Skip to main content

Journeyman Electrician Exam

Wiring Methods Practice Questions

70 practice questions with detailed explanations — aligned to the Journeyman Electrician Exam.

  1. Q1.What is the maximum distance between supports for 1/2 inch Electrical Metallic Tubing (EMT)?

    A.3 feet
    B.5 feet
    C.10 feet
    D.12 feet
    C10 feet

    Explanation: NEC 358.30(A) requires EMT to be securely fastened at least every 10 feet.

    Join 1,000+ users passing the Journeyman Electrician

  2. Q2.Type NM cable shall be secured within _____ of every box or cabinet.

    A.6 inches
    B.8 inches
    C.12 inches
    D.18 inches
    C12 inches

    Explanation: NEC 334.30 requires Type NM cable to be secured within 12 inches of every outlet box, junction box, cabinet, or fitting.

    Join 1,000+ users passing the Journeyman Electrician

  3. Q3.Rigid Metal Conduit (RMC) shall be supported at intervals not exceeding:

    A.6 feet
    B.10 feet
    C.12 feet
    D.20 feet
    B10 feet

    Explanation: NEC 344.30(B)(1) requires RMC to be supported at intervals not exceeding 10 feet (unless larger sizes and vertical runs permit greater distance, 10 ft is the standard rule).

    Join 1,000+ users passing the Journeyman Electrician

  4. Q4.Liquidtight Flexible Metal Conduit (LFMC) shall be securely fastened within _____ of each box or other conduit termination.

    A.6 inches
    B.12 inches
    C.18 inches
    D.24 inches
    B12 inches

    Explanation: NEC 350.30(A) requires LFMC to be secured within 12 inches of the termination.

    Join 1,000+ users passing the Journeyman Electrician

  5. Q5.What is the minimum cover requirement for PVC conduit installed under a driveway of a one-family dwelling?

    A.12 inches
    B.18 inches
    C.24 inches
    D.6 inches
    B18 inches

    Explanation: Table 300.5 Col 3 (Nonmetallic Raceways) under 'Driveways... One and Two Family Dwellings' requires 18 inches of cover.

    Join 1,000+ users passing the Journeyman Electrician

  6. Q6.Nonmetallic-Sheathed Cable (Type NM) is permitted to be used in:

    A.Commercial garages
    B.One- and two-family dwellings
    C.Theatres
    D.Motion picture studios
    BOne- and two-family dwellings

    Explanation: NEC 334.10 permits NM cable in one- and two-family dwellings (and multifamily/other structures types III, IV, V). It is prohibited in commercial garages, theaters, etc. by 334.12.

    Join 1,000+ users passing the Journeyman Electrician

  7. Q7.Cables installed in shallow grooves in wood studs must be protected by a steel plate if the edge of the hole is less than _____ from the nearest edge of the stud.

    A.1/2 inch
    B.1 inch
    C.1-1/4 inches
    D.1-1/2 inches
    C1-1/4 inches

    Explanation: NEC 300.4(A)(1) requires a 1/16 inch steel plate if the hole/groove is less than 1-1/4 inches from the edge of the wood member.

    Join 1,000+ users passing the Journeyman Electrician

  8. Q8.Which wiring method is NOT permitted in a plenum (air-handling) space?

    A.Electrical Metallic Tubing (EMT)
    B.Type MC Cable (smooth or corrugated sheath)
    C.Type NM Cable
    D.Rigid Metal Conduit
    CType NM Cable

    Explanation: NEC 300.22(C) prohibits Type NM cable in spaces used for environmental air (plenums) because it emits toxic fumes when burned. Metal raceways and plenum-rated cables are required.

    Join 1,000+ users passing the Journeyman Electrician

  9. Q9.When using Armored Cable (Type AC), an anti-short bushing is:

    A.Required only for damp locations
    B.Required at every termination point
    C.Optional if the connector has an insulated throat
    D.Not required for 12 AWG or smaller
    BRequired at every termination point

    Explanation: NEC 320.40 requires an insulating bushing (anti-short) at the termination of Type AC cable to protect wires from the sharp metal armor.

    Join 1,000+ users passing the Journeyman Electrician

  10. Q10.Surface Metal Raceways (like Wiremold) shall only be installed in:

    A.Dry locations
    B.Wet locations
    C.Corrosive locations
    D.Underground locations
    ADry locations

    Explanation: NEC 386.10 states that surface metal raceways shall be permitted in dry locations. 386.12 prohibits them in severe corrosive environments or hoistways (unless listed).

    Join 1,000+ users passing the Journeyman Electrician

  11. Q11.Underground service conductors that are not encased in concrete and are buried 18 inches or more below grade shall have their location identified by a warning ribbon placed _____ above the underground installation.

    A.6 inches
    B.12 inches
    C.18 inches
    D.24 inches
    B12 inches

    Explanation: NEC 300.5(D)(3) requires a warning ribbon at least 12 inches above the underground installation for service conductors not encased in concrete.

    Join 1,000+ users passing the Journeyman Electrician

  12. Q12.When Types NM or AC cable are run through bored holes in framing members, holes shall be bored so that the edge of the hole is not less than _____ from the nearest edge of the wood member.

    A.1/2 inch
    B.3/4 inch
    C.1 inch
    D.1 1/4 inches
    D1 1/4 inches

    Explanation: NEC 300.4(A)(1) sets the 1 1/4 inch distance to protect the cable from drywall screws/nails.

    Join 1,000+ users passing the Journeyman Electrician

  13. Q13.Flat Cable Assemblies (Type FC) shall be permitted only in:

    A.Surface metal raceways
    B.Exposed locations
    C.Hoistways
    D.Battery rooms
    BExposed locations

    Explanation: NEC 322.10(1) permits Type FC for exposed locations. It is mounted on a specific channel.

    Join 1,000+ users passing the Journeyman Electrician

  14. Q14.Cable trays are considered:

    A.A raceway
    B.A support system
    C.An enclosure
    D.A conduit
    BA support system

    Explanation: NEC 392.2 defines a cable tray system as a unit or assembly of units or sections and associated fittings forming a structural system used to securely fasten or support cables and raceways. It is technically a 'support system' for wiring methods, not a raceway itself (though often treated similarly for fill).

    Join 1,000+ users passing the Journeyman Electrician

  15. Q15.According to NEC 2026, Article 722 was expanded to include rules for 'Class 4' systems. Which wiring method is explicitly permitted for Class 4 Fault-Managed Power?

    A.Type FMP Cable
    B.Type NM Cable
    C.Standard Ethernet Cable (Cat 5e)
    D.Uninsulated conductors
    AType FMP Cable

    Explanation: Class 4 systems (Fault-Managed Power) require specific cables designated for the safety protocols they use. Type FMP (Fault-Managed Power) is the designation.

    Join 1,000+ users passing the Journeyman Electrician

  16. Q16.Expansion fittings for PVC conduit are required where the thermal expansion and contraction is expected to exceed:

    A.1/8 inch
    B.1/4 inch
    C.1/2 inch
    D.1 inch
    B1/4 inch

    Explanation: NEC 352.44 requires expansion fittings where length change is expected to be 1/4 inch (6 mm) or greater in a straight run.

    Join 1,000+ users passing the Journeyman Electrician

  17. Q17.The maximum number of 1/4 bends (90 degrees) allowed in a run of conduit between pull points is:

    A.Two (180 degrees)
    B.Three (270 degrees)
    C.Four (360 degrees)
    D.Five (450 degrees)
    CFour (360 degrees)

    Explanation: NEC 358.26 (and similar for other conduits) limits bends to 360 degrees total (equivalent to four quarter bends).

    Join 1,000+ users passing the Journeyman Electrician

  18. Q18.Metal Clad Cable (Type MC) supports are not required when the cable is fished between access points in finished buildings or concealed spaces.

    A.True
    B.False
    C.Only if less than 6 feet
    D.Only if supported at ends
    ATrue

    Explanation: NEC 330.30(D)(1) permits MC cable to be unsupported when fished between access points through concealed spaces in finished buildings.

    Join 1,000+ users passing the Journeyman Electrician

  19. Q19.In a vertical raceway, 1/0 AWG copper conductors must be supported at intervals not exceeding:

    A.50 feet
    B.60 feet
    C.80 feet
    D.100 feet
    D100 feet

    Explanation: NEC Table 300.19(A) requires support for 1/0 AWG copper in vertical raceways at intervals not exceeding 100 feet.

    Join 1,000+ users passing the Journeyman Electrician

  20. Q20.What is the minimum depth of working space in front of a 480V panelboard (Condition 2: Exposed Live Parts vs Grounded Wall)?

    A.3 feet
    B.3.5 feet
    C.4 feet
    D.5 feet
    B3.5 feet

    Explanation: Table 110.26(A)(1). Voltage 151-600V. Condition 2 (Live parts opposite grounded surface/concrete). Distance required is 3 feet 6 inches (3.5 ft). (Condition 1 is 3 ft, Condition 3 is 4 ft).

    Join 1,000+ users passing the Journeyman Electrician

  21. Q21.Electrical Nonmetallic Tubing (ENT), also known as 'Smurf Tube', is permitted to be installed:

    A.In direct sunlight without listing
    B.Embedded in concrete slabs
    C.For system voltages over 1000V
    D.In theaters
    BEmbedded in concrete slabs

    Explanation: NEC 362.10 allows ENT to be embedded in concrete slabs on grade or above grade. It is generally not permitted in direct sunlight unless marked, nor in theaters (assembly occupancies) unless concealed.

    Join 1,000+ users passing the Journeyman Electrician

  22. Q22.When using Service-Entrance Cable (Type SE) for interior branch circuits, the cable must be:

    A.Secured every 4.5 feet
    B.Used only for ranges and dryers
    C.Installed in a raceway
    D.Used provided the insulated conductors are rated for the circuit voltage and temp (typically 75°C)
    DUsed provided the insulated conductors are rated for the circuit voltage and temp (typically 75°C)

    Explanation: NEC 338.10(B)(4) requires Type SE cable used for interior wiring to comply with Part II of Article 334 (NM Cable), excluding 334.80 ampacity limits if insulation is rated higher? Wait. 338.10(B)(4)(a) says interior installations must comply with Part II of Article 334. This invokes the securing/supporting rules of NM (4.5 ft), but the most distinct requirement often tested is that it follows NM rules generally.

    Join 1,000+ users passing the Journeyman Electrician

  23. Q23.Splices and taps shall not be made within raceways unless:

    A.The raceway is EMT
    B.The fill is less than 20%
    C.The raceway is a wireway with removable covers
    D.The voltage is less than 50V
    CThe raceway is a wireway with removable covers

    Explanation: NEC 376.56 permits splices and taps within metal wireways (which have covers), provided they do not fill more than 75% of the cross-section. Standard conduits (EMT/RMC) cannot contain splices.

    Join 1,000+ users passing the Journeyman Electrician

  24. Q24.A box installed in a wet location must be:

    A.Weatherproof
    B.Rainproof only
    C.Listed for damp locations
    D.NEMA 1
    AWeatherproof

    Explanation: NEC 314.15 requires boxes in wet locations to be listed for use in wet locations (often marked 'Wet Location' or 'Weatherproof').

    Join 1,000+ users passing the Journeyman Electrician

  25. Q25.Insulated bushings are required on raceways containing conductors of _____ or larger.

    A.8 AWG
    B.6 AWG
    C.4 AWG
    D.4/0 AWG
    C4 AWG

    Explanation: NEC 300.4(G) requires an insulating bushing (or smooth rounded entry) where raceways contain ungrounded conductors 4 AWG or larger entering a cabinet, box, or enclosure.

    Join 1,000+ users passing the Journeyman Electrician

  26. Q26.The minimum length of free conductor to be left at each outlet, junction, and switch point for splices is:

    A.3 inches
    B.4 inches
    C.6 inches
    D.8 inches
    C6 inches

    Explanation: NEC 300.14 requires at least 6 inches of free conductor, measured from the point in the box where it emerges from its raceway or cable sheath.

    Join 1,000+ users passing the Journeyman Electrician

  27. Q27.Horizontal runs of RMC supported by openings through framing members at intervals not exceeding 10 feet and securely fastened within _____ of termination points are permitted.

    A.1 foot
    B.3 feet
    C.5 feet
    D.10 feet
    B3 feet

    Explanation: NEC 344.30(B)(4) allows horizontal runs of RMC through framing members to be supported by the members (no extra straps) if fastened within 3 feet of termination.

    Join 1,000+ users passing the Journeyman Electrician

  28. Q28.At what distance from a box must the first support be installed for Flexible Metal Conduit (FMC)?

    A.6 inches
    B.12 inches
    C.18 inches
    D.24 inches
    B12 inches

    Explanation: NEC 348.30(A) requires FMC to be securely fastened within 12 inches of each box, cabinet, conduit body, or other termination.

    Join 1,000+ users passing the Journeyman Electrician

  29. Q29.Underfloor raceways shall not be installed:

    A.In concrete
    B.Where subject to corrosive vapors
    C.In office buildings
    D.Beneath carpet
    BWhere subject to corrosive vapors

    Explanation: NEC 390.12(1) prohibits underfloor raceways where subject to corrosive vapors.

    Join 1,000+ users passing the Journeyman Electrician

  30. Q30.A fitting is defined as an accessory such as a locknut, bushing, or other part of a wiring system that is intended primarily to perform a ____ function.

    A.Electrical
    B.Mechanical
    C.Grounding
    D.Insulating
    BMechanical

    Explanation: NEC 100 Definition: A fitting performs a mechanical function rather than an electrical one.

    Join 1,000+ users passing the Journeyman Electrician

  31. Q31.Type TC (Tray Cable) cable is permitted to be used:

    A.Installed in cable trays
    B.As open wiring on brackets
    C.Installed as aerial cable on a messenger
    D.Directly buried without listing
    AInstalled in cable trays

    Explanation: NEC 336.10 permits Type TC cable for power, lighting, control, and signal circuits in cable trays. (Direct burial requires specific listing 'TC-ER' or similar marking).

    Join 1,000+ users passing the Journeyman Electrician

  32. Q32.Where conductors 4 AWG and larger enter an enclosure, the insulating bushing is required to protect the conductors. Is a metal bushing with a bakelite throat acceptable?

    A.Yes
    B.No, it must be wholly insulating material
    C.Only for voltages under 250V
    D.Only for grounded conductors
    AYes

    Explanation: NEC 300.4(G) accepts insulating bushings or 'other identified insulating material'. A metal bushing with an insulating insert (throat) is the standard method of compliance.

    Join 1,000+ users passing the Journeyman Electrician

  33. Q33.What is the maximum distance between supports for a vertical run of 500 kcmil copper conductors in a raceway?

    A.50 feet
    B.60 feet
    C.80 feet
    D.100 feet
    A50 feet

    Explanation: NEC Table 300.19(A) requires support every 50 feet for conductors 250 kcmil through 500 kcmil copper.

    Join 1,000+ users passing the Journeyman Electrician

  34. Q34.When installing PVC conduit, if the temperature change is 40°F, an expansion fitting is required if the run exceeds:

    A.25 feet
    B.45 feet
    C.50 feet
    D.The length where length change is 1/4 inch
    DThe length where length change is 1/4 inch

    Explanation: NEC 352.44 requires expansion fittings where the length change is 1/4 inch or greater. The specific length of run depends on the calculation (Table 352.44). For a 40°F change, PVC expands approx 1.6 inches per 100 ft. A 1/4 inch change happens in about 15 feet. But the 'code rule' answer is the condition: 'Where the length change is expected to be 1/4 inch or greater'.

