  1. Q1.Transformers rated over 112.5 kVA installed indoors shall be installed in a fire-resistant vault unless they are:

    A.Dry-type with Class 155 insulation
    B.Dry-type with Class 155 or higher insulation and separated from combustible material
    C.Oil-filled
    D.Located in a basement
    BDry-type with Class 155 or higher insulation and separated from combustible material

    Explanation: NEC 450.21(B) Exception allows dry-type transformers >112.5 kVA to be installed without a vault if they have Class 155 or higher insulation and are separated from combustible material by a fire-resistant heat-insulating barrier or 6 ft horizontal/12 ft vertical distance.

    Join 1,000+ users passing the Journeyman Electrician

  2. Q2.Calculate the maximum primary overcurrent protection rating for a 480V/120V, 50 kVA transformer (Primary Current = 60A) using the 'Primary Only' protection method.

    A.60 Amps
    B.75 Amps
    C.80 Amps
    D.100 Amps
    B75 Amps

    Explanation: Per Table 450.3(B), Primary Only protection for transformers 9A or more is 125%. 60A x 1.25 = 75A. Since 75A is a standard overcurrent device size, the maximum rating is 75A.

    Join 1,000+ users passing the Journeyman Electrician

  3. Q3.What is the maximum rating for the secondary overcurrent device of a transformer (600V or less) when using 'Primary and Secondary' protection, if the secondary current is 100A?

    A.100 Amps
    B.110 Amps
    C.125 Amps
    D.150 Amps
    C125 Amps

    Explanation: Table 450.3(B) Secondary Protection column (when Primary is up to 250%): Secondary max is 125% (Note 1 allows next size up). 100 * 1.25 = 125A. Since 125A is standard, it is the max (next size up only applies if non-standard, but since 125 is standard, it stops there).

    Join 1,000+ users passing the Journeyman Electrician

  4. Q4.Dry-type transformers installed indoors and rated 112.5 kVA or less must be separated from combustible material by at least:

    A.6 inches
    B.12 inches
    C.24 inches
    D.3 feet
    B12 inches

    Explanation: NEC 450.21(A) requires dry-type transformers 112.5 kVA or less to be separated from combustible material by 12 inches (unless separated by a fire-resistant heat-insulating barrier).

    Join 1,000+ users passing the Journeyman Electrician

  5. Q5.Transformer vaults shall have a fire resistance rating of not less than:

    A.1 hour
    B.2 hours
    C.3 hours
    D.4 hours
    C3 hours

    Explanation: NEC 450.42 requires the walls and roof of a transformer vault to have a fire resistance of 3 hours (unless protected by automatic sprinkler, then 1 hour is permitted). The standard rule is 3 hours.

    Join 1,000+ users passing the Journeyman Electrician

  6. Q6.A door sill or curb is required for a transformer vault. The minimum height is:

    A.2 inches
    B.4 inches
    C.6 inches
    D.8 inches
    B4 inches

    Explanation: NEC 450.43(B) requires a door sill or curb of sufficient height to confine the oil from the largest transformer, but in no case less than 4 inches.

    Join 1,000+ users passing the Journeyman Electrician

  7. Q7.Ventilation openings for transformer vaults shall have a net area of not less than _____ square inches per kVA of transformer capacity.

    A.1 sq in
    B.2 sq in
    C.3 sq in
    D.5 sq in
    C3 sq in

    Explanation: NEC 450.45(C) requires 3 square inches per kVA of transformer capacity, but never less than 1 sq ft total.

    Join 1,000+ users passing the Journeyman Electrician

  8. Q8.Askarel-insulated transformers installed indoors:

    A.Are prohibited
    B.Must be in a vault
    C.Must be provided with a pressure-relief vent vented to the outdoors
    D.Require 6 hours fire rating
    CMust be provided with a pressure-relief vent vented to the outdoors

    Explanation: NEC 450.25 requires Askarel-insulated transformers installed indoors to be rated for such use and provided with a pressure-relief vent vented to the outside (gas is toxic).

    Join 1,000+ users passing the Journeyman Electrician

  9. Q9.When a transformer supplies a 120/240V single-phase panelboard, the grounded conductor (neutral) must be bonded to:

    A.The transformer case
    B.The building steel
    C.The grounding electrode system
    D.All of the above
    DAll of the above

    Explanation: For a separately derived system, the system bonding jumper connects the neutral to the equipment grounding conductor (case) and the grounding electrode conductor (building steel/electrode).

    Join 1,000+ users passing the Journeyman Electrician

  10. Q10.Autotransformers are permitted to be used for:

    A.Branch circuits generally
    B.Only where the grounded conductor is common to both primary and secondary
    C.Patient care areas
    D.Swimming pool lighting
    BOnly where the grounded conductor is common to both primary and secondary

    Explanation: NEC 210.9 (and 450.4) permits autotransformers only if the system supplied has a grounded conductor that is electrically connected to the grounded conductor of the system supplying the autotransformer (common neutral).

    Join 1,000+ users passing the Journeyman Electrician

  11. Q11.A dry-type transformer is installed in a hollow space of a building (e.g., suspended ceiling). It must be rated not more than _____.

    A.15 kVA
    B.50 kVA
    C.112.5 kVA
    D.1000 kVA
    B50 kVA

    Explanation: NEC 450.13(B) allows dry-type transformers rated 50 kVA or less to be installed in hollow spaces of buildings not permanently closed in by the structure.

    Join 1,000+ users passing the Journeyman Electrician

  12. Q12.The disconnecting means for a transformer must be:

    A.Within 10 feet
    B.Within sight of the transformer
    C.Located in a separate room
    D.Lockable in the open position
    DLockable in the open position

    Explanation: NEC 450.14 requires a disconnecting means that is lockable in the open position (in accordance with 110.25) to be located in sight of the transformer, unless the location is remote and the disconnect is lockable/labeled.

    Join 1,000+ users passing the Journeyman Electrician

  13. Q13.Parallel operation of transformers is permitted only if:

    A.They are the same kVA rating
    B.They have the same impedance and voltage ratio
    C.They are from the same manufacturer
    D.They are oil-filled
    BThey have the same impedance and voltage ratio

    Explanation: NEC 450.7 states that transformers may be operated in parallel and switched as a unit provided they have the same transformation ratio, impedance, and other characteristics suitable for parallel operation.

    Join 1,000+ users passing the Journeyman Electrician

  14. Q14.Pipes or ducts foreign to the electrical installation shall not pass through a transformer vault unless:

    A.They are insulated
    B.They contain non-flammable material
    C.They are concrete encased
    D.They are prohibited entirely
    DThey are prohibited entirely

    Explanation: NEC 450.47 states that pipes or ducts foreign to the electrical installation shall not pass through the vault.

    Join 1,000+ users passing the Journeyman Electrician

  15. Q15.Calculate the primary OCPD rating for a 600V transformer (Primary Current 150A) where secondary protection is NOT provided.

    A.150 Amps
    B.175 Amps
    C.187.5 Amps
    D.200 Amps
    D200 Amps

    Explanation: Table 450.3(B) Primary Only protection: 125% of 150A = 187.5A. Note 1 allows the next higher standard rating. The next standard rating after 187.5A is 200A.

    Join 1,000+ users passing the Journeyman Electrician

  16. Q16.What is the minimum height of a curb required around an oil-filled transformer installed indoors?

    A.2 inches
    B.3 inches
    C.4 inches
    D.6 inches
    C4 inches

    Explanation: NEC 450.43(B) requires a sill or curb of at least 4 inches for transformer vaults to contain oil.

    Join 1,000+ users passing the Journeyman Electrician

  17. Q17.A zigzag (interconnected star) grounding autotransformer shall not be used on:

    A.A 3-phase, 3-wire system
    B.A 3-phase, 4-wire system
    C.A system where the neutral is not grounded
    D.Systems over 1000V
    BA 3-phase, 4-wire system

    Explanation: NEC 450.5 states that a zigzag grounding autotransformer shall not be installed on the load side of any system grounding connection, effectively prohibiting it on a 4-wire system that already has a neutral.

    Join 1,000+ users passing the Journeyman Electrician

  18. Q18.Transformer ventilating openings shall be covered with:

    A.Plywood
    B.Durable gratings, screens, or louvers
    C.Sheet metal
    D.Plastic mesh
    BDurable gratings, screens, or louvers

    Explanation: NEC 450.45(D) requires ventilation openings to be covered with durable gratings, screens, or louvers to prevent entry of animals/foreign objects.

    Join 1,000+ users passing the Journeyman Electrician

  19. Q19.When a secondary tie circuit connects two power sources, it must be protected by:

    A.A fuse at each end
    B.A limiter at each end
    C.An automatic transfer switch
    D.Ground fault protection
    BA limiter at each end

    Explanation: NEC 450.6(A)(3) requires a limiter (a special high-capacity fuse) at each end of the tie circuit for protection in network systems.

    Join 1,000+ users passing the Journeyman Electrician

  20. Q20.Transformers shall be marked with which of the following?

    A.Name of manufacturer
    B.Rated kVA
    C.Frequency and Voltage
    D.All of the above
    DAll of the above

    Explanation: NEC 450.11 requires transformers to be provided with a nameplate giving the name of the manufacturer, rated kVA, frequency, primary and secondary voltage, etc.

    Join 1,000+ users passing the Journeyman Electrician

  21. Q21.Less-flammable liquid-insulated transformers installed indoors without a vault must meet listing requirements and the liquid must have a fire point of not less than:

    A.200°C
    B.300°C
    C.400°C
    D.500°C
    B300°C

    Explanation: NEC 450.23(A) requires the liquid to have a fire point of not less than 300°C.

    Join 1,000+ users passing the Journeyman Electrician

  22. Q22.Are transformers permitted to be installed on the roof of a building?

    A.No, never.
    B.Yes, if the roof is structural concrete.
    C.Yes, if oil-filled and provided with a curb.
    D.Yes, dry-type or specific liquid-filled types are permitted.
    DYes, dry-type or specific liquid-filled types are permitted.

    Explanation: NEC 450.22 (Dry Type Outdoor) and 450.23-26 imply outdoor installation is permitted. There is no prohibition against roof installation provided structural support and clearances (450.27 for oil-insulated outdoor) are met. Oil-insulated on roofs must respect fire escape clearances.

    Join 1,000+ users passing the Journeyman Electrician

  23. Q23.Materials shall not be stored in transformer vaults.

    A.True
    B.False
    ATrue

    Explanation: NEC 450.48 explicitly states that materials shall not be stored in transformer vaults.

    Join 1,000+ users passing the Journeyman Electrician

  24. Q24.A step-down transformer has a primary voltage of 480V and a secondary voltage of 120V. If 10A flows in the primary, what is the secondary current (assuming 100% efficiency)?

    A.2.5 Amps
    B.10 Amps
    C.20 Amps
    D.40 Amps
    D40 Amps

    Explanation: Power In = Power Out. 480V * 10A = 4800VA. 4800VA / 120V = 40 Amps.

    Join 1,000+ users passing the Journeyman Electrician

  25. Q25.Terminal bars in transformers must be:

    A.Torqued to manufacturer specifications
    B.Painted red
    C.Made of aluminum only
    D.Accessible without removing covers
    ATorqued to manufacturer specifications

    Explanation: NEC 110.14(D) requires torque values to be achieved. NEC 450.12 requires the transformer (and terminals) to be accessible.

    Join 1,000+ users passing the Journeyman Electrician