Skip to main content

Journeyman Electrician Exam

Voltage Drop Practice Questions

29 practice questions with detailed explanations — aligned to the Journeyman Electrician Exam.

Master Voltage Drop to boost your score on the Journeyman Electrician Exam. Each question below mirrors the style and difficulty of real exam questions, complete with detailed explanations so you understand the why behind every answer. Work through all 29 questions, review any that trip you up, and use the related topics below to round out your preparation.

  1. Q1.The NEC recommends that the maximum voltage drop for a branch circuit should not exceed:

    A.2%
    B.3%
    C.5%
    D.6%
    B3%

    Explanation: NEC 210.19(A) Informational Note recommends that voltage drop on branch circuits should not exceed 3%.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  2. Q2.The combined voltage drop for the feeder and branch circuit should not exceed:

    A.3%
    B.4%
    C.5%
    D.6%
    C5%

    Explanation: NEC 210.19(A) Informational Note 4 suggests a total combined voltage drop of 5% (e.g., 2% feeder + 3% branch, or vice versa).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  3. Q3.Calculate the voltage drop on a 120V single-phase circuit supplying a 16A load. The conductor is 12 AWG solid copper (K=12.9) and the length is 100 feet (one way).

    A.2.5 Volts
    B.5.3 Volts
    C.6.4 Volts
    D.8.1 Volts
    C6.4 Volts

    Explanation: Using the voltage drop formula VD = (2 × K × I × L) / CM, where K = 12.9 for copper, I = 16A, L = 100 ft, and CM for 12 AWG copper = 6,530: VD = (2 × 12.9 × 16 × 100) / 6,530 = 41,280 / 6,530 ≈ 6.3 Volts. This is closest to 6.4 Volts. Alternatively, using the resistance method with R = 1.93 Ω/kft for 12 AWG: VD = 2 × 16 × 1.93 × (100/1000) ≈ 6.2 Volts, also rounding to 6.4V.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  4. Q4.If the voltage at the panel is 240V and the voltage at the load is 230V, what is the percentage of voltage drop?

    A.2.5%
    B.4.2%
    C.5.0%
    D.10.0%
    B4.2%

    Explanation: Drop = 240 - 230 = 10V. % = (10 / 240) * 100 = 4.166%. Rounds to 4.2%.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  5. Q5.What is the standard 'K' factor used for Aluminum conductors in voltage drop calculations?

    A.10.8
    B.12.9
    C.21.2
    D.18.0
    C21.2

    Explanation: The standard resistivity (K) value used for Aluminum in exam calculations is 21.2 (Ohm-CM/ft).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  6. Q6.When calculating voltage drop for a 3-phase system, the formula is modified by:

    A.Dividing by 2
    B.Multiplying by 1.732 instead of 2
    C.Using K=21.2
    D.Ignoring the neutral
    BMultiplying by 1.732 instead of 2

    Explanation: Single phase VD = 2KIL/CM. Three phase VD = 1.732 * K * I * L / CM.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  7. Q7.A 208V, 3-phase motor draws 40A. The distance is 150 ft. What minimum size Copper wire is needed to keep Voltage Drop under 3% (6.24V)? (Use K=12.9).

    A.8 AWG
    B.6 AWG
    C.4 AWG
    D.2 AWG
    B6 AWG

    Explanation: CM = (1.732 * K * I * L) / VD. CM = (1.732 * 12.9 * 40 * 150) / 6.24. CM = 134,056 / 6.24 = 21,483. Table 8: 8 AWG = 16,510. 6 AWG = 26,240. Since 21,483 > 16,510, we need 6 AWG.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  8. Q8.Excessive voltage drop can cause which of the following?

    A.Motors to run cooler
    B.Lights to burn brighter
    C.Motors to overheat and burn out
    D.Circuit breakers to trip faster
    CMotors to overheat and burn out

    Explanation: Low voltage forces motors to draw more current to maintain torque, leading to overheating and potential burnout.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  9. Q9.To reduce voltage drop, you should:

    A.Increase the wire gauge number (e.g., 12 to 14)
    B.Increase the conductor cross-sectional area (e.g., 12 to 10)
    C.Increase the circuit length
    D.Use Aluminum instead of Copper
    BIncrease the conductor cross-sectional area (e.g., 12 to 10)

    Explanation: Increasing the circular mils (area) decreases resistance. Moving from 12 AWG to 10 AWG (larger wire) reduces drop.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  10. Q10.For a fire pump, the voltage drop at the motor terminals during starting (locked rotor) shall not exceed:

    A.5%
    B.10%
    C.15%
    D.25%
    C15%

    Explanation: NEC 695.7(A) states that voltage at the fire pump controller line terminals shall not drop more than 15% below normal during starting (locked rotor).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  11. Q11.When the fire pump is running at 115% load, the voltage at the motor terminals shall not drop more than:

    A.3%
    B.5%
    C.10%
    D.15%
    B5%

    Explanation: NEC 695.7(B) requires that the voltage not drop more than 5% below the rating of the motor when running at 115% full load.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  12. Q12.Which NEC article contains the Informational Note regarding voltage drop efficiency?

    A.Article 110
    B.Article 210
    C.Article 250
    D.Article 430
    BArticle 210

    Explanation: Article 210.19(A) Informational Note 4 contains the 3% / 5% efficiency recommendation.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  13. Q13.Calculate the Circular Mils (CM) of a conductor required to carry 50A for 200 ft on a 240V single-phase circuit with max 3% drop (7.2V). (K=12.9).

    A.35,833 CM
    B.26,240 CM
    C.41,740 CM
    D.52,620 CM
    A35,833 CM

    Explanation: CM = (2 * K * I * L) / VD. CM = (2 * 12.9 * 50 * 200) / 7.2. CM = 258,000 / 7.2 = 35,833 CM. (This would require 4 AWG, which is 41,740 CM).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  14. Q14.Sensitive electronic equipment often requires a cleaner power supply. When sizing conductors for this equipment, what is often prioritized?

    A.Minimizing Voltage Drop
    B.Maximizing Voltage Drop
    C.Using Aluminum conductors
    D.Using shared neutrals
    AMinimizing Voltage Drop

    Explanation: Minimizing voltage drop (often to 1-2%) is critical for sensitive electronics to prevent resets or data errors.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  15. Q15.The resistance of a 1000 ft length of 10 AWG Copper wire (uncoated) is approximately:

    A.0.5 Ohms
    B.1.2 Ohms
    C.2.0 Ohms
    D.5.0 Ohms
    B1.2 Ohms

    Explanation: Chapter 9 Table 8 lists 10 AWG Uncoated Copper resistance at approx 1.2 ohms per 1000 ft (specifically 0.998 to 1.2 depending on stranding/coating, solid is ~1.0, stranded ~1.2). 1.2 is the safe field calc value.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  16. Q16.A circuit is 200 feet long using 12 AWG copper (R=2 ohms/kft). The load is 10A. What is the voltage drop?

    A.2 Volts
    B.4 Volts
    C.8 Volts
    D.12 Volts
    C8 Volts

    Explanation: Using the resistance method: VD = 2 × I × R × (L/1000). With I = 10A, R = 2 Ω/kft, and L = 200 ft: VD = 2 × 10 × 2 × (200/1000) = 2 × 10 × 2 × 0.2 = 8 Volts. The factor of 2 accounts for both the outgoing and return conductors in a single-phase circuit.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  17. Q17.A circuit is 200 feet long (one way) using 12 AWG copper (approx 2 ohms/1000 ft). The load is 10A. What is the voltage drop?

    A.2 Volts
    B.4 Volts
    C.8 Volts
    D.10 Volts
    C8 Volts

    Explanation: Total wire length = 2 * 200 = 400 ft. Resistance = 400 ft * (2 ohms/1000 ft) = 0.8 ohms. V = I * R = 10A * 0.8 ohms = 8 Volts.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  18. Q18.If you parallel two conductors per phase, what happens to the voltage drop?

    A.It doubles
    B.It stays the same
    C.It decreases by half
    D.It increases by 50%
    CIt decreases by half

    Explanation: Paralleling two identical conductors effectively doubles the Circular Mils (Area). Since VD is inversely proportional to Area (VD = KIL/CM), doubling the area halves the voltage drop.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  19. Q19.In a DC circuit, which factor is NOT used in the voltage drop formula?

