Journeyman Electrician Exam
Overcurrent Protection Practice Questions
47 practice questions with detailed explanations — aligned to the Journeyman Electrician Exam.
Master Overcurrent Protection to boost your score on the Journeyman Electrician Exam. Each question below mirrors the style and difficulty of real exam questions, complete with detailed explanations so you understand the why behind every answer. Work through all 47 questions, review any that trip you up, and use the related topics below to round out your preparation.
Q1.Which of the following is a standard rating for a fuse or inverse time circuit breaker?
A.55 AmpsB.65 AmpsC.75 AmpsD.85 Amps✓D. 85 AmpsExplanation: NEC 240.6(A) lists the standard ampere ratings for fuses and inverse time circuit breakers: 15, 20, 25, 30, 35, 40, 45, 50, 60, 70, 80, 90, 100, 110, 125, 150, 175, 200, 225, 250, 300, 350, 400, 450, 500, 600, 700, 800, 1000, 1200, 1600, 2000, 2500, 3000, 4000, 5000, and 6000 amperes. Of the options given, 85 Amps is not a standard rating listed in NEC 240.6(A).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q2.Which of the following is a standard ampere rating for a circuit breaker per NEC 240.6(A)?
A.65 AmpsB.75 AmpsC.110 AmpsD.115 Amps✓C. 110 AmpsExplanation: NEC 240.6(A) lists 110 Amps as a standard rating. (65, 75, and 115 are not standard ratings).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q3.Conductors must generally be protected against overcurrent at the point where:
A.They terminateB.They receive their supplyC.The voltage drop exceeds 3%D.They enter a building✓B. They receive their supplyExplanation: NEC 240.21 requires overcurrent protection to be provided in each ungrounded circuit conductor at the point where the conductors receive their supply.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q4.The 'Next Size Up' rule (240.4(B)) permits using a higher rated overcurrent device if the conductor ampacity does not match a standard rating, provided the rating does not exceed:
A.600 AmpsB.800 AmpsC.1000 AmpsD.1200 Amps✓B. 800 AmpsExplanation: NEC 240.4(B) applies only to overcurrent devices rated 800 amperes or less.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q5.Under the '10-foot Tap Rule' (240.21(B)(1)), tap conductors are permitted without overcurrent protection at the tap point if their ampacity is at least:
A.The rating of the feeder deviceB.1/10 the rating of the feeder deviceC.1/3 the rating of the feeder deviceD.125% of the load✓B. 1/10 the rating of the feeder deviceExplanation: NEC 240.21(B)(1) requires tap conductors not over 10 feet long to have an ampacity not less than the combined calculated load AND not less than 1/10 the rating of the overcurrent device protecting the feeder.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q6.Supplementary overcurrent protection (like a fuse in a light fixture) is:
A.A substitute for branch-circuit protectionB.Required to be readily accessibleC.Not required to be readily accessibleD.Required to be rated at 125% of load✓C. Not required to be readily accessibleExplanation: NEC 240.10 specifies that supplementary overcurrent protection is not a substitute for branch-circuit protection. NEC 240.24(A) Exception 2 states that supplementary OCPDs are not required to be readily accessible.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q7.Circuit breakers used to switch 120V or 277V fluorescent lighting circuits on a daily basis must be marked:
A.SWD or HIDB.HACRC.D-CurveD.Rated for Duty✓A. SWD or HIDExplanation: NEC 240.83(D) requires breakers used as switches for 120V/277V fluorescent lighting to be marked SWD (Switching Duty) or HID (High Intensity Discharge).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q8.Overcurrent devices shall be readily accessible. Which of the following locations is permitted for installing an OCPD?
A.In a bathroom of a dwelling unitB.Over the steps of a stairwayC.In a clothes closet (unless combustible material)D.In a guest room of a hotel✓D. In a guest room of a hotelExplanation: NEC 240.24 prohibits OCPDs in dwelling bathrooms (E), over steps of a stairway (F), and near easily ignitable material (clothes closets) (D). Guest rooms are permitted (provided they are accessible to the occupant, though management often holds keys to service areas, guest access limits apply. However, dwelling bathrooms and stairways are explicit NOs. Guest rooms are generally allowed if not in prohibited spots).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q9.Where a circuit breaker is rated 1200A or higher, what special method must be provided to reduce clearing time?
A.Ground Fault Protection of Equipment (GFPE)B.Arc Energy ReductionC.Current Limiting FusesD.Zone Selective Interlocking only✓B. Arc Energy ReductionExplanation: NEC 240.87 requires an Arc Energy Reduction method (such as zone-selective interlocking, differential relaying, or maintenance switch) for breakers rated (or adjustable to) 1200A or higher.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q10.Plug fuses of the Edison-base type shall be used only:
A.For new installationsB.As a replacement in existing installationsC.For circuits over 120VD.For motor circuits✓B. As a replacement in existing installationsExplanation: NEC 240.51(B) states that Edison-base plug fuses shall be used only as replacements in existing installations where there is no evidence of overfusing or tampering.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q11.For a circuit supplied by a transformer arc welder, the overcurrent protection is permitted to be rated at not more than ____ of the primary current.
A.125%B.200%C.250%D.300%✓B. 200%Explanation: NEC 630.12(A) allows the overcurrent protection for an arc welder to be rated or set at not more than 200% of the rated primary current.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q12.Circuit breakers used in 3-phase, 4-wire, delta-connected systems where the voltage to ground exceeds 120V (e.g., High-Leg Delta) must be rated:
A.120/240VB.240VC.480Y/277VD.Straight 240V or slash rated if neutral is present✓B. 240VExplanation: NEC 240.85 states that a circuit breaker with a slash rating (e.g., 120/240V) shall be permitted only in a grounded circuit where the nominal voltage of any conductor to ground does not exceed the lower of the two values. In a High-Leg Delta (208V to ground on the high leg), a 120/240V breaker is NOT permitted on the high leg because 208V > 120V. A straight rated 240V breaker is required.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q13.A fuse is stamped with 'Class RK1'. This indicates the fuse is:
A.RenewableB.Current-LimitingC.Non-Time Delay onlyD.Rated for DC only✓B. Current-LimitingExplanation: Class R (RK1 and RK5) fuses are Current-Limiting fuses designed to reject non-current limiting fuses in the same holder (rejection clips).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q14.Standard fuse holders for cartridge fuses shall be so designed that it is difficult to put a fuse of any given class into a fuse holder that is designed for a ____ lower or higher ampere rating.
A.CurrentB.VoltageC.ClassD.Interrupting capacity✓A. CurrentExplanation: NEC 240.60(B) requires that cartridge fuse holders be designed so that it is difficult to insert a fuse of a given current rating into a holder designed for a different current range. This non-interchangeability requirement is based on current range classifications (0–30A, 31–60A, 61–100A, etc.), preventing installation of an incorrectly rated fuse that could allow dangerous overcurrents.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q15.What is the maximum overcurrent protection allowed for a 20A branch circuit supplying a single non-motor appliance?
A.15 AmpsB.20 AmpsC.25 AmpsD.30 Amps✓B. 20 AmpsExplanation: NEC 210.20(B) states that the rating of the overcurrent device shall not exceed the rating of the branch circuit (20A). For a single appliance, 422.11(E) says it shall not exceed 20A if the appliance is rated 13.3A or less (standard 20A limit applies).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q16.Ground-fault protection of equipment (GFPE) shall be provided for solidly grounded wye electric services of more than 150 volts to ground but not exceeding 600 volts phase-to-phase for each service disconnect rated _____ or more.
A.800 AmpsB.1000 AmpsC.1200 AmpsD.2000 Amps✓B. 1000 AmpsExplanation: NEC 230.95 requires GFPE for solidly grounded wye services (like 480Y/277V) rated 1000 amperes or more.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q17.The maximum setting for Ground-Fault Protection of Equipment (GFPE) shall be _____ and the time delay shall not exceed 1 second for ground faults of 3000 amperes or more.
A.1000 AmpsB.1200 AmpsC.3000 AmpsD.600 Amps✓B. 1200 AmpsExplanation: NEC 230.95(A) sets the maximum setting for GFPE at 1200 Amperes.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q18.Fuses and circuit breakers must be marked with their ampere rating. For hex-shaped fuses or fuses with a hex-shaped opening in the cap, the rating is:
A.15 Amps or lessB.Between 15 and 30 AmpsC.Between 30 and 60 AmpsD.Over 60 Amps✓A. 15 Amps or lessExplanation: NEC 240.50(C) requires plug fuses of 15 amperes and lower to be identified by a hexagonal configuration.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q19.Overcurrent devices for panelboards supplied by a transformer (secondary side) must be located:
A.On the primary side onlyB.Within 10 feet of the transformerC.In the panelboard or on the line side of the panelboardD.Anywhere in the building✓C. In the panelboard or on the line side of the panelboardExplanation: NEC 408.36 requires that panelboards be protected by an overcurrent device having a rating not greater than that of the panelboard, located within or at any point on the supply side of the panelboard.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q20.A tap conductor is 20 feet long. To comply with the '25-foot Tap Rule' (240.21(B)(2)), the tap conductor ampacity must be at least ____ of the rating of the overcurrent device protecting the feeder.
A.1/10B.1/3C.1/5D.1/2✓B. 1/3Explanation: NEC 240.21(B)(2) states that for taps not over 25 feet, the ampacity must be at least 1/3 of the rating of the feeder OCPD.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q21.Which Article provides the specific requirements for overcurrent protection of Air Conditioning and Refrigerating Equipment?
A.Article 240B.Article 430C.Article 440D.Article 450✓C. Article 440Explanation: Article 440 Parts III and VI cover the specific overcurrent protection rules for HVAC equipment (often allowing higher ratings than standard motors to accommodate hermetic compressors).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q22.If a circuit breaker has an adjustable trip setting, the 'rating' of the breaker is considered to be:
A.The lowest possible settingB.The setting at the time of inspectionC.The maximum possible settingD.The average of the range✓C. The maximum possible settingExplanation: NEC 240.6(B) states that the rating of an adjustable trip circuit breaker is the maximum setting possible, unless access is restricted (sealed cover, locked door, password protected).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q23.Overcurrent devices shall not be located in the vicinity of easily ignitable material, such as in:
A.GaragesB.Clothes closetsC.AtticsD.Kitchens✓B. Clothes closetsExplanation: NEC 240.24(D) explicitly prohibits installing overcurrent devices in clothes closets.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q24.A 'Series Rated' system allows a downstream circuit breaker to have an interrupting rating lower than the available fault current if:
A.The upstream breaker is rated for the full fault current and the combination is tested/listed.B.The downstream breaker is a fuse.C.The voltage is less than 120V.D.A professional engineer calculates the impedance.✓A. The upstream breaker is rated for the full fault current and the combination is tested/listed.Explanation: NEC 240.86(B) permits series ratings where the combination of the line-side (protecting) device and load-side device is tested and listed for the available fault current.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q25.The handle position of a circuit breaker must indicate:
A.The voltage ratingB.Whether it is Open (Off) or Closed (On)C.The trip curveD.The manufacturer date✓B. Whether it is Open (Off) or Closed (On)Explanation: NEC 240.81 requires that circuit breakers clearly indicate whether they are in the open (off) or closed (on) position. If vertically mounted, 'up' must be 'on'.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q26.NEC 2026 240.24(G) adds a new prohibition for locating overcurrent devices in:
A.Commercial KitchensB.Battery RoomsC.Enclosures for Limited Energy Systems unless listedD.Spaces dedicated to egress (emergency exits)✓D. Spaces dedicated to egress (emergency exits)Explanation: Safety updates in 2026 focus on keeping OCPDs out of critical egress paths to prevent obstruction during emergencies.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q27.Under NEC 2026, reconditioned circuit breakers must be listed as 'reconditioned' and the original listing mark must be:
A.RemovedB.ObscuredC.Retained (not removed)D.Replaced with a generic label✓A. RemovedExplanation: Under NEC 2026 rules for reconditioned circuit breakers (referencing NEC 240.88 and 110.21), the original listing mark must be removed from the device after reconditioning. The reconditioner takes responsibility for the equipment and applies a new listing mark identifying it as reconditioned. Removing the original mark prevents confusion about the equipment's current certification status.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q28.What is the maximum overcurrent protection for an 18 AWG fixture wire used in a 120V circuit?
A.7 AmpsB.10 AmpsC.15 AmpsD.20 Amps✓A. 7 AmpsExplanation: NEC 240.5(B)(2) or 240.4(D)(1) limits 18 AWG copper protection to 7 Amperes.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q29.A 200A fuse is installed in a circuit with a fault current of 50,000A. The fuse must have an Interrupting Rating (AIC) of at least:
A.10,000 AmpsB.22,000 AmpsC.42,000 AmpsD.50,000 Amps✓D. 50,000 AmpsExplanation: NEC 110.9 requires that equipment intended to interrupt current at fault levels shall have an interrupting rating sufficient for the nominal circuit voltage and the current that is available at the line terminals (must be >= Available Fault Current).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q30.The '25-foot Tap Rule' applies to taps supplying:
A.A panelboard or switchboard onlyB.A transformerC.A motor control centerD.Any load provided the ampacity is 1/3 feeder rating✓D. Any load provided the ampacity is 1/3 feeder ratingExplanation: The 25-foot tap rule under NEC 240.21(B)(2) permits a tap conductor to extend up to 25 feet from the point of the larger feeder conductor, provided the tap conductor terminates in a single circuit breaker or set of fuses rated at the tap conductor ampacity. This single protective device may then supply a panelboard, switchboard, or any other load. The key requirement is that the tap terminates in a single overcurrent device.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q31.Arc-Fault Circuit Interrupter (AFCI) protection is required for 120V, single-phase, 15A and 20A branch circuits in which dwelling unit areas?
A.Bedrooms onlyB.Kitchens and Laundry areas onlyC.Kitchens, Family Rooms, Dining Rooms, Living Rooms, Bedrooms, and similar areasD.Bathrooms and Garages✓C. Kitchens, Family Rooms, Dining Rooms, Living Rooms, Bedrooms, and similar areasExplanation: NEC 210.12(A) requires AFCI protection for almost all dwelling unit living areas: Kitchens, family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, laundry areas.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q32.For a transformer with a primary current of less than 2 Amps, the primary overcurrent protection is permitted to be set at not more than:
A.125%B.167%C.250%D.300%✓D. 300%Explanation: NEC Table 450.3(B) allows primary overcurrent protection for transformers with primary current less than 2A to be set at a maximum of 300%.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q33.When locating overcurrent devices for a feeder supplying a mobile home, the disconnect must be located within _____ of the mobile home.
A.15 feetB.20 feetC.30 feetD.50 feet✓C. 30 feetExplanation: NEC 550.32(A) requires the mobile home service equipment (disconnect/OCP) to be located in sight from and not more than 30 feet from the exterior wall of the mobile home.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q34.A circuit breaker with a slash rating of 120/240V is installed in a panelboard. This breaker is permitted to be used on:
A.A solidly grounded 120/240V single-phase systemB.A 277/480V systemC.A 480V delta systemD.An ungrounded 240V delta system✓A. A solidly grounded 120/240V single-phase systemExplanation: Slash-rated breakers (120/240V) can only be used where the voltage to ground does not exceed the lower value (120V). A 120/240V single-phase system has 120V to ground.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q35.Where a feeder taps into a busway, the overcurrent device is not required at the tap if the tap length does not exceed:
A.10 feetB.25 feetC.50 feetD.100 feet✓B. 25 feetExplanation: Busway taps invoke the 25-foot tap rule (240.21(B)(2)) or specific busway rules in 368.17(C) which allow 50 feet for industrial, but generally 25 feet applies for standard feeder taps.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q36.Supplementary overcurrent protective devices must have an interrupting rating:
A.Equal to the branch circuit ratingB.At least equal to the available fault current at the device terminalsC.Of 10,000 Amps minimumD.Of 5,000 Amps maximum✓B. At least equal to the available fault current at the device terminalsExplanation: NEC 240.101(B) requires supplementary OCPDs to have an interrupting rating at least equal to the available fault current at the line terminals of the device.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q37.According to 240.4(C), for overcurrent devices rated over 800 Amperes, the conductor ampacity must be:
A.Equal to or greater than the rating of the deviceB.At least 83% of the device ratingC.Allowed to be less than the device rating (next size up)D.Determined by the 60°C column✓A. Equal to or greater than the rating of the deviceExplanation: The 'Next Size Up' rule does NOT apply to devices over 800A. The conductor ampacity must be equal to or greater than the OCPD rating.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q38.In a supervised industrial installation, tap conductors up to 100 feet long are permitted if the ampacity is not less than _____ of the feeder rating.
A.1/10B.1/3C.1/2D.1/4✓B. 1/3Explanation: NEC 240.21(B)(5) allows 100-foot taps in supervised industrial installations if the ampacity is at least 1/3 of the rating of the overcurrent device protecting the feeder.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q39.What is the maximum standard rating for a fuse?
A.5000 AmpsB.6000 AmpsC.8000 AmpsD.10000 Amps✓B. 6000 AmpsExplanation: NEC 240.6(A) lists the standard ampere ratings. The list goes up to 6000 Amperes.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q40.Overcurrent protection for an electric boiler (heating load) using resistance elements shall be sized at:
A.100% of the loadB.125% of the loadC.150% of the loadD.250% of the load✓B. 125% of the loadExplanation: NEC 424.3(B) generally considers fixed electric space heating equipment a continuous load, requiring OCPDs and conductors to be sized at 125% of the total load.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q41.Which fuse class is not permitted to be used in new installations of 250V switches?
A.Class HB.Class RC.Class JD.Class T✓A. Class HExplanation: NEC 240.60(D) restricts renewable fuses (Class H renewable cartridge fuses) to replacement use only in existing installations. Class H fuses are not permitted in new installations because they lack the current-limiting capability and rejection features required for modern electrical systems. Class R, Class J, and Class T fuses are acceptable for new work.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q42.Renewable link cartridge fuses (Class H) shall be permitted to be used only:
A.In industrial establishmentsB.Where voltage is less than 120VC.For replacement in existing installations where no evidence of overfusing existsD.In motor control centers✓C. For replacement in existing installations where no evidence of overfusing existsExplanation: NEC 240.60(D) states that Class H renewable fuses shall be used only for replacement in existing installations where there is no evidence of overfusing or tampering.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q43.If a multiwire branch circuit supplies line-to-line loads, the overcurrent device must:
A.Be rated 150% of the loadB.Open all ungrounded conductors of the circuit simultaneouslyC.Be located in a separate enclosureD.Be a single-pole breaker for each phase✓B. Open all ungrounded conductors of the circuit simultaneouslyExplanation: NEC 240.15(B)(1) requires that for multiwire branch circuits supplying line-to-line loads, the OCPD must disconnect all ungrounded conductors simultaneously (multipole breaker or handle tie).
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q44.When protection is required for a transformer secondary (600V or less), and the secondary current is 100A, the maximum breaker rating is:
A.100 AmpsB.110 AmpsC.125 AmpsD.250 Amps✓C. 125 AmpsExplanation: Table 450.3(B) allows secondary protection at 125% of the rated secondary current. 100A * 1.25 = 125A.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q45.Arc-Fault Circuit Interrupters (AFCIs) function by detecting:
A.A current imbalance of 5mAB.Heat build-up in the wireC.Characteristic current signatures of arcing faultsD.Voltage spikes over 600V✓C. Characteristic current signatures of arcing faultsExplanation: AFCIs use electronic logic to recognize the specific waveform characteristics (signatures) of hazardous arcing faults.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q46.A breaker protecting a fire pump circuit must be set to:
A.Trip at 125% of FLCB.Trip at 300% of FLCC.Hold the locked-rotor current indefinitelyD.Trip instantaneously at 200%✓C. Hold the locked-rotor current indefinitelyExplanation: NEC 695.4(B)(2) requires the fire pump OCPD to hold locked-rotor current indefinitely to ensure the pump runs until destruction if necessary during a fire.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime
Q47.The maximum rating of a time-delay fuse for a motor branch circuit (3-phase) is:
A.150%B.175%C.225%D.300%✓B. 175%Explanation: Table 430.52 sets the max rating for Dual Element (Time-Delay) fuses at 175% of Full Load Current.
See answer — start free trial3-day free trial · $9.99/mo after · cancel anytime