    Join 1,000+ users passing the Journeyman Electrician

  35. Q35.Busways shall be supported at intervals not exceeding _____ unless otherwise designed and marked.

    A.3 feet
    B.5 feet
    C.10 feet
    D.12 feet
    B5 feet

    Explanation: NEC 368.30 requires busways to be supported at intervals not exceeding 5 feet unless otherwise designed and marked.

    Join 1,000+ users passing the Journeyman Electrician

  36. Q36.NEC 2026 300.5(D) updates regarding 'Protection from Damage' for underground conductors now emphasizes protecting:

    A.Emerging grade-level conductors with Schedule 80 PVC
    B.Conductors in manholes
    C.Low voltage landscape lighting
    D.Direct burial cable in clay soil
    AEmerging grade-level conductors with Schedule 80 PVC

    Explanation: The 2026 code reinforces that conductors emerging from grade must be protected by enclosures or raceways (Schedule 80 PVC) to a point 8 feet above grade.

    Join 1,000+ users passing the Journeyman Electrician

  37. Q37.Multi-outlet assemblies (like Plugmold) are not permitted:

    A.In dry locations
    B.Where concealed
    C.Where voltage is 120V
    D.Through partitions
    BWhere concealed

    Explanation: NEC 380.12 prohibits multi-outlet assemblies where concealed.

    Join 1,000+ users passing the Journeyman Electrician

  38. Q38.Nonmetallic Extension (surface extensions) shall be run:

    A.Concealed
    B.Exposed only
    C.Through floors
    D.Through walls
    BExposed only

    Explanation: NEC 382.10 requires Nonmetallic Extensions to be run exposed.

    Join 1,000+ users passing the Journeyman Electrician

  39. Q39.The maximum size of Electrical Metallic Tubing (EMT) tubing is:

    A.3 inch
    B.4 inch
    C.5 inch
    D.6 inch
    B4 inch

    Explanation: NEC 358.20(B) states the maximum size for EMT is Metric Designator 103 (Trade Size 4).

    Join 1,000+ users passing the Journeyman Electrician

  40. Q40.Integrated Gas Spacer Cable (Type IGS) uses which gas for insulation?

    A.Nitrogen
    B.Sulfur Hexafluoride (SF6)
    C.Helium
    D.Oxygen
    BSulfur Hexafluoride (SF6)

    Explanation: NEC 326.2 defines Type IGS cable as using Sulfur Hexafluoride (SF6) gas.

    Join 1,000+ users passing the Journeyman Electrician

  41. Q41.Strut-type channel raceways shall be supported at intervals not exceeding:

    A.5 feet
    B.10 feet
    C.15 feet
    D.20 feet
    B10 feet

    Explanation: NEC 384.30 requires strut-type channel raceways to be supported at intervals not exceeding 10 feet.

    Join 1,000+ users passing the Journeyman Electrician

  42. Q42.Auxiliary gutters shall not extend greater than _____ beyond the equipment they supplement.

    A.10 feet
    B.20 feet
    C.30 feet
    D.50 feet
    C30 feet

    Explanation: NEC 366.12 states auxiliary gutters shall not extend more than 30 feet beyond the equipment.

    Join 1,000+ users passing the Journeyman Electrician

  43. Q43.Cellular Concrete Floor Raceways are limited to conductors not larger than:

    A.1/0 AWG
    B.4/0 AWG
    C.500 kcmil
    D.No limit
    A1/0 AWG

    Explanation: NEC 372.20 limits conductor size in cellular concrete floor raceways to 1/0 AWG, except by special permission.

    Join 1,000+ users passing the Journeyman Electrician

  44. Q44.When raceways are installed in a suspended ceiling used for environmental air (plenum), which type is permitted?

    A.Schedule 40 PVC
    B.Electrical Metallic Tubing (EMT)
    C.ENT (Smurf Tube)
    D.Liquidtight Flexible Nonmetallic Conduit
    BElectrical Metallic Tubing (EMT)

    Explanation: NEC 300.22(C) requires metal raceways (like EMT) or plenum-rated cables. Standard PVC and ENT are not permitted due to smoke generation.

    Join 1,000+ users passing the Journeyman Electrician

  45. Q45.What is the maximum fill percentage for a conduit over 24 inches long containing more than 2 conductors?

    A.31%
    B.40%
    C.53%
    D.60%
    B40%

    Explanation: Chapter 9 Table 1 limits conduit fill to 40% for over 2 conductors (new or existing).

    Join 1,000+ users passing the Journeyman Electrician

  46. Q46.Electrical Nonmetallic Tubing (ENT), also known as 'Smurf Tube', is permitted to be installed:

    A.In direct sunlight without listing
    B.Embedded in concrete slabs
    C.For system voltages over 1000V
    D.In theaters
    BEmbedded in concrete slabs

    Explanation: NEC 362.10 allows ENT to be embedded in concrete slabs on grade or above grade. It is generally not permitted in direct sunlight unless marked, nor in theaters (assembly occupancies) unless concealed.

    Join 1,000+ users passing the Journeyman Electrician

  47. Q47.When using Service-Entrance Cable (Type SE) for interior branch circuits, the cable must be:

    A.Secured every 4.5 feet
    B.Used only for ranges and dryers
    C.Installed in a raceway
    D.Used provided the insulated conductors are rated for the circuit voltage and temp (typically 75°C)
    DUsed provided the insulated conductors are rated for the circuit voltage and temp (typically 75°C)

    Explanation: NEC 338.10(B)(4) requires Type SE cable used for interior wiring to comply with Part II of Article 334 (NM Cable), excluding 334.80 ampacity limits if insulation is rated higher? Wait. 338.10(B)(4)(a) says interior installations must comply with Part II of Article 334. This invokes the securing/supporting rules of NM (4.5 ft), but the most distinct requirement often tested is that it follows NM rules generally.

    Join 1,000+ users passing the Journeyman Electrician

  48. Q48.Splices and taps shall not be made within raceways unless:

    A.The raceway is EMT
    B.The fill is less than 20%
    C.The raceway is a wireway with removable covers
    D.The voltage is less than 50V
    CThe raceway is a wireway with removable covers

    Explanation: NEC 376.56 permits splices and taps within metal wireways (which have covers), provided they do not fill more than 75% of the cross-section. Standard conduits (EMT/RMC) cannot contain splices.

    Join 1,000+ users passing the Journeyman Electrician

  49. Q49.A box installed in a wet location must be:

    A.Weatherproof
    B.Rainproof only
    C.Listed for damp locations
    D.NEMA 1
    AWeatherproof

    Explanation: NEC 314.15 requires boxes in wet locations to be listed for use in wet locations (often marked 'Wet Location' or 'Weatherproof').

    Join 1,000+ users passing the Journeyman Electrician

  50. Q50.Insulated bushings are required on raceways containing conductors of _____ or larger.

    A.8 AWG
    B.6 AWG
    C.4 AWG
    D.4/0 AWG
    C4 AWG

    Explanation: NEC 300.4(G) requires an insulating bushing (or smooth rounded entry) where raceways contain ungrounded conductors 4 AWG or larger entering a cabinet, box, or enclosure.

    Join 1,000+ users passing the Journeyman Electrician

  51. Q51.The minimum length of free conductor to be left at each outlet, junction, and switch point for splices is:

    A.3 inches
    B.4 inches
    C.6 inches
    D.8 inches
    C6 inches

    Explanation: NEC 300.14 requires at least 6 inches of free conductor, measured from the point in the box where it emerges from its raceway or cable sheath.

    Join 1,000+ users passing the Journeyman Electrician

  52. Q52.Horizontal runs of RMC supported by openings through framing members at intervals not exceeding 10 feet and securely fastened within _____ of termination points are permitted.

    A.1 foot
    B.3 feet
    C.5 feet
    D.10 feet
    B3 feet

    Explanation: NEC 344.30(B)(4) allows horizontal runs of RMC through framing members to be supported by the members (no extra straps) if fastened within 3 feet of termination.

    Join 1,000+ users passing the Journeyman Electrician

  53. Q53.At what distance from a box must the first support be installed for Flexible Metal Conduit (FMC)?

    A.6 inches
    B.12 inches
    C.18 inches
    D.24 inches
    B12 inches

    Explanation: NEC 348.30(A) requires FMC to be securely fastened within 12 inches of each box, cabinet, conduit body, or other termination.

    Join 1,000+ users passing the Journeyman Electrician

  54. Q54.Underfloor raceways shall not be installed:

    A.In concrete
    B.Where subject to corrosive vapors
    C.In office buildings
    D.Beneath carpet
    BWhere subject to corrosive vapors

    Explanation: NEC 390.12(1) prohibits underfloor raceways where subject to corrosive vapors.

    Join 1,000+ users passing the Journeyman Electrician

  55. Q55.A fitting is defined as an accessory such as a locknut, bushing, or other part of a wiring system that is intended primarily to perform a ____ function.

    A.Electrical
    B.Mechanical
    C.Grounding
    D.Insulating
    BMechanical

    Explanation: NEC 100 Definition: A fitting performs a mechanical function rather than an electrical one.

    Join 1,000+ users passing the Journeyman Electrician

  56. Q56.Type TC (Tray Cable) cable is permitted to be used:

    A.Installed in cable trays
    B.As open wiring on brackets
    C.Installed as aerial cable on a messenger
    D.Directly buried without listing
    AInstalled in cable trays

    Explanation: NEC 336.10 permits Type TC cable for power, lighting, control, and signal circuits in cable trays. (Direct burial requires specific listing 'TC-ER' or similar marking).

    Join 1,000+ users passing the Journeyman Electrician

  57. Q57.Where conductors 4 AWG and larger enter an enclosure, the insulating bushing is required to protect the conductors. Is a metal bushing with a bakelite throat acceptable?

    A.Yes
    B.No, it must be wholly insulating material
    C.Only for voltages under 250V
    D.Only for grounded conductors
    AYes

    Explanation: NEC 300.4(G) accepts insulating bushings or 'other identified insulating material'. A metal bushing with an insulating insert (throat) is the standard method of compliance.

    Join 1,000+ users passing the Journeyman Electrician

  58. Q58.What is the maximum distance between supports for a vertical run of 500 kcmil copper conductors in a raceway?

    A.50 feet
    B.60 feet
    C.80 feet
    D.100 feet
    A50 feet

    Explanation: NEC Table 300.19(A) requires support every 50 feet for conductors 250 kcmil through 500 kcmil copper.

    Join 1,000+ users passing the Journeyman Electrician

  59. Q59.When installing PVC conduit, if the temperature change is 40°F, an expansion fitting is required if the run exceeds:

    A.25 feet
    B.45 feet
    C.50 feet
    D.The length where length change is 1/4 inch
    DThe length where length change is 1/4 inch

    Explanation: NEC 352.44 requires expansion fittings where the length change is 1/4 inch or greater. The specific length of run depends on the calculation (Table 352.44). For a 40°F change, PVC expands approx 1.6 inches per 100 ft. A 1/4 inch change happens in about 15 feet. But the 'code rule' answer is the condition: 'Where the length change is expected to be 1/4 inch or greater'.

    Join 1,000+ users passing the Journeyman Electrician

  60. Q60.Busways shall be supported at intervals not exceeding _____ unless otherwise designed and marked.

    A.3 feet
    B.5 feet
    C.10 feet
    D.12 feet
    B5 feet

    Explanation: NEC 368.30 requires busways to be supported at intervals not exceeding 5 feet unless otherwise designed and marked.

    Join 1,000+ users passing the Journeyman Electrician

  61. Q61.NEC 2026 300.5(D) updates regarding 'Protection from Damage' for underground conductors now emphasizes protecting:

    A.Emerging grade-level conductors with Schedule 80 PVC
    B.Conductors in manholes
    C.Low voltage landscape lighting
    D.Direct burial cable in clay soil
    AEmerging grade-level conductors with Schedule 80 PVC

    Explanation: The 2026 code reinforces that conductors emerging from grade must be protected by enclosures or raceways (Schedule 80 PVC) to a point 8 feet above grade.

    Join 1,000+ users passing the Journeyman Electrician

  62. Q62.Multi-outlet assemblies (like Plugmold) are not permitted:

    A.In dry locations
    B.Where concealed
    C.Where voltage is 120V
    D.Through partitions
    BWhere concealed

    Explanation: NEC 380.12 prohibits multi-outlet assemblies where concealed.

    Join 1,000+ users passing the Journeyman Electrician

  63. Q63.Nonmetallic Extension (surface extensions) shall be run:

    A.Concealed
    B.Exposed only
    C.Through floors
    D.Through walls
    BExposed only

    Explanation: NEC 382.10 requires Nonmetallic Extensions to be run exposed.

    Join 1,000+ users passing the Journeyman Electrician

  64. Q64.The maximum size of Electrical Metallic Tubing (EMT) tubing is:

    A.3 inch
    B.4 inch
    C.5 inch
    D.6 inch
    B4 inch

    Explanation: NEC 358.20(B) states the maximum size for EMT is Metric Designator 103 (Trade Size 4).

    Join 1,000+ users passing the Journeyman Electrician

  65. Q65.Integrated Gas Spacer Cable (Type IGS) uses which gas for insulation?

    A.Nitrogen
    B.Sulfur Hexafluoride (SF6)
    C.Helium
    D.Oxygen
    BSulfur Hexafluoride (SF6)

    Explanation: NEC 326.2 defines Type IGS cable as using Sulfur Hexafluoride (SF6) gas.

    Join 1,000+ users passing the Journeyman Electrician

  66. Q66.Strut-type channel raceways shall be supported at intervals not exceeding:

    A.5 feet
    B.10 feet
    C.15 feet
    D.20 feet
    B10 feet

    Explanation: NEC 384.30 requires strut-type channel raceways to be supported at intervals not exceeding 10 feet.

    Join 1,000+ users passing the Journeyman Electrician

  67. Q67.Auxiliary gutters shall not extend greater than _____ beyond the equipment they supplement.

    A.10 feet
    B.20 feet
    C.30 feet
    D.50 feet
    C30 feet

    Explanation: NEC 366.12 states auxiliary gutters shall not extend more than 30 feet beyond the equipment.

    Join 1,000+ users passing the Journeyman Electrician

  68. Q68.Cellular Concrete Floor Raceways are limited to conductors not larger than:

    A.1/0 AWG
    B.4/0 AWG
    C.500 kcmil
    D.No limit
    A1/0 AWG

    Explanation: NEC 372.20 limits conductor size in cellular concrete floor raceways to 1/0 AWG, except by special permission.

    Join 1,000+ users passing the Journeyman Electrician

  69. Q69.When raceways are installed in a suspended ceiling used for environmental air (plenum), which type is permitted?

    A.Schedule 40 PVC
    B.Electrical Metallic Tubing (EMT)
    C.ENT (Smurf Tube)
    D.Liquidtight Flexible Nonmetallic Conduit
    BElectrical Metallic Tubing (EMT)

    Explanation: NEC 300.22(C) requires metal raceways (like EMT) or plenum-rated cables. Standard PVC and ENT are not permitted due to smoke generation.

    Join 1,000+ users passing the Journeyman Electrician

  70. Q70.What is the maximum fill percentage for a conduit over 24 inches long containing more than 2 conductors?

    A.31%
    B.40%
    C.53%
    D.60%
    B40%

    Explanation: Chapter 9 Table 1 limits conduit fill to 40% for over 2 conductors (new or existing).

    Join 1,000+ users passing the Journeyman Electrician