman Electrician

  13. Q13.In a Spray Application Area (Spray Booth), motors located in the spray area must be:

    A.Totally Enclosed Fan Cooled (TEFC)
    B.Explosionproof and listed for the location
    C.Standard open drip-proof
    D.Located outside the booth only
    BExplosionproof and listed for the location

    Explanation: NEC 516.3 / 501. Motors in the Class I Div 1 spray area must be specifically listed for the location (Explosionproof).

    Join 1,000+ users passing the Journeyman Electrician

  14. Q14.Type MI (Mineral Insulated) cable is permitted in Class I, Division 1 locations.

    A.True
    B.False
    ATrue

    Explanation: NEC 501.10(A)(1) permits Type MI cable with termination fittings listed for the location in Class I, Div 1.

    Join 1,000+ users passing the Journeyman Electrician

  15. Q15.Seals are required in Class I, Division 1 locations where the conduit leaves the Division 1 area and enters a:

    A.Non-hazardous area
    B.Division 2 area
    C.Both A and B
    D.None of the above
    CBoth A and B

    Explanation: NEC 501.15(A)(4) requires a boundary seal where the conduit leaves the Div 1 area and enters a Div 2 or unclassified area.

    Join 1,000+ users passing the Journeyman Electrician

  16. Q16.Which part of a Health Care Facility is considered a hazardous location involving flammable anesthetics?

    A.Patient Rooms
    B.Operating Rooms (if flammable anesthetics are used)
    C.Corridors
    D.Waiting Areas
    BOperating Rooms (if flammable anesthetics are used)

    Explanation: NEC 517.60. While flammable anesthetics are rare today, the code classifies areas where they are used as hazardous. (Most modern ORs are unclassified because non-flammable agents are used, but the definition remains).

    Join 1,000+ users passing the Journeyman Electrician

  17. Q17.In a Class II location, dust-ignitionproof enclosures are required for:

    A.Switches
    B.Circuit Breakers
    C.Motor Controllers
    D.All of the above
    DAll of the above

    Explanation: NEC 502.115 requires switches, circuit breakers, and controllers in Class II locations to be in dust-ignitionproof enclosures.

    Join 1,000+ users passing the Journeyman Electrician

  18. Q18.Conduit unions used in Class I locations must be:

    A.Standard malleable iron
    B.Explosionproof / Listed for the location
    C.Die-cast zinc
    D.PVC
    BExplosionproof / Listed for the location

    Explanation: Fittings and unions in Class I locations must be listed for the location (Explosionproof).

    Join 1,000+ users passing the Journeyman Electrician

  19. Q19.For a Bulk Storage Plant (Fuel), the area 5 feet around a vent pipe opening is:

    A.Class I, Division 1
    B.Class I, Division 2
    C.Unclassified
    D.Class II, Division 1
    AClass I, Division 1

    Explanation: Table 515.3: The area within 5 feet of a vent opening is Class I, Division 1.

    Join 1,000+ users passing the Journeyman Electrician

  20. Q20.Which of the following wiring methods is NOT permitted in Class II, Division 1?

    A.Threaded RMC
    B.Type MI Cable
    C.Electrical Metallic Tubing (EMT)
    D.Type MC Cable (listed for location)
    CElectrical Metallic Tubing (EMT)

    Explanation: NEC 502.10(A). EMT is not permitted in Class II, Division 1 (Dust). It is permitted in Div 2.

    Join 1,000+ users passing the Journeyman Electrician

Want all 585 questions?

Download VoltExam — $17.99 Lifetime

Offline access, 585+ questions, built-in calculators. One-time unlock, no subscription.