    A.Current (I)
    B.Length (L)
    C.Power Factor
    D.Resistance (R)
    CPower Factor

    Explanation: DC circuits do not have Power Factor (or reactance). The formula is purely resistive (V=IR).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  20. Q20.Is voltage drop consideration mandatory in the NEC for general branch circuits?

    A.Yes, strictly mandatory
    B.No, it is an Informational Note (recommendation)
    C.Only for circuits over 100A
    D.Only for hospitals
    BNo, it is an Informational Note (recommendation)

    Explanation: For general branch circuits, 210.19(A) FPN is an explanatory note, not a mandatory code rule (enforceable language like 'shall'). However, 695.7 (Fire Pumps) and 647 (Sensitive Equip) are mandatory.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  21. Q21.When upsizing conductors for voltage drop, what must also be checked?

    A.The equipment grounding conductor size
    B.The insulation color
    C.The conduit type
    D.The manufacturer date
    AThe equipment grounding conductor size

    Explanation: NEC 250.122(B) requires that if ungrounded conductors are increased in size (e.g. for voltage drop), the equipment grounding conductor must be increased proportionately.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  22. Q22.A 120V circuit has a 5% voltage drop. What is the voltage at the load?

    A.110 Volts
    B.114 Volts
    C.115 Volts
    D.116 Volts
    B114 Volts

    Explanation: 5% of 120V = 6 Volts. 120 - 6 = 114 Volts.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  23. Q23.Which conductor material has a higher 'K' value (more resistance)?

    A.Copper
    B.Aluminum
    C.Gold
    D.Silver
    BAluminum

    Explanation: Aluminum (K ~21.2) has higher resistance than Copper (K ~12.9).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  24. Q24.For a 240V, single-phase circuit, the '2' in the formula 2KIL/CM represents:

    A.The two ungrounded conductors (there and back)
    B.The safety factor
    C.The voltage multiplier
    D.The temperature correction
    AThe two ungrounded conductors (there and back)

    Explanation: The '2' accounts for the total length of the wire (out to the load and back to the source).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  25. Q25.A conductor has 10,000 CM. If you switch to a conductor with 20,000 CM, the voltage drop will:

    A.Double
    B.Be cut in half
    C.Stay the same
    D.Increase by 10%
    BBe cut in half

    Explanation: Doubling the Circular Mils (denominator) halves the result (Voltage Drop).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  26. Q26.In a 3-wire, single-phase 120/240V circuit carrying a balanced load, what is the voltage drop on the neutral?

    A.Same as the hot wires
    B.Zero
    C.Half the hot wires
    D.Double the hot wires
    BZero

    Explanation: In a perfectly balanced 3-wire single-phase circuit, the neutral carries 0 amps. Since V=IR, if I=0, the voltage drop on the neutral is 0.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  27. Q27.Which formula gives single-phase voltage drop?

    A.VD = (2 x K x I x L) / CM
    B.VD = (K x I x L) / CM
    C.VD = (1.732 x K x I x L) / CM
    D.VD = (2 x CM) / (K x I x L)
    AVD = (2 x K x I x L) / CM

    Explanation: Single-phase voltage drop is VD = (2 x K x I x L) / CM. The three-phase version replaces the 2 with 1.732 (the square root of 3).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  28. Q28.In the voltage drop formula, what is the approximate value of the constant K for copper conductors?

    A.11.2
    B.12.9
    C.17.0
    D.21.2
    B12.9

    Explanation: K is approximately 12.9 for copper and 21.2 for aluminum (ohms-circular mils per foot).

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

  29. Q29.A 120 V, 20 A branch circuit runs 100 ft (one way) on 10 AWG copper (10,380 circular mils). What is the approximate percentage voltage drop?

    A.1.6%
    B.2.6%
    C.4.1%
    D.6.0%
    C4.1%

    Explanation: VD = (2 x 12.9 x 20 x 100) / 10,380 = 4.97 V. As a percentage: 4.97 / 120 = 4.1%, which exceeds the NEC's recommended 3% maximum for branch circuits, so you would upsize to 8 AWG.

    See answer — start free trial

    3-day free trial · $9.99/mo after · cancel anytime

More Journeyman Electrician Exam Topics

Studying for the Journeyman Electrician exam? Read more about Electrician Prep