Transformers Practice Questions
25 practice questions with detailed explanations — aligned to the Journeyman Electrician Exam.
Q1.Transformers rated over 112.5 kVA installed indoors shall be installed in a fire-resistant vault unless they are:
A.Dry-type with Class 155 insulationB.Dry-type with Class 155 or higher insulation and separated from combustible materialC.Oil-filledD.Located in a basementB. Dry-type with Class 155 or higher insulation and separated from combustible materialExplanation: NEC 450.21(B) Exception allows dry-type transformers >112.5 kVA to be installed without a vault if they have Class 155 or higher insulation and are separated from combustible material by a fire-resistant heat-insulating barrier or 6 ft horizontal/12 ft vertical distance.
Join 1,000+ users passing the Journeyman Electrician
Q2.Calculate the maximum primary overcurrent protection rating for a 480V/120V, 50 kVA transformer (Primary Current = 60A) using the 'Primary Only' protection method.
A.60 AmpsB.75 AmpsC.80 AmpsD.100 AmpsB. 75 AmpsExplanation: Per Table 450.3(B), Primary Only protection for transformers 9A or more is 125%. 60A x 1.25 = 75A. Since 75A is a standard overcurrent device size, the maximum rating is 75A.
Join 1,000+ users passing the Journeyman Electrician
Q3.What is the maximum rating for the secondary overcurrent device of a transformer (600V or less) when using 'Primary and Secondary' protection, if the secondary current is 100A?
A.100 AmpsB.110 AmpsC.125 AmpsD.150 AmpsC. 125 AmpsExplanation: Table 450.3(B) Secondary Protection column (when Primary is up to 250%): Secondary max is 125% (Note 1 allows next size up). 100 * 1.25 = 125A. Since 125A is standard, it is the max (next size up only applies if non-standard, but since 125 is standard, it stops there).
Join 1,000+ users passing the Journeyman Electrician
Q4.Dry-type transformers installed indoors and rated 112.5 kVA or less must be separated from combustible material by at least:
A.6 inchesB.12 inchesC.24 inchesD.3 feetB. 12 inchesExplanation: NEC 450.21(A) requires dry-type transformers 112.5 kVA or less to be separated from combustible material by 12 inches (unless separated by a fire-resistant heat-insulating barrier).
Join 1,000+ users passing the Journeyman Electrician
Q5.Transformer vaults shall have a fire resistance rating of not less than:
A.1 hourB.2 hoursC.3 hoursD.4 hoursC. 3 hoursExplanation: NEC 450.42 requires the walls and roof of a transformer vault to have a fire resistance of 3 hours (unless protected by automatic sprinkler, then 1 hour is permitted). The standard rule is 3 hours.
Join 1,000+ users passing the Journeyman Electrician
Q6.A door sill or curb is required for a transformer vault. The minimum height is:
A.2 inchesB.4 inchesC.6 inchesD.8 inchesB. 4 inchesExplanation: NEC 450.43(B) requires a door sill or curb of sufficient height to confine the oil from the largest transformer, but in no case less than 4 inches.
Join 1,000+ users passing the Journeyman Electrician
Q7.Ventilation openings for transformer vaults shall have a net area of not less than _____ square inches per kVA of transformer capacity.
A.1 sq inB.2 sq inC.3 sq inD.5 sq inC. 3 sq inExplanation: NEC 450.45(C) requires 3 square inches per kVA of transformer capacity, but never less than 1 sq ft total.
Join 1,000+ users passing the Journeyman Electrician
Q8.Askarel-insulated transformers installed indoors:
A.Are prohibitedB.Must be in a vaultC.Must be provided with a pressure-relief vent vented to the outdoorsD.Require 6 hours fire ratingC. Must be provided with a pressure-relief vent vented to the outdoorsExplanation: NEC 450.25 requires Askarel-insulated transformers installed indoors to be rated for such use and provided with a pressure-relief vent vented to the outside (gas is toxic).
Join 1,000+ users passing the Journeyman Electrician
Q9.When a transformer supplies a 120/240V single-phase panelboard, the grounded conductor (neutral) must be bonded to:
A.The transformer caseB.The building steelC.The grounding electrode systemD.All of the aboveD. All of the aboveExplanation: For a separately derived system, the system bonding jumper connects the neutral to the equipment grounding conductor (case) and the grounding electrode conductor (building steel/electrode).
Join 1,000+ users passing the Journeyman Electrician
Q10.Autotransformers are permitted to be used for:
A.Branch circuits generallyB.Only where the grounded conductor is common to both primary and secondaryC.Patient care areasD.Swimming pool lightingB. Only where the grounded conductor is common to both primary and secondaryExplanation: NEC 210.9 (and 450.4) permits autotransformers only if the system supplied has a grounded conductor that is electrically connected to the grounded conductor of the system supplying the autotransformer (common neutral).
Join 1,000+ users passing the Journeyman Electrician
Q11.A dry-type transformer is installed in a hollow space of a building (e.g., suspended ceiling). It must be rated not more than _____.
A.15 kVAB.50 kVAC.112.5 kVAD.1000 kVAB. 50 kVAExplanation: NEC 450.13(B) allows dry-type transformers rated 50 kVA or less to be installed in hollow spaces of buildings not permanently closed in by the structure.
Join 1,000+ users passing the Journeyman Electrician
Q12.The disconnecting means for a transformer must be:
A.Within 10 feetB.Within sight of the transformerC.Located in a separate roomD.Lockable in the open positionD. Lockable in the open positionExplanation: NEC 450.14 requires a disconnecting means that is lockable in the open position (in accordance with 110.25) to be located in sight of the transformer, unless the location is remote and the disconnect is lockable/labeled.
Join 1,000+ users passing the Journeyman Electrician
Q13.Parallel operation of transformers is permitted only if:
A.They are the same kVA ratingB.They have the same impedance and voltage ratioC.They are from the same manufacturerD.They are oil-filledB. They have the same impedance and voltage ratioExplanation: NEC 450.7 states that transformers may be operated in parallel and switched as a unit provided they have the same transformation ratio, impedance, and other characteristics suitable for parallel operation.
Join 1,000+ users passing the Journeyman Electrician
Q14.Pipes or ducts foreign to the electrical installation shall not pass through a transformer vault unless:
A.They are insulatedB.They contain non-flammable materialC.They are concrete encasedD.They are prohibited entirelyD. They are prohibited entirelyExplanation: NEC 450.47 states that pipes or ducts foreign to the electrical installation shall not pass through the vault.
Join 1,000+ users passing the Journeyman Electrician
Q15.Calculate the primary OCPD rating for a 600V transformer (Primary Current 150A) where secondary protection is NOT provided.
A.150 AmpsB.175 AmpsC.187.5 AmpsD.200 AmpsD. 200 AmpsExplanation: Table 450.3(B) Primary Only protection: 125% of 150A = 187.5A. Note 1 allows the next higher standard rating. The next standard rating after 187.5A is 200A.
Join 1,000+ users passing the Journeyman Electrician
Q16.What is the minimum height of a curb required around an oil-filled transformer installed indoors?
A.2 inchesB.3 inchesC.4 inchesD.6 inchesC. 4 inchesExplanation: NEC 450.43(B) requires a sill or curb of at least 4 inches for transformer vaults to contain oil.
Join 1,000+ users passing the Journeyman Electrician
Q17.A zigzag (interconnected star) grounding autotransformer shall not be used on:
A.A 3-phase, 3-wire systemB.A 3-phase, 4-wire systemC.A system where the neutral is not groundedD.Systems over 1000VB. A 3-phase, 4-wire systemExplanation: NEC 450.5 states that a zigzag grounding autotransformer shall not be installed on the load side of any system grounding connection, effectively prohibiting it on a 4-wire system that already has a neutral.
Join 1,000+ users passing the Journeyman Electrician
Q18.Transformer ventilating openings shall be covered with:
A.PlywoodB.Durable gratings, screens, or louversC.Sheet metalD.Plastic meshB. Durable gratings, screens, or louversExplanation: NEC 450.45(D) requires ventilation openings to be covered with durable gratings, screens, or louvers to prevent entry of animals/foreign objects.
Join 1,000+ users passing the Journeyman Electrician
Q19.When a secondary tie circuit connects two power sources, it must be protected by:
A.A fuse at each endB.A limiter at each endC.An automatic transfer switchD.Ground fault protectionB. A limiter at each endExplanation: NEC 450.6(A)(3) requires a limiter (a special high-capacity fuse) at each end of the tie circuit for protection in network systems.
Join 1,000+ users passing the Journeyman Electrician
Q20.Transformers shall be marked with which of the following?
A.Name of manufacturerB.Rated kVAC.Frequency and VoltageD.All of the aboveD. All of the aboveExplanation: NEC 450.11 requires transformers to be provided with a nameplate giving the name of the manufacturer, rated kVA, frequency, primary and secondary voltage, etc.
Join 1,000+ users passing the Journeyman Electrician
Q21.Less-flammable liquid-insulated transformers installed indoors without a vault must meet listing requirements and the liquid must have a fire point of not less than:
A.200°CB.300°CC.400°CD.500°CB. 300°CExplanation: NEC 450.23(A) requires the liquid to have a fire point of not less than 300°C.
Join 1,000+ users passing the Journeyman Electrician
Q22.Are transformers permitted to be installed on the roof of a building?
A.No, never.B.Yes, if the roof is structural concrete.C.Yes, if oil-filled and provided with a curb.D.Yes, dry-type or specific liquid-filled types are permitted.D. Yes, dry-type or specific liquid-filled types are permitted.Explanation: NEC 450.22 (Dry Type Outdoor) and 450.23-26 imply outdoor installation is permitted. There is no prohibition against roof installation provided structural support and clearances (450.27 for oil-insulated outdoor) are met. Oil-insulated on roofs must respect fire escape clearances.
Join 1,000+ users passing the Journeyman Electrician
Q23.Materials shall not be stored in transformer vaults.
A.TrueB.FalseA. TrueExplanation: NEC 450.48 explicitly states that materials shall not be stored in transformer vaults.
Join 1,000+ users passing the Journeyman Electrician
Q24.A step-down transformer has a primary voltage of 480V and a secondary voltage of 120V. If 10A flows in the primary, what is the secondary current (assuming 100% efficiency)?
A.2.5 AmpsB.10 AmpsC.20 AmpsD.40 AmpsD. 40 AmpsExplanation: Power In = Power Out. 480V * 10A = 4800VA. 4800VA / 120V = 40 Amps.
Join 1,000+ users passing the Journeyman Electrician
Q25.Terminal bars in transformers must